"A legitimate stage has the proscenium opening protected by nozzles  
supplied by a deluge valve attached to a manual standpipe.  The  
nozzles are 30 ft above the stage floor. The heat detectors are at the  
ceiling on the stage side. The engineer has specified 65 deg. pattern  
spray nozzles with 2.3 K-factor. NFPA 101 states that the curtain  
should be kept completely wet for 30 minutes. Does the demand from the  
deluge system need to be added to the sprinkler demand from the stage  
ceiling? How do you determine the water demand for the nozzles?"



We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our  
informal interpretation is that the demand from the deluge system  
should be added to the sprinkler system demand and the deluge design  
is based on 3 gpm per linear foot.



The requirement for including demand for a water curtain in your  
calculations is found under Section 11.3.3.3. This section states, "If  
a single fire can be expected to operate sprinklers within the water  
curtain and within the design area of a hydraulically calculated  
system, the water supply to the water curtain shall be added to the  
water demand of the hydraulic calculations and shall be balanced to  
the calculated area demand." In addition, Section 11.3.3.1 establishes  
the delivery density the deluge system will have to deliver as 3 gpm  
per lineal foot with no sprinkler discharging less than 15 gpm.  
Regarding the nozzles that were specified, Section 8.15.16.2 indicates  
that the deluge system shall be provided with open sprinklers. An open  
sprinkler is different from a directional spray nozzle, so a question  
back to the specifying engineer is warranted. A directional spray  
nozzle will provide water in a specific, directional pattern according  
to NFPA 15 and is usually applied to a surface area such as vessels or  
transformers. NFPA 13 for stages addresses water curtains where the  
water discharges from open sprinklers and provides a curtain of water  
in front of the opening. Open sprinklers do not provide specific,  
directional discharge patterns onto a vertical surface. Note that the  
small    K-factor of 2.3 will require a higher pressure to deliver the  
required 15 gpm for each sprinkler.



-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.



Copyright ⌐ 2009, American Fire Sprinkler Association.  All Rights  
Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.

  
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to