American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

-------------------
TECHNICAL UPDATE
JUNE 10, 2009
-------------------

Is a waterflow pressure switch required on a dry system if the dry  
system is
being fed by a wet system that has a waterflow switch?


We have reviewed NFPA 13, 2007 Edition that you indicated as the  
applicable standard. Our informal interpretation is that a waterflow  
device is required.

Section 6.9.2.2.1 indicates that the alarm apparatus for a dry pipe  
system shall consist of listed alarm attachments to the dry pipe  
valve. The purpose of the waterflow switch is to indicate that the dry  
pipe system has tripped due to a lower air pressure and water was  
introduced into the system. Even though the wet pipe system waterflow  
switch will likely activate, the gauges could be overlooked on the dry  
pipe system or the gauge readings could be meaningless to an untrained  
person during the waterflow alarm investigation. The standard does  
acknowledge that the dry pipe system can be downstream of the wet pipe  
system’s alarm valve in Section 6.9.2.2.2. This section allows the  
waterflow alarm from the dry pipe system can be connected into the wet  
pipe system alarm sounding or annunciating device. However, the  
standard also indicates that if the dry pipe system has 20 or less  
sprinklers, Section 8.17.1 indicates a local waterflow alarm is not  
needed. Applying the same size restriction to the need of a waterflow  
device is appropriate.

-----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist.  This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association.  All Rights  
Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to