American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

______________________

TECHNICAL UPDATE
June 17, 2009
______________________

”I am currently working on a project with 14 dry pipe systems in a  
manufacturing facility. Due the large size of the building and a  
future phase II, we cannot get to an exterior wall on several systems  
to install a test connection as per NFPA 13:8.17.4.3.3 which states:  
“The trip test connection shall be located on the end of the most  
distant sprinkler pipe in the upper story and shall be equipped with a  
readily accessible shutoff valve and plug not less than 1 inch.”  The  
commentary in the handbook also indicates that this requirement is so  
the approximate time from opening of the most distant sprinkler in the  
system until water flows from that sprinkler can be measured. All of  
these systems have a capacity of less than 750 gallons. Since NFPA  
13:7.2.3.4 does not require you to meet any water delivery time due to  
the system size; is it necessary to locate the test connection as per  
8.17.4.3.3?”

We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our  
informal interpretation is yes, because as part of the acceptance  
testing required by Section 24.2.3.2 you have to establish a baseline  
number for comparison by future inspections required by NFPA 25.

Note though that 8.17.4.3 doesn't say it has to discharge outside. The  
guidance for wet pipe in 8.17.4.2.3 is reasonable to follow.  If you  
do run a long pipe to the exterior, discuss with the AHJ that the time  
will be increased. Despite having no restrictions, you wouldn't want  
the AHJ going off on a larger than expected number.


-----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association.  All Rights  
Reserved

--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to