Concealed Combustible Space Under Pitched Roof

"Is perpendicular to the slope up the slope or the other way? If I have 
sprinklers
spaced at a maximum of 15 ft up the slope, I would then space the sprinklers at 
a maximum of 8 ft the other way and calculate the heads at 7 psi. I'm not quite 
sure which way is considered perpendicular to the slope and which way is 
considered
parallel to the roof slope. I think parallel to the roof slope would be from the
 low point to the high point (peak) with the sprinkler maximum of 15 ft in this 
direction. Is this correct?"

We have reviewed NFPA 13, 2010 edition that you indicated as the applicable 
standard.
Our informal interpretation is that parallel to the roof slope would be from the
 low point to the high point (peak).

Your question indicates that there may be some confusion in the application of 
the
terms "perpendicular" and "parallel" to the slope in Table 8.6.2.2.1(a). The 
slope
is from the eave to the peak. In a concealed space with a sloped roof greater 
than
4 in 12, heat from a fire will migrate quickly up the slope instead of spreading
 out horizontally in all directions as it would if the roof were horizontal.  At
 normal light hazard spacing the heat from a fire located between rows of 
sprinklers
could go up the slope to the peak and the sprinklers nearest the fire would be 
slow
to activate, if at all.  The criteria call for the sprinklers to be closer 
together
to promote prompt activation of the sprinklers nearest the fire.  For example, 
in
an attic with A-frame wood trusses spaced at 2 ft on centers, the branch lines 
would
be installed perpendicular to and hung from the trusses.  They would be parallel
 to the roof peak.  If the 8 x 15 ft spacing option were chosen, the lines would
 be 15 ft apart along the slope and the sprinklers would be 8 ft apart along the
 lines.  This 8 ft dimension is perpendicular to the trusses, parallel to the 
line
of the peak, and in NFPA 13's wording "perpendicular to the slope". This would 
allow
one to choose a starting pressure necessary to deliver the density for a light 
hazard
design. If the sprinklers are spaced perpendicular to the slope greater than 8 
ft
up to a maximum of 10 ft, the minimum starting pressure is 20 psi. Regarding the
 5 ft minimum distance from the eave, the spacing can then be up to 7 1/2 ft 
from
the eave if the 8 x 15 ft option is selected. There may be some confusion in 
applying
the commentary in the handbook on section 8.6.4.1.4.3 for the sprinklers near 
the
eave. The commentary indicates that sprinklers are required to be installed no 
closer
than 5 ft from the intersection of the truss chords or the wood rafters and the 
ceiling joists so that, if the fire starts along the eave, there will be a 
sprinkler
close to the fire. The sprinklers located near the eave will also provide 
protection
for a fire entering the concealed space from along the eave. The commentary is 
referring
to the sprinkler spacing parallel with the eave as being closer together and not
 the 5 ft minimum distance from the eave.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Counterfeit UL and ULC Marks on Pipe Hangers
UL and ULC warn of counterfeit marks on fire sprinkler pipe hangers (Release 
12PN-33)
(Click here for a pdf version 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-1gpbcPLfFfW4d1iCulc0i_wMnvh7cG2DQ0N6DJuiFnEQ9GDlb2-Sk4bCYHCHvg4uDa7M8EkQm2Ls5CDSiTaGJy-BZjgl4SANziQWto0HQ-4AFxVfXVxCIzJqjPHFcfWAnvGblNgxrDTphhLpVrHD6FDHtaavl35fq0QBIofpIC9VeKUXbbqKFmmqz1kL2EFQ=])
Northbrook, IL - September 15, 2012 - UL and ULC are notifying distributors, 
contractors,
fire departments, regulatory agencies, and authorities having jurisdiction that 
the Fire Sprinkler Pipe Hangers identified below bears a counterfeit UL and ULC 
Certification Mark. The Fire Sprinkler Pipe Hanger has not been evaluated by UL 
or ULC to the appropriate Standards for Safety and it is unknown if the Fire 
Sprinkler
complies with any safety requirements.
Name of Product: ¾" AU-100
Identification: On the product:
The product bears counterfeit UL and ULC Mark and the following information:  ¾"
 (AU) in a circle followed by -100.
Photographs of the product with counterfeit Marks:
UL Press Release 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY9_qBPw_2dvrqdsnDH27En2-Xg8D956DlYlTNi1fHjBCZuox_GSC3fEsoAjgSSTSuQCC8TkkXNCrOB-buwN4xLsDkwMQJzleJ1DQw98qbo1T4xQX8q24KJp_YXguzO8s7uAgVW7bKSBUAEYUh8HS3FQF8jl6BNkyFty-VFbT7mc9wMEqsAQ3vuF4aCY7bXSW_gZtaBcfxu_ukKzAd_bmBZfSg96XsQTAxRAS6a1d5nnCiQbZWrjrZ19PkW9OV5A4dZOG2SvYvqPDLH5L3ZFkCQ0okrU4EBh2ORTq2sdOdEgSg1aom1_p2YkkUZz_2DZ8b38KrQ36D0756Huv4DvpHPzCg2jtB9z0WPrx8Q8wZE_JgnwfqDyqZWLRKl6C2JOJkQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY_Gx9ZVUNTvzZS0SoNfDF_-9aJj8S3IkDZ2oIpSfKmCTjiHLbDQCgA5cFSnZuOpk7_IRMsZZXfbDxoh0oe0GICeDRtr89jeKxQn0lMeugU7Qg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Download the PDF Version of
Technical Update
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY_qL7Lve6ljynrHOT2MBGzYYTsyjGKehokRPeuFbhXT3vQmGGUqEg6y6Tf-Vqr1FU21jyDf2fa78m-wPOfX2tzhsllCYZ4SVvRdGjG4uuCYhC9IUuCg3Mk66wwbp1rMiPBkOQ1AkiZQZGd9jctQJHMZt8hNMxNX58Rv8-xakOn1fJjYfqs7gSmV7XVk9LCsoa4=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY92iGN4pAAkkuOSoB_NZpmXCpJcv8fUQwIsNRmYVvZfqrYRL_Lc2EgAwlaJS8iX-srUzdf04wrAIiAxQzMki82TBBI8WK30-1I_2-K2IXUBXSlTtzFkH3QEBMQaZIc1QKZbGTEQFbDX7UVyjYv_dmQt6c6sTTwqPwUcW3JrZk6TvQ==]
Last Class for 2012

Nov. 5 - Nov. 16

(click here for details) 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-Cj8MQeznn3GaMjUkwhRKd6Y0nClB5EMG4sF0qpxm3kZPTQLUhC77U13yTS3Z7u0vu7CsAZYQu9c3R1e6XukcIOSgkRiZRzmCKdeg8AEIa2QYLleojGpeI3l6kmCOTlzn345SnLBxx6mUK0a7T1xAVYj6MLS5gu2M=]

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-st7E6kl1JKQaERcsyJicHG0l9HZm7YMRevyxzMtXH8rt1IEQw9OMmuTxQph2rIyoLYvivibR5K-KQsz9VKpqKeUyeAtK0iTU2afLOsyLWp4pFDU8Mw1H2jJ5m8i_Vs0wxQNgL3ybkOsxMFqtHySyX4IEKKv1INeLacW48-DAQa-dcVlfzUWHJV5OfThw6FuECqaFiYBV4DrVJvn2_U6Np4AYPXABgeuQqAVbE4PlB1tt3TqjMIvjOoDzUp1r3Wj2xONFjFIeo1g0vsPL1_oic].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY__2dayz3LSiOeGE1t3u_Uo7tiL2hLe_viWAfm6QxYNaPsn850iMVejN5ESaRJqRKST9xm3IHJ13AGOI-tby-bVGmJV1IkCoCMU_WFQnsbw4Y-u-HgcdPlV]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Antifreeze TIAs
TIAs on NFPA 13, NFPA 13R, NFPA 13D, and NFPA 25 on antifreeze issues. It is a 
single
document covering all of the TIA's and is located (along with all the other 
information
previously released by NFPA) on the NFPA website at:
http://www.nfpa.org/antifreeze 
[http://www.nfpa.org/itemDetail.asp?categoryID=2064&itemID=48038&cookie_test=1]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-0j_TUI6rGIYcfjGilVDH2C_YkOCWlPzBoTy_rB31eHSnBhFpnslk_LN3b0kuRywy6L01Lnyqk_7bqntC2kBzRBZe92pHHhJNAaPkyXVDuLntDhMSBmfQ1KL0gAaQtv8CxoWawI_LjgscCt9NSZTxK8CHlIol0u7Q=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY8cqRLMmaDf9kx7qA_awoV9NDeNhq_N5sHXnqejpV3dyMBE8dekh2HnvSg4egVN7OrHz3xNCBhK-8aXLSGbaVf-Hjd3DbdFXvZ62BuAQwrQHbfgE2nXGTIaz376GCMMZ7P69hrrUhuwYnbmOosz3bZNHkBHCsUxc-E=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY_Gx9ZVUNTvzZS0SoNfDF_-9aJj8S3IkDZ2oIpSfKmCTjiHLbDQCgA5cFSnZuOpk7_IRMsZZXfbDxoh0oe0GICeDRtr89jeKxQn0lMeugU7Qg==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-st7E6kl1JKQaERcsyJicHG0l9HZm7YMRevyxzMtXH8rt1IEQw9OMmuTxQph2rIyoLYvivibR5K-KQsz9VKpqKeUyeAtK0iTU2afLOsyLWp4pFDU8Mw1H2jJ5m8i_Vs0wxQNgL3ybkOsxMFqtHySyX4IEKKv1INeLacW48-DAQa-dcVlfzUWHJV5OfThw6FuECqaFiYBV4DrVJvn2_U6Np4AYPXABgeuQqAVbE4PlB1tt3TqjMIvjOoDzUp1r3Wj2xONFjFIeo1g0vsPL1_oic]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY_WRiiEYPf3jjqwtJc9INlFtaTz3t39_hUcGa3xwLuDK-8KdR23csg7swuHrn5N7if1Q3WQHtZWV8-Bvw8X8Tw5hG1-hXre7iKd0hv2_pFghjhjk30ORbhXp4BlYsJvmu8jwIiU4eIIsw==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-6Y87PTUmG4Xfd2kWOLoCq1ClyNccrbQfTR_lBYskUcD-abMClsBJ4KXfiKSVnuORNgNnPtzBpRKn8A3-ceu47bxDiaLaP-RVkzsDj46P8KZDpUaYX1qc99ewBPjITYxRBzGHpQhUiR_TmO8sVcEzi]
National  
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-t20z0oNx2q9aCLVwFBmnkqtZ8KNgve8VAuOpxOrfrmInv-X1icWW5j2aWlUZaJJP--rV5tEU_3_vIPbsGpVJ7Ee4ivbF_tA6JfK95dUydTw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY-t20z0oNx2q9aCLVwFBmnkqtZ8KNgve8VAuOpxOrfrmInv-X1icWW5j2aWlUZaJJP--rV5tEU_3_vIPbsGpVJ7Ee4ivbF_tA6JfK95dUydTw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY8PLcnOq-A2f9DrL3X3qLdtch6bKpipbLcBlIcl0v0_ZCHdbLws59OoIB_sFV9AUaaTFfnlnumwPZVhlcx1kIkCrOrjK51Vq5DZChAlbOox4a3v8eUmjX-1aDVduWk1-GV8AjN9z6iVakiTiiSpl82i]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY8MbQIn_e6Dx-aCgL5ijFWCg8CKA70RpcuF1MTNUWY-NyTlGdpl6ihT8kUU62mwf2H_Rr7RYW5gkJZwPXyKwSGWR8U1cR2Wvi7iE9CProbs_kahYp4deYXaJtejXmNLwCw=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001yDBItY4KoY_Z1RK9PWgQ3htdZe3vKi4uOy3VXHILbo0xuqMfJWaSj8gw9hHUFVf4uqZtO95bG2o5A2lswGWMyMyWRgZGTR0xzLpOsDrtF-RYL-ZcuaLBqMOpX5i6GTS4IH6AiZPoRCpkr5N70v2NzflQbpbiNaiSQuLko7H_WrM=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1111022830315


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001goXqIYmsv4u6LGQVZfduLQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001goXqIYmsv4u6LGQVZfduLQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to