American Fire Sprinkler Association

12750 Merit Drive Suite 350,  Dallas, Texas 75251

Ph: (214) 349-5965   Fax: (214) 276-0908

____________



TECH TALK

AUGUST 2008

____________



LOCATION OF THE FIRE DEPARTMENT CONNECTION WITH FIRE PUMPS

The location of the fire department connection (FDC) should be located downstream of the fire pump discharge valve and not located on the inlet or suction side of the fire pump even though the NFPA 20 standard does not specifically indicate as such except in the annex. The reason for this is

that a FDC on the suction side of the pump will compound the water pressure when the fire department pumper uses the FDC. This arrangement will be similar to two pumps located in series where the pressures are added. An example is

the fire pump is operating at 100 psi at 1500 gpm and a fire department pumper pressurizes the FDC at 150 psi that is located on the suction side of the pump. Add the pressure at the FDC of 150 psi to the fire pump pressure of 100 psi will equal a total pressure of 250 psi at the discharge side of the fire pump (not considering friction loss). The 250 psi pressure will likely exceed the system component pressure ratings. Thus the FDC must located after the discharge valve on the fire pump so the fire pump and the fire department pumper will be in parallel and the pressures will not be compounded. There are no installation standards of the FDC in NFPA 20 since it is located outside its boundaries (i.e. located downstream of the discharge control valve). The reference to a FDC in the 2007 edition of NFPA 20 is Figure A.5.19.1.2(b) where it shows the location and references either NFPA 13 or NFPA 14.



NEW ISSUE OF THE CODE AUTHORITY(r) (TCA) AVAILABLE

Underwriters Laboratories Inc. released Issue 2, 2008, of The Code Authority(r) (TCA) newsletter for regulatory authorities. This publication is now available on UL's Web site at: http://www.ul.com/ tca/ and this edition features an article Understanding Fire Pump Controller Applications.



FSA RESIDENTIAL FIRE SPRINKLER SYSTEM INSTALLATION GUIDE

AFSA has a new fire sprinkler fitter correspondence training program that teaches installers the techniques for residential fire sprinkler system installation according to the 2007 NFPA 13D, Standard for the Installation of Sprinkler Systems in one-Two-Family Dwellings and Manufactured Homes in as little as 6 months! For more information call (214) 349-5965.



    Member:  $200 with online testing ($250 with paper testing)

Non-Member:  $500 with online testing ($550 with paper testing)



Not a member? AFSA will give every new company that joins between now and July 2009 one complimentary copy of this training guide, a ($500 value), yours free for becoming an AFSA member. So join today!



-------------------------------

Mark your calendars for the next Virtual Seminar

Multipurpose Sprinkler Systems and the Fire Sprinkler Contractor



* Rescheduled September 30, 2008



To Register:  Event ID: 14088

12:00 PM EDT

11:00 AM CDT

10:00 PM MDT

 9:00 AM PDT

Earn:  0.15 CEU's / 1.5 CPD's.


      Member:    $ 90 per connection

  Non Member:    $130 per connection

CEU Certificate: $ 40 per listener to receive CEU Certificate.



If any listeners at your site need CEU/CPD credit, the processing fee is an additional $40 per person. Enter each person's full name and e- mail address you are purchasing CEU/CPD credits for including yourself to receive Certificate.



To Register:

Online: www.krm.com/afsa

By Phone: 800-775-7654, please have your credit card information ready.

By Fax: 800-676-0734.  Fax completed form with Credit Card information.

By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI 54702-1187 (Payment must accompany registration)



Future AFSA Virtual Seminar

October 30, 2008

December 18, 2008



2008 AFSA DESIGN SCHOOLS

Beginning System Planning School

September. 22-October. 3, 2008

November 3-14, 2008.



Registration Prices:

      Member  $1100

 Non-Member   $1600

NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks prior to each class.

-------------------------------

TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection- engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association, 12750 Merit Drive, Ste 350, Dallas, TX 75251. Voice (214) 349-5965 ext 124 or Fax (214) 276-0908. All rights reserved.



If you'd rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail to [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to