Exterior Walkways with Type V Construction Sprinkler Criteria

A hotel of type V construction is under construction and being protected per NFPA 13R. The exterior walkways require sprinkler protection by a local requirement. A residential dry sidewall does not exist. What design criteria would this walkway fall under? Sprinkler protection is not required by NFPA 13R but may be required by the building code. The IBC Section [F] 903.3.1.2.1 goes outside the dwelling unit for balconies, patios and decks and indicates sprinkler protection shall be provided for exterior balconies where the building is of Type V construction. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch to 6 inches below the structural members, and a maximum distance of 14 inches below the deck of the exterior balconies that are constructed of open wood joist construction. Section 903.3.2 requires the use of residential or quick response sprinklers in dwelling units and sleeping units in Group R and light- hazard occupancies as defined in NFPA 13. The criteria is intended to ensure that within the dwelling unit a fast response sprinkler is used, which is now unnecessary since it is required by NFPA 13 and 13R. Additionally it╒s not intended to delete the allowance to use the residential sprinkler criteria identified in NFPA 13 and 13R.



The bottom line is that the hydraulic design criteria for the balconies will be per NFPA 13R. The main question is do we apply the criteria for ╥within╙ or ╥outside╙ the dwelling unit. Although, NFPA 13R does not provide guidance for exterior, open corridors or balconies, garages are addressed. This, plus NFPA 13 criteria on corridors, shows us that it is appropriate to treat balconies as being ╥within╙ the dwelling unit. It would be reasonable to use the protection requirement of 6.8.3.3 for garages. NFPA 13R allows garages to be sprinklered with quick-response sprinklers designed to provide a density of 0.05 gpm/ft2 over the area of the garage or 7 psi (which ever is greater), but not to exceed four sprinklers. The area would not be applicable in this case, but the four sprinklers flowing would be applied.



NFPA 14 2007 EDITION HOSE LENGTH

Sentence Correction from the November 2008 Tech Talk:

╥If the travel distances for sprinklered (150 ft spacing) and nonsprinklered (200 ft) areas are exceeded, additional hose connections are required.╙ The distances are reversed and should read: ╥If the travel distances for sprinklered (200 ft spacing) and non sprinklered (150 ft) areas are exceeded, additional hose connections are required.╙

We apologize for the error.

AFSA Technical Services Staff

-----------------------------











2009 AFSA DESIGN SCHOOLS

Beginning System Planning School

January 12-23, 2009

February 9-20, 2009

March 9-20, 2009

April 20-May 1, 2009

May 11-22, 2009

July 13-24, 2009

August 10-21, 2009

November 9-20, 2009



Registration Prices:

     Member   $1100

 Non-Member   $1600



NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks prior to each class.





AFSA/OSU Fire Sprinkler Inspection Training & Certificate Course

Stillwater, OK╩

- Receive a $100 off any 2009 course

February 9-11, 2009

      May 4-6, 2009

Contact Brandy Mays at 405-744-5369 for registration form.





NEW Fire Sprinkler Systems

Hydraulic Calculations- Part 3 on

eCampus!


This 2-hour interactive online

course is the third in a series

covering the topic of hydraulic

calculations for fire sprinkler

systems. For more information, go

to the AFSA website.

     Member  $ 90

 Non-Member  $100


-------------

TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection- engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.


Copyright (c) 2008, American Fire Sprinkler Association, 12750 Merit Drive, Ste 350, Dallas, TX 75251. Voice (214) 349-5965 ext 124 or Fax (214) 276-0908. All rights reserved.

-----------

If you╒d rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail to [email protected]. Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.





 _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to