AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

March 29, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Only New Sprinklers Shall Be Installed

That is a base requirement that has been in the NFPA 13 standard for some time 
in
Section 6.2.1. New material in the 2013 edition says that when a sprinkler has 
been
removed for any reason, it shall not be reinstalled per Section 6.2.1.1. The 
handbook
commentary for this new material says that because of concerns that sprinklers 
could
be damaged during the removal process, this requirement was added to the 2013 
edition
to clarify that when a sprinkler is removed from the piping it is to be replaced
 with a new sprinkler.  When a sprinkler is removed, damage could occur to the 
water
seal and operating element, specifically a glass bulb type element, which could 
impact sprinkler performance without any visual indication.

There is a contradiction in the handbook commentary regarding the re-use of 
sprinklers
under Section 6.1.2.2. This section addresses that reconditioned sprinklers 
shall
not be permitted to be utilized on any new or existing system. In the commentary
 is a frequently asked question (FAQ) - "Where can existing installed sprinklers
 be utilized?" The commentary response is where sprinklers have been installed 
in
a building on a temporary basis - for example, prior to finishing ceiling work -
 such sprinklers can be moved to the new location after finishing the ceiling.  
Another example of where an existing installed sprinkler can be moved is during 
the installation of a new ceiling underneath an existing ceiling, provided the 
sprinklers
are of the proper orientation and the associated hazard has not changed. This 
commentary
has been in the previous editions of the handbook. When the committee took 
action
regarding Section 6.2.1 that only new sprinklers shall be installed, the 
commentary
material may have been overlooked during the editing process and was not 
removed.
The proposal stage for the 2013 edition of NFPA 13 attempted to provide guidance
 when sprinklers can be re-used. The re-use of sprinklers was opposed by several
 comments during the comment stage resulting in the new Section 6.2.1.1.

The bottom line is, "only new sprinklers shall be installed".
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF17e6BWmiGgiISgQyy4Xv799eTbcISHkoPfMsD9kbFq1_gD6wby3v37wKTC1ZhbcVXJtRfsRhIiO5VCp5pqrfBj5BEWsuAepAu2B3XoMYByjg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF3I0ZRls9trQW7ecaJV_xP1UGDNovRdo9MW_da4aqiWzAk1sTP3-NnPGpmX_4_CCxLnQ1-OaluM-4-fmFWK59Cm2l0-Nlb-UzKBCjzin_bX7hvg2S6J7E3diaf2qC1TSwsgfvy2nngpb4lepIHvRid_w-3IXKRhJ3l2Gbu6u47c9cxFvfTkbJOVFAG73CQE3d0=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Webinar
Bob Caputo
to Present an
AFSA Webinar on
"Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13
Part 2 - Installation Requirements"
Wed., April 17, 2013
Free to AFSA members!
Register Button 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF2X2DtGyaVIQGB_jE8LcRBSp9sywFXLhGt53vTBw43JBSiGF-OSRnAjJ_MOcZDXQF70OwXm47mmyQ01PaRpKgfWeEnX5c7V7bxxRRxMaowkBqtCyAJcuOuzop8v1s-TpEJAvcfznLYxB2r6nUHDaXKi]
For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF0gUlABJ1cDCBc1FlVk8Y2aREScYaxS0OkRV9iad8zpxhb-SN-xmlKqR831qxwmccZJSUJ8dVkOuWe9d0IooRB42ZhBZ8AxwT7SXY96ReCiEP9RpwYuIomq0I-GW18dHtKogyymCjhQavqxInMWgGph6dbplmB_JOIGeKOJim73icfSqujvDI_CG9hf5rbTf8KuGJ3gVDes7fWOmG54dVpIxf1ja3wWcOLF3LkJ6ZjClt_hGM9WXmhV8JDK5nxBW-339ZZrDqEFBIdVvQrb5Wcb].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
May 13 - May 24, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF0gUlABJ1cDCBc1FlVk8Y2aREScYaxS0OkRV9iad8zpxhb-SN-xmlKqR831qxwmccZJSUJ8dVkOuWe9d0IooRB42ZhBZ8AxwT7SXY96ReCiEP9RpwYuIomq0I-GW18dHtKogyymCjhQavqxInMWgGph6dbplmB_JOIGeKOJim73icfSqujvDI_CG9hf5rbTf8KuGJ3gVDes7fWOmG54dVpIxf1ja3wWcOLF3LkJ6ZjClt_hGM9WXmhV8JDK5nxBW-339ZZrDqEFBIdVvQrb5Wcb].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF3FPxgFgapAUrLI5lhknqvqR6bwDSCEC8PRRPPOb7eA6nsF6wqII0mFceepS8b0UYS-Ysn3YgMN8LUIJw5XyOv4guhKIF5wsnF2uiCik8i6z4FSWiJT_TjX]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF2c3DSyeUUgwN7VMdB2rzxQ-ejU-ksB6GuRcwJdfjyKmWKDsAHrqK0z5xySKUzXT8aM60DMrWXRrHz_tJXHC1PrWo8EzhkYDxsVbDjlV7QjfyrsE0qaVZlRE0vTZzye0UQgNxhWJXfl_8pCxAVbD0T7yNQwJPFm0uU=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF0hCw6cs3CErrDXEVrxfbXdtDFZXw1oYlRKZnaPIROsb72u4Iav28BqEUYiQzU6knbeTkdRHlOupPO26rQrMqKfM7ZlKmaWR4e9fjqEBnyyEwsOG6TdrCkj58g25CaYNE4fKakupzGegYywyzriURcbXbQjAXGpvLY=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF17e6BWmiGgiISgQyy4Xv799eTbcISHkoPfMsD9kbFq1_gD6wby3v37wKTC1ZhbcVXJtRfsRhIiO5VCp5pqrfBj5BEWsuAepAu2B3XoMYByjg==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF0gUlABJ1cDCBc1FlVk8Y2aREScYaxS0OkRV9iad8zpxhb-SN-xmlKqR831qxwmccZJSUJ8dVkOuWe9d0IooRB42ZhBZ8AxwT7SXY96ReCiEP9RpwYuIomq0I-GW18dHtKogyymCjhQavqxInMWgGph6dbplmB_JOIGeKOJim73icfSqujvDI_CG9hf5rbTf8KuGJ3gVDes7fWOmG54dVpIxf1ja3wWcOLF3LkJ6ZjClt_hGM9WXmhV8JDK5nxBW-339ZZrDqEFBIdVvQrb5Wcb]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF2usuN8f6UBHVPX4dJ7ou8Dfbnhxj-PdbdkoWzxpx1whjPOKoma3xlWUl5o_iMgBA6MWOFbUw83WUPhzrBDRbXMUXDmFveKivTrGGT16HxQ3FraRl_jvXg_IaMFrsQwyQ8ee63aVkHicQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF3dq_fNgFWURmqbJBF2LV0FA_0Tvo5_KlX7qfyZNT1TQX3qA4-w3_ARxyGuQ4_FYjbsYs1Ke2Y2lZpH_eCOLdzNUQdMMN1BOMUfDZFJ0OB0SUOtG4ggqgzXYXAjnVKmyYFfBXpV9jb9RIKLhk_b1Yf6]
National  
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF1E9IoP-9VVDOR7Eewvs69z5FCabBQI2EMcysiJOy1xGQLrvV9L7HTfp_8KW7J9M_1M41F_s2wshpNkY0Wbf1J_9tBMXU9UdejI-pXSdwuBUQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF1E9IoP-9VVDOR7Eewvs69z5FCabBQI2EMcysiJOy1xGQLrvV9L7HTfp_8KW7J9M_1M41F_s2wshpNkY0Wbf1J_9tBMXU9UdejI-pXSdwuBUQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF0PzQ6IgsYpSRrWC9yCJGBdkxM8kMm3ezT2wfdgcxgf0xwwkBVzbIQHWVPPpgqVKelH_FsJQ2DqxAJXNNdcRppF0nqigVyB7cN1sgQIsfgIC4Coy77Z7bPeGxAw0iPUKX0WWbdk_GePGunlYcssASM-]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF3mFTgacFFXQI6_a7vQu2ylNIf2UeBiSMhTUd7120o2Fp8VTIQk_4tChNPGYaBtYkEMYV_DqGVbr0QFkkUUA8zo3IjiIcldph9HWLrxqBN4Yo7hlzV7cs2S1s1lmx8SEx4=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001pWWWgf5zMF3doX0yYHlyziC7rQJk5UX5nv4WKbY4XISNR6mLcgUiTOpE95_EN9GEc_ossrvaGPbPvPg92pLOzZZzE9qSHRMG5iXHfycjCcTA76c0H2Z6xR1ZH655-SEG20dfOp_RGNCENdDF4neFjBgIjRrW5nJfP0v98-gKNRw=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1112886015236


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0015GKbGhoBxk5ojNU35U9gsw%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0015GKbGhoBxk5ojNU35U9gsw%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to