"A building has a ceiling slope of 3.5 in 12 that has Class III storage to 12 ft high. The 1999 Edition of NFPA 13 allowed miscellaneous storage to have sloped ceilings and the 2002 Edition does not since 12.1.7 applies to Chapter 12 where miscellaneous storage is located. Are sloped ceilings allowed for miscellaneous storage?"



We have reviewed the 2002 Edition of NFPA 13 as the applicable Standard. Our informal interpretation is that miscellaneous storage is permitted to have a sloped ceiling greater than 2 in 12.



The general requirement of 12.1.7 in the 2002 Edition indicates that the criteria apply to buildings with ceiling slopes not exceeding 2 in 12. There are no overriding statements in 12.1.10 for miscellaneous storage indicating that the ceiling must not exceed 2 in 12 slope. This was not the intent of the committee from the information provided in the 2006 Report on Proposal and Report on Comments. This was corrected in the 2007 Edition in Section 13.2.2 to clarify that the design criteria and modifiers of Chapter 11 shall be applicable. Thus a slope exceeding 2 in 12 is permitted for miscellaneous storage. As you indicated in your question, the 1999 edition in Section 7-2.3.2.2 for miscellaneous storage permitted a ceiling slope greater than 2 in 12. Section 7-3.1.3 indicated that the sprinkler system criteria specified in Section 7-3 is intended to apply to buildings with ceiling slopes not exceeding 2 in 12. Since Section 7-3 does not apply to Section 7-2, the ceiling slope limitation did not apply to miscellaneous storage.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to