American Fire Sprinkler Association

12750 Merit Dr., Suite 350 * Dallas TX 75251

Ph: (214) 349-5965 Fax: (214) 276-0908



-----------------

TECHNICAL UPDATE

May 21, 2009

-----------------



I have a double interlock preaction system that is approximately 20  
gallons and potentially another system that will be approximately 600  
gal. Is it the intent of NFPA 13, Section 7.3.2.3.1.1 and 7.3.2.3.1.3  
to install a traditional inspectors test connection arrangement at the  
most remote branch line and at the highest elevation, or a test  
manifold regardless of the system size? Section 8.17.4.4.3 &  
8.17.4.4.4 seem to suggest that the traditional inspectors test  
connection arrangement would only be required if the system was over  
750 gallons. So would a system that was 15 gallons or 749 gallons  
still require the traditional inspectors test connection arrangement  
if 7.3.2.3.1.2 is not met?



We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our  
informal interpretation is that an inspectors test connection at the  
most remote branch line at the highest elevation will be required.



Section 8.17.4.4.1 calls for a test connection for a preaction system  
only when it utilizes supervisory air. But, Sections 8.17.4.4.3 and  
8.17.4.4 indicates that trip test connections are required for double  
interlock preaction systems in excess of 750 gallons. These sections  
may have been an oversight from the committee when the changes were  
made for Section 7.3.2.3 for water delivery requirements in the 2007  
Edition. Sections 8.17.4.4.3 and 8.17.4.4 were changed during the  
A2009 Report on Proposals (ROP) in 13-237. The substantiation states,  
"These revisions are needed in recognition of the current allowances  
in 7.3.2.3.1.1 and 7.3.2.3.1.3 to size double interlock preaction  
systems that will discharge within 60 seconds or from a manifold in  
accordance with the parameters of Table 7.2.3.6.1.  As with all dry  
pipe systems, all double interlock preaction systems should have a  
trip test connection." Also related to this subject, Section 7.3.2.3  
was further modified during the June 2009 Report on Comments (ROC)  
meeting where a new section 7.3.2.3.1.1 was added that will state, "A  
system size for double interlock preaction systems of not more than  
500 gal shall be permitted and shall not be required to meet any  
specific water delivery requirement to the trip test connection." The  
existing sections will remain and renumbered accordingly.  Although  
the use of the material from the A2009 ROP and ROC is premature, a  
challenge during the vote at the annual NFPA meeting in June 2009 is  
not expected.



-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist.  This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.



Copyright ⌐ 2009, American Fire Sprinkler Association.  All Rights  
Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected].   Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to