American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

------------------
TECHNICAL UPDATE
FEBRUARY 17, 2010
------------------

In a 13R system where the balcony is protected per the IBC, the wet-pipe branch 
line drops down from above the ceiling within the 6 inch exterior wall to a dry 
horizontal sidewall sprinkler. The drop nipple is completely wrapped in 
insulation. The barrel length is approximately 3-1/2 inches. This area is 
assigned a lowest temperature below -20 degrees F. Does this installation 
comply with NFPA 13, 2007 section 8.4.10?

We have reviewed 13, 2007 Edition that you indicated as the applicable 
standard.  Our informal interpretation is that it appears that it does not 
comply with NFPA 13 on freeze protection requirements.

There are actually two freeze protection criteria that are a problem. The first 
is that all portions of a sprinkler system must be protected against freezing.  
To accomplish this, all pipe containing water must be exposed to air that is at 
or above 40 degrees F or protected against freezing (see 13:8.16.4.1.1). This 
can be accomplished using a dry pipe or antifreeze system or heat tracing 
(although branch lines can not yet use heat tracing since there is no listed 
product on the market). Although the insulation on the outside of the drop 
nipple reduces its exposure to the cold, having insulation on the inner portion 
of the drop nipple reduces its exposure to heat. Insulation alone does not stop 
a pipe from freezing but must be used in conjunction with exposure to heat.  
Technically, it is a matter of heat transfer and if the transferred heat to the 
pipe is greater than the transferred loss of heat from the pipe, the pipe will 
not freeze. So in mild climates with very short periods of freezing 
temperatures, it may not be a problem. But in more severe climates with 
sustained cold periods, insulation alone simply increases the time required for 
the pipe to freeze. 

The second issue is that there are barrel length requirements to avoid freezing 
caused by the cold being conducted through the sprinkler barrel to its 
connection to the pipe containing water (see 13:8.4.10.1). This means that part 
of the sprinkler barrel must be exposed to heated air inside the building. The 
requirement for the barrel to be exposed to heated air is explicitly stated in 
the manufacturer’s installation instructions, as is the minimum exposed length. 
 One manufacturer specifies for exposure to -20 degrees F a minimum of 12 
inches of barrel when exposed to air that is at least 40 degrees F. The length 
increases to 18 inches for -40 degrees F.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2010, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to