RETAIL CLASSIFICATION

Generally speaking, NFPA 13 expects the actual contents to be used  
when determining the hazard classification of a facility and the rare  
change to be treated like any other building that changes it?s use  
sometime in its life span.  On the other hand, retail is treated  
differently since the contents of a retail facility typically change  
on a regular basis (either from carrying new products or new  
occupants). This is especially true in malls. There are situations,  
though, where imposing a higher classification for likely change is  
not warranted. For instance, if you had a manufacturing facility, say  
for steel parts, that had a large sales area, light hazard would be  
appropriate since it isn?t likely to change. Additionally, if it did  
change, it would be viewed like any facility change whereby both the  
IBC and IFC would require an evaluation of the system for the new use.  
For a retail application, consider an individual building used  
entirely as a jewelry store.  There are limited combustibles that  
clearly fall within the definition for light hazard. So, should the  
sprinkler protection be based on the actual contents or must the annex  
example in A.5.3.2 of ordinary hazard group II for retail be applied? 
╙ It is reasonable to apply the actual contents for determining the  
hazard classification.



Items to be considered when evaluating facilities are: ownership of  
building, is it an individual building, and is it expected to remain  
the same? Also, is the owner aware that major changes to the system  
would probably be required for other uses? It is also worth  
considering if the building is required to be protected since if it  
isn╒t then the owner should be allowed to decide whether they want a  
more costly system that allows the flexibility for other uses/ 
occupants. Again, in malls this is not an option but for many small,  
individual retail facilities that seldom change, basing the design on  
the current, actual hazard is appropriate. Naturally, this would  
require approval by the AHJ.



UPDATING THE STANDARDS

The NFPA 14 committee is in the ROC stage but there is some work to be  
done to coordinate with NFPA 20╒s new high-rise chapter. The NFPA 20  
committee proposed when fire pumps are located in series that they be  
located within the same room.  This concept sounds good but this  
presents some challenges or conflicts to the NFPA 14 standard. There  
was insufficient time to address the impacts by the NFPA 14 committee  
so the end result was that NITMAMs were submitted on the new NFPA 20  
challenging the high-rise requirements. The NITMAMs will be address  
during the floor vote during NFPA?s annual meeting. Watch for a  
summary on the result of this topic in an upcoming issue in Sprinkler  
Age.

---------------------------------------------

2009 AFSA DESIGN SCHOOLS

Beginning System Planning School

May 11-22, 2009 (Sold Out)

July 13-24, 2009

November 9-20, 2009

Registration Prices:

     Member   $1100

Non-Member   $1600



NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks  
prior to each class.





WEBINAR EVENT

The Use of Specific Application Sprinklers in Combustible Attic

And Interstitial Spaces and Extended Coverage Sprinklers

May 7, 2009

11:00 AM CDT



Registration Prices:

     Member   $75

Non-Member   $125

1.5 CPDs and   0.15 CEUs.

To register go to: www.firesprinkler.org/training/preactionseminar.html





AFSA/OSU FIRE SPRINKLER INSPECTION TRAINING & CERTIFICATE COURSE

Stillwater, OK

May 4-6, 2009

- Receive a $100 off any 2009 course

Contact Brandy Mays at 405-744-5369 for registration form.



AFSA 28TH ANNUAL CONVENTION & EXHIBITION BOOTH RESERVATIONS

Booth reservations are available now till the end of May.

Reserve your booth today.

Go to: www.firesprinkler.org/convention/exhibition



NEW- FIRE SPRINKLER SYSTEMS NFPA CONFERENCE & EXPOSITION

JUNE 8-11, 2009

Chicago, IL

---------------------------------------------

TechTalk is prepared by the Technical Services Department of the  
American Fire Sprinkler Association: Vice President of Engineering and  
Technical Services, Roland Huggins, a PE registered in fire protection  
engineering; Phill Brown, a CFPS and a NICET IV certified automatic  
sprinkler technician, and Tom Wellen, a degreed fire protection- 
engineering technologist. Opinions are provided with the understanding  
that AFSA assumes no liability for the opinions or actions taken on  
them and they are not to be considered the official interpretation of  
the NFPA or that of its technical committees.



Copyright (c) 2009, American Fire Sprinkler Association, 12750 Merit  
Drive, Ste 350, Dallas, TX 75251. Voice (214) 349-5965 ext 124 or Fax  
(214) 276-0908.  All rights reserved.

---------------------------------------------

If you╒d rather not receive future faxes from AFSA, fax your removal  
request to (888) 839-4830 or e-mail to [email protected].  
Please include your company name and the specific fax numbers(s) at  
which you do not wish to receive faxes from us. Our failure to comply  
with your request may be unlawful.











  
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to