American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908

-----------------
TECHNICAL UPDATE
JULY 14, 2010
-----------------

“The NFPA 13 standard for Class II, III or IV commodities mentions wood 
products, but nothing such as wood chips.  What would the commodity 
classification of wood chips in plastic bags palletized to 20 ft high be 
considered?”

We have reviewed NFPA 13, 2010 Edition as the applicable standard.  Our 
informal interpretation is that wood chips still fall within the standard 
definitions for commodities.

There is nothing unique about wood being in smaller pieces so it would be 
treated the same as other wood products. The definitions also include specified 
amounts of plastics to account for packing material and containers/bags. As per 
13:5.6.3.3.2, a Class III is allowed up to 5% of the pallet load to be a Group 
A plastic. If it exceeds that amount, it would either be a Class IV (if within 
its allowed amounts) or a Group A plastic. The problem you have is that with 
the wood chips being within plastic bags (such that water cannot pre-wet the 
storage), it is considered encapsulated. NFPA 13:14.2 provides guidance for 
encapsulated commodities only up to 15 ft. The annex tells us that up to 15 ft, 
we treat encapsulated the same as standard storage, but up to 20 ft additional 
protection is required. Unfortunately, NFPA 13 does not provide any additional 
guidance. This leaves us to follow other criteria such as FM Loss Prevention 
Data sheet 8-9 (which can be obtained for free from the FM Global website). An 
exception to this is when ESFR sprinklers are applied in accordance with Table 
14.4.1. If the commodity was placed in storage racks, then Chapter 16 would 
apply where it does provide criteria for encapsulated commodities.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; Phill Brown, a NICET IV certified 
automatic sprinkler technician and NFPA Certified Fire Protection Specialist 
(CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This 
is provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 


Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to