TECHNICAL UPDATE
JANUARY 13, 2010
-------------------

My understanding is that NFPA 13R will allow you to omit sprinkler protection 
in linen and laundry chute but the IBC also addresses laundry chutes, 
903.2.10.2 Rubbish and Linen Chutes. An automatic sprinkler system shall be 
installed at the top of rubbish and linen chutes and in their terminal rooms. 
Chutes extending through three or more floors shall have additional sprinkler 
heads installed within such chutes at alternate floors. Chute sprinklers shall 
be accessible for servicing.  Does the IBC section 903.2.10.2 override NFPA 13R 
in this case and would sprinkler protection be required in a laundry/linen 
chute?

We have reviewed NFPA 13R, 2007 Edition and the 2006 Edition of the IBC that 
you indicated as the applicable standard and code. Our informal interpretation 
is that the IBC will require the linen chute to be sprinklered. NFPA 13R does 
not discuss linen chutes but the IBC in Section 903.2.10.2 does require the 
protection of the chute. The IBC sets the requirement for the protection of the 
linen chute for all buildings sprinklered or not. 

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 
 Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected].   Please include your company name 
and the specific fax numbers(s) at which you do not wish to receive faxes from 
us.  Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to