American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

-----------------
TECHNICAL UPDATE
MARCH 12, 2010
-----------------

I am installing a residential system in a home that has a basement that is 
being sprinklered with a wet pipe system. From this system, I am installing an 
antifreeze loop for the upper portion of the home. My sprinkler riser has a 
reduced pressure backflow preventer (RPZ) at the point of connection to the 
fire line. The riser piping would go vertical from the RPZ device feeding the 
wet pipe sprinkler system to the antifreeze loop subsystem. Am I required to 
install an additional RPZ as shown Figure 8.3.3.3.2.1? If not, is an expansion 
chamber required at the RPZ on the system riser?”

We have reviewed NFPA 13D, 2010 Edition as the applicable standard. Our 
informal interpretation is that if a RPZ is on the system riser, the antifreeze 
loop can be connected in accordance with Figure 8.3.3.3.1.1.

NFPA 13D considers Figure 8.3.3.3.1.1 and Figure 8.3.3.3.2.1 equally acceptable 
and does not dictate the requirement for a backflow preventer. It is the IBC 
and IPC that dictates protection against backflow and specifically states that 
if the system contains antifreeze that a RPZ type of backflow preventer shall 
be used. Since your system riser contains an RPZ, the IPC is satisfied so you 
can connect your antifreeze portion to the wet pipe sprinkler system using 
Figure 8.3.3.3.1.1 (the old drop loop and check valve with a hole). This 
isolates the antifreeze solution while allowing the build-up in pressure form 
temperature changes to vent ck into the wet pipe system. The requirement for an 
expansion chamber is literally a requirement just for antifreeze systems 
connected to a wet-pipe system.  The expectation is that these systems are 
small and there is not enough trapped air to cushion the thermal expansion. 
There is no requirement in NFPA 13D (or NFPA 13) for an expansion chamber to be 
installed on a wet pipe system that utilizes a backflow preventer.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
-------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected].   Please include your company name 
and the specific fax numbers(s) at which you do not wish to receive faxes from 
us.  Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to