Clearance Hole

"A multistory building has a 4-inch standpipe. If clearance holes are provided 
in
accordance with 9.3.4.3 are flexible couplings still required within 12-inches 
above
and within 24-inches below the floor in a multistory building?"

We have reviewed NFPA 13, 2010 edition as the applicable standard. Our informal 
interpretation is that flexible couplings are required.

Section 9.3.2.3(2) indicates that flexible couplings shall be installed within 
12-inches
above and within 24-inches below the floor in multistory buildings. Note that 
there
is no exception provided to omit flexible couplings in that section when 
clearance
holes are provided. As such, flexible couplings are required above and below the
 floor even if a clearance hole is provided. Number (3) of this section does 
provide
an exception when clearance holes are provided. It states, "On both sides of 
concrete
or masonry walls within 1 ft of the wall surface, unless clearance is provided 
in
accordance with 9.3.4." Section 9.3.4.5 indicates that no clearance shall be 
required
if flexible couplings are located within 1 ft of each side of a wall, floor, 
platform,
or foundation. This allows the clearance hole to be omitted but does not allow 
for
the flexible couplings to be removed. Flexible couplings are needed above and 
below
since a floor clamp is usually provided on the upper side of the penetration and
 story drift.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Proposed TIAs for Antifreeze - NFPA 13, 13R, 13D, 25
Comments due July 2, 2012
The following Tentative Interim Amendments (TIAs) have been  proposed to NFPA 
for
NFPA 13, 13R, 13D and 25.  They are being published  for public review and 
comment.
 Comments should be filed with the  Secretary, Standards Council, by July 2, 
2012.
 The links to the TIAs are in blue text below:
NFPA 13
TIA 1066 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13/ProposedTIA1066NFPA13.pdf]
NFPA 13R
TIA 1062 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1062NFPA13R.pdf]
TIA 1065 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1065NFPA13R.pdf]
NFPA 13D
TIA 1060 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1060NFPA13D.pdf]
TIA 1061 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1061NFPA13D.pdf]
TIA 1067 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13D/ProposedTIA1067NFPA13D.pdf]
NFPA 25
TIA 1068 
[http://www.nfpa.org/Assets/files/AboutTheCodes/25/ProposedTIA1068NFPA25.pdf]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVs0B6mQ1k_EEAbvlxc2UDi0f8swx7mezECrDDiTq4cdSfq_pBWNs1gW2XQOL6oq7MxXP8GmMK1c4d2p9IhxeOtbWh1ilr1Mb1kORhzvUYwIQ==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Printable Copy
PDF Version 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeUhKJgeL7J0S0bzZ4OShwo9M1UKK7sKeFpcuM6IK44hL1pcCJg2Aqoq2W3-bQzWUBqDP-cC1HSOqcapwjN85ILk3gTV7jATZyNrXueHMzn75A6RM8HMatbjHSF0XVNkPJrWmGpW_EAmW27ssh8ibzOxMy7EKik5SldgnWt5m3HzANkCYR_BVum5mIFSomi7_-Q=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeWsswben2tq2fe7xtiwf6S4qTvsna9yoXG35g91ixu3QsCXOAmJNeTGi4Wj4crXy35ty3OzwkKlRDslEKD5t2x_4Uwb6pB4Knf5c8BG_OLaoggnCe1Is630A0Afg23r4GcbrK-D76Uu2KpURrmVbv_azpFmJbzJ2ERfFyjhT9lz1g==]

July 23 - Aug. 3 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeWsswben2tq2fe7xtiwf6S4qTvsna9yoXG35g91ixu3QsCXOAmJNeTGi4Wj4crXy35ty3OzwkKlRDslEKD5t2x_4Uwb6pB4Knf5c8BG_OLaoggnCe1Is630A0Afg23r4GcbrK-D76Uu2KpURrmVbv_azpFmJbzJ2ERfFyjhT9lz1g==]
Sold Out!

Nov. 5 - Nov. 16

(click here for details) 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeWC7SMbpADh-4dUuvyxTV-acXGhQxcnN_yxrtnbM-fY9VbTqS2ZdT9OlbijMi9_KoUuTmtAeTSiyk0-7YxTaHmwdyUDzKYU7e0qsfJWjOj-zWzcGy7-0TvU_ULxcypQ2MitPzQPE2Gg8fCX-0Zdh9HgG9vhSEFLjtM=]

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVWoybn5aCxko7JalFrzU36niuPUW57pUhxV1X1iny-mW_IIhUuTgAp4bTjhSxkxPRhtN54X0orTKNv1P_fKGCxBIBh-8H2B3eLYcSpnIzuPk-9yq0LGTC17lubJ8eHQamC2bmly-d4in1QLEE23uZKSsGW5NGLH5lAH5PWMajWOdLpU8ve2jntkb7MGBI8mr4__sL1_FigZLmeG13vWmWz2-3fzNLMIOSTR0zZcI8JKtNvbQ2on-OArDvAdyU-ko3w57home8K7q1-N9GpsZ_Q].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeW_2_oc8YiiROVPYOCaHchp3TmLe4cf_42l7M1f6YokxV79YC5OsIAnShxO9qE7ipZ1QVFF3ZcEYKyqseEG4MNMlat0h4ZtnZhFfHuU3_qFaTRHmbh4m2_OMgeJvRWLxD1HH7lCoH4MZuudOu8sSgJevlCEVHL8Vds=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeUti5Pm0HrlImtiKwoFIlUhi-fUWy8COVhZiRMTRyHz7nuk1MxLYmjaLD-vtg8GDvMdBD_n4VE9f77pF-uULOlRSvybGG5bdAzMGhyabIFuBQ0aUOEvsupUQaiIXPZ4-W8dm9vxMNXDMff_qTHW0NBify42QDdGm2U=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVs0B6mQ1k_EEAbvlxc2UDi0f8swx7mezECrDDiTq4cdSfq_pBWNs1gW2XQOL6oq7MxXP8GmMK1c4d2p9IhxeOtbWh1ilr1Mb1kORhzvUYwIQ==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVWoybn5aCxko7JalFrzU36niuPUW57pUhxV1X1iny-mW_IIhUuTgAp4bTjhSxkxPRhtN54X0orTKNv1P_fKGCxBIBh-8H2B3eLYcSpnIzuPk-9yq0LGTC17lubJ8eHQamC2bmly-d4in1QLEE23uZKSsGW5NGLH5lAH5PWMajWOdLpU8ve2jntkb7MGBI8mr4__sL1_FigZLmeG13vWmWz2-3fzNLMIOSTR0zZcI8JKtNvbQ2on-OArDvAdyU-ko3w57home8K7q1-N9GpsZ_Q]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVoukhw_NfRpBCcInt18QSkFPaTh46spEf2H3S9-yWMYIoDQwpUVDiRNm_R8BGMp3CrqAQ-3-qdBSPAKHzW8cTxeUqepH6Yx0jAcDDFvpzJqN1Wym0rwjm11ao6gY_kXqf1JIKFZtLjLw==]
Fire Sprinkler eCampus 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeXtpjCgzJocHMxNP-JInUqpRiBTDcjhixvntBRnM_90G1CDGKaQYqK3aQEniqf5B0VK4vL36KqtfBrN_D5MaTwWUIntLw0OBGMPvb2AVZ2lCZjzVrhjaTlK]
   Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeVeZ1SUFc66C95vcVeXBvyHZmIez1ULey8D0PO5mjgDTtVjWx3-eWMhICGGkvyAi2DpH6OK2xjUy7TapeQpYQOn6dNNGS_O_2qGGPCWyzPPSWn0X1s2l9lGXxABJQpCxM1Ih-euvB1lYvt9OshsMI7j]
National  
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeU-TevHJ_mHK-2g1QjADRTn5r5sasUC73iKdz0pVfynvZZVfrE3PvAe1PBMGR6IFjqMSWisNnXCSlFKRMQN4uxT1LTRHaUVYv4vKOXozzklmQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeU-TevHJ_mHK-2g1QjADRTn5r5sasUC73iKdz0pVfynvZZVfrE3PvAe1PBMGR6IFjqMSWisNnXCSlFKRMQN4uxT1LTRHaUVYv4vKOXozzklmQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeV0tTQ9nalL8h6DiOyeZuZQcjSi5ovuMZqGZRX0QYCgt7VxWRDnml7hYOO7nWqUeNm9-o6KmJnWB2GtvZH4ZTY5MJ35XgJOVpvdA0cRckiJBzve1JLsmMa__q4GoPsMcpBxBocNihdLXSSfnFQg-bI4]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeXuoeqpU8UPTRMPnJT0Ize-h_FYrirG2ZJ3XxlHQ9PcE0BPqZttL7fUY_CY_GUxmqff5Q5Pe-dHkP0194pKxJZqFtV2Z7sermeGOqy_w4fkVp8fYcLkAdoSSCFCdNNW7p8=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=0016pKuzQzmzeUB6tsnIkORJ5pF5pH4w9paPJtNzev8eSZTMOZLeyDUBFuI9JqWJFU9anYITXhK9tycSEW5Qrt3JSloi33lhL9ycv4jcosT2Q_HmiGPHIgv631IsOlkaapL_W0Zis8bb2zk8xSycBJ53_gYS4LCg4WpC7ZG68uaiZ8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1110347090292


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0019NxJVM25myWIA3bL56yM7A%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0019NxJVM25myWIA3bL56yM7A%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to