American Fire Sprinkler Association

12750 Merit Dr., Suite 350 Dallas TX 75251

Ph:  (214) 349-5965   Fax:  (214) 276-0908


-----------------

TECHNICAL UPDATE

JULY 7, 2010

-----------------


When supporting pipe from a wood structure such as an attic and  
additional wood members are installed to support the sprinkler system,  
does the additional wood have to be attached to the wood truss or  
joists with bolts sized per NFPA 13 or can this be attached in the  
same method the trusses were constructed?


We have reviewed NFPA 13, 2007 Edition that you indicated as the  
applicable standard. Our informal interpretation is that NFPA 13  
requirements for fasteners do not apply to the assembly of structural  
members.


The scope of Chapter 9 in NFPA 13 is for the support of the sprinkler  
system piping and the attachments to the structure.╩This chapter does  
not address additional wood structural members and its fasteners that  
will support sprinkler piping. Thus the loading of the system piping  
should be communicated to the structural engineer to verify the  
assembly will support the load, as is noted in NFPA-13, section  
9.1.1.2.╩Guidance is provided by the manufacturers of engineered wood  
products on supporting fire sprinkler piping from the structure.╩As  
an example, composite wood joists have thin particleboard as webbing  
and it is not sufficient to support the loads of sprinkler piping and  
seismic loads.╩Additional wood blocking or slave piece is added for  
the pipe support attachment where the types of fasteners for those  
applications are specified, and the data from the manufacturers  
provides extensive information on the type of fasteners to be used,  
how many are required, and how they should be spaced.


-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Roland Huggins, a PE registered in fire protection  
engineering ,Vice President of Engineering and Technical Services;  
Phill Brown, a NICET IV certified automatic sprinkler technician and  
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a  
degreed fire protection engineering technologist.  This is provided  
with the understanding that the AFSA assumes no liability for this  
opinion or actions taken on it and they are not to be considered the  
official position of the NFPA or its technical committees.



Copyright ⌐ 2010, American Fire Sprinkler Association.  All Rights  
Reserved

--------------------------

If you╒d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request at [email protected].   Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to