American Fire Sprinkler Association

12750 Merit Dr., Suite 350 * Dallas TX 75251

Ph: (214) 349-5965   Fax: (214) 276-0908



-------------------

TECHNICAL UPDATE

DECEMBER 3, 2008

-------------------



I am working on a 13R system for a hotel that has exterior walkways that is type V construction so the exterior walkways would require sprinkler protection. We want to use dry sidewalls beneath the walkways. They do not make a residential dry sidewall. What design criteria would this walkway fall under?



We have reviewed NFPA 13R, 2002 Edition and the 2003 Edition of the IBC that you indicated as the applicable standard. Our informal interpretation is that sprinkler protection is not required by NFPA 13R but will be required by the IBC. The criterion for the sprinkler protection is not defined by the IBC but should be the same as 13R for inside the dwelling unit.



IBC Section [F] 903.3.1.2.1 Balconies, patios and decks indicates that sprinkler protection shall be provided for exterior balconies where the building is of Type V construction. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch to 6 inches below the structural members, and a maximum distance of 14 inches below the deck of the exterior balconies that are constructed of open wood joist construction. Section 903.3.2 requires the use of residential or quick response sprinklers in dwelling units and sleeping units in Group R and light-hazard occupancies as defined in NFPA 13. This criteria is intended to ensure that within the dwelling unit a fast response sprinkler is used, which is now unnecessary since it is required by NFPA 13 and 13R. Additionally it's not intended to delete the allowance to use the residential sprinkler criteria identified in NFPA 13 and 13R.



The bottom line is that the hydraulic design criteria for the balconies will be per NFPA 13R. The main question is do we apply the criteria for "within" or "outside" the dwelling unit. Although, NFPA 13R does not provide guidance for exterior, open corridors or balconies, garages are addressed. This, plus NFPA 13 criteria on corridors, shows us that it is appropriate to treat balconies as being "within" the dwelling unit. It would be reasonable to use the protection requirement of 6.8.3.3 for garages. NFPA 13R allows garages to be sprinklered with quick-response sprinklers designed to provide a density of 0.05 gpm/ft2 over the area of the garage or 7 psi (which ever is greater), but not to exceed four sprinklers. The area would not be applicable in this case but the four sprinklers would be. Since this is not addressed in NFPA 13R, discuss it with the AHJ beforehand.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright ⌐ 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request at [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.