American Fire Sprinkler Association

12750 Merit Dr., Suite 350 Dallas TX 75251

Ph: (214) 349-5965   Fax: (214) 276-0908



------------------------------

TECHNICAL UPDATE

AUGUST 13, 2008

------------------------------



We have a building with an unheated attic space of approximately 3,900 square feet. The project specifications are requiring a wet fire protection system with the piping to be insulated and heat traced to prevent freezing. Is it the intent of Section 8.16.4.1 to allow this method of freeze protection for an entire system in lieu of a dry type system? Would sprinkler heads be protected from freezing by heat tracing branch line piping?"



We have reviewed the 2007 edition of NFPA 13 as the applicable standard. Our informal interpretation is that heat tracing is permitted in lieu of a dry pipe system but heat trace products are not yet available for branch line applications.



A manufacturer has reported that there is no heat tracing cable available with a listing for branch lines since the testing procedures have not yet been developed or defined by FM or UL. UL has been contacted and they confirmed that there is not yet a test standard and that a significant amount of work must be completed on the ANSI standard before testing can begin. A time estimated completion date has not yet been identified.



The heat tracing will affect the sprinklers thus the testing standard will have to address this issue. The concern is that the tracing wire may overheat the branch line and activate the sprinkler. The current UL listing is for use on piping between the system control valve and the system branch lines, but does not include the branch lines. Thus a dry pipe or antifreeze system should be installed for attic space unless the space is heated above 40 degrees F where a wet pipe system could be installed.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.