I have a wood building with a crawl space constructed of TJI’s with  
OSB decking.  I have omitted the sprinklers in the crawl space because  
it meets all the criteria of 8.15.6. What size should the remote area  
be for the wet system above it (i.e. 1,500 or 3,000 sf)?”

We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our  
informal interpretation is the remote area is 3,000 sf.

The situation you describe is not identified in Section 11.2.3.1.4(4)  
where this section gives the instances where the remote area increase  
to 3,000 is not required. Thus, Section 11.2.3.1.4(3) applies which  
specifically calls out concealed spaces described in Section 8.15.6.  
As such, the minimum area of sprinkler operation for that portion of  
the building shall be 3,000 sf. This section also indicates that the  
design area of 3,000 sf shall be applied only to the sprinkler system  
or portions of the sprinkler system that are adjacent to the  
qualifying combustible concealed space. Note also, that when a remote  
area of 3,000 sf is used, Figure 11.2.3.1.1 allows one to go up the  
curve to a lesser density. For example, in a light hazard application,  
the density for a remote area of 3,000 sf is 0.07 gpm. The purpose of  
the 3,000 sf remote area increase is to compensate for a larger fire  
that is expected if the unprotected concealed space is involved.

-----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist.  This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association.  All Rights  
Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request to [email protected].   Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to