"A self-storage facility has solid partition walls located more than 18 in. down from the deflector. Chain link fencing is applied from the top of the wall up to the roof deck for security. Should the chain link fencing be treated as an obstruction or wall?"



We have reviewed the 2007 edition of NFPA 13 as the applicable Standard. Our informal interpretation is that chain link fencing is not an obstruction and should not be treated as a wall.



NFPA 13 does not specifically address chain link fencing as an obstruction or wall but we can gain clues from NFPA 13 on how to deal with this application. First is the definition for unobstructed construction where the structural members do not impede heat flow or water distribution in a manner that materially affects the ability of sprinklers to control or suppress a fire. In addition, the horizontal structural members are not solid, where the openings are at least 70 percent of the cross section area and the depth of the member does not exceed the least dimension of the openings. Annex material for bar joist construction with fireproofing applied is considered obstructed if the fireproofing is greater than 30 percent of the area (less than 70 percent open) of the joist in Section A.3.7.1 (7). Another area the standard addresses a similar issue is privacy curtains in section 8.6.5.2.2.1 where the fabric mesh on ceiling tracks and have openings in the mesh equal to 70 percent or greater and extend a minimum of 22 in. from ceiling shall not be considered obstructions. The handbook commentary indicates that this applies to light hazard occupancies only since the testing involved a light hazard environment. The testing showed that as much water reached the opposite side of the curtain as allowed by Section 8.6.5.2.2 for suspended or floor-mounted vertical obstructions. In considering the self-storage application, the solid walls are located more than 18 in. down from the deflector and are not considered obstructions by NFPA 13. The sprinklers are also spaced less than light hazard occupancies even though the fuel package is higher for the storage. The chain link fencing located above the wall is more than 70 percent open and will not impede heat flow. Since the heat will readily flow to the ceiling, the next question is will enough water get onto the floor area? We often think that every inch of floor space must be directly wetted. This isn't the case. As shown for obstructions greater than 18 in. below the sprinkler, we can have obstructions up to 4 ft wide without sprinklers beneath them. In addition, solid obstructions such as bookshelves in libraries are acceptable as long as there is an 18-inch clearance. This explicitly tells us that we can tolerate a fair amount of shadowing on the floor and still maintain control of the fire. Thus the chain link fencing installed above the wall is not an obstruction.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to