"Piping is installed and supported by hangers that are 16 to 18 in. long. A person can reach up and move the system by hand. Is there a limit to the motion in sprinkler piping when is installed outside seismic zones? Is "sway brace" synonymous with "seismic brace" only to be applied in seismic zones?"



We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our informal interpretation is that the standard does not explicit indicate that the pipe should be prevented from movement when it is not required to protect the system against damage from earthquakes. Regarding the second question, sway bracing is synonymous with seismic bracing and shall be installed when systems are required to be protected against damage from earthquakes since both are referenced under 13:9.3.



To address the first question on pipe motion, the standard does not address sway or movement for a system that does not require earthquake bracing. There is an expectation that the piping should remain in place, but the system piping will move or sway as water flows in the piping. The use of swivel rings, clevis hangers, and rod lengths greater than 6 in. will allow the piping to move or sway. There is little impact on the system performance if the piping were to sway when upright or pendent sprinklers are used. The pipe will move but not sufficiently to move the pendent out of the ceiling sheathing, affect the area of coverage, cause sprinklers to operate from impacting nearby objects or allows pipe joints to fail. There is more concern where sidewall sprinklers penetrating sheathing in a wall where too much movement could cause the head to move behind the sheathing. This is addressed in 13:9.2.3.6 that indicates wall mounted sidewall sprinklers be restrained to prevent lateral movement mainly so the sprinkler does not move behind the wall sheathing. Another area that addresses pipe movement is when the system piping is laid on the structural member that it be secured to prevent pipe movement according to 13:A.9.1.1. Lastly, sprigs that are 4 ft or loner also have to be restrained against lateral movement according to 13:9.2.3.7. The bottom line is that when the system is supported according to 13:9.1 and 9.2, it is considered adequate to prevent excessive movement according to the standard and the piping is expected to remain in its original location and position for fire control. It is not the intent of the standard that sway or seismic bracing be provided for systems outside of areas where protection against damage from earthquakes referenced in 13:9.3.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to