American Fire Sprinkler Association [http://www.firesprinkler.org/] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ A newsletter dealing with codes and other technical issues May 24, 2013 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ NFPA 13R Exterior Corridor "I have an AHJ quoting the 2013 NFPA 13R referring to the open walkway and is saying that sprinklers are required since it is a balcony. What is your interpretation of this requirement?" We have reviewed NFPA 13R, 2010 edition that you indicated as the applicable standard as well as the 2013 edition. Our informal interpretation is that sprinklers are not required in the corridor. The 2013 edition is very similar to the 2010 edition requirements. The 2013 edition in Section 6.6.5 is explicit where it states, "Except as provided for in 6.6.5.1, sprinklers shall not be required in any porches, balconies, corridors, carports, porte cocheres, and stairs that are open and attached." The annex for this section says an example of an open corridor, stair, or breezeway is one that is exposed to the outside atmosphere (temperature). Another example is an exterior wraparound corridor that is typical in a two- to three-story motel. [See Figure A.6.6.5(a) through Figure A.6.6.5(e).] The 2013 handbook commentary says that since NFPA 13R is concerned primarily with providing life safety by way of affordable installations, these exterior areas are allowed to remain unprotected, while still providing an acceptable degree of building protection. Protection of these spaces requires some sort of system that is sensitive to freeze protection in many areas. Providing a dry system, antifreeze system, or listed heat tracing system to protect these portions of the building can add substantial cost with a limited return in life safety. It is understood that this standard is used in many areas where freezing conditions are not an issue. Based on the statistics provided in Table A.1.2, the limited number of fatalities caused by fires that start in these areas does not warrant the sprinkler protection being required in these spaces. Owners can require that their design professionals incorporate sprinklers into these areas, if so desired. The new 6.6.5.1 in the 2013 edition also states, "Where a roof or deck is provided above, sprinklers shall be installed to protect attached exterior balconies, attached exterior decks, and ground floor patios serving dwelling units in buildings of Construction Type V." The handbook commentary under this section says that the committee has made a major shift regarding porches, balconies, decks, and ground floor patios serving dwelling units in buildings of Type V construction. Type V construction applies to the entire building, and not just the construction of the balcony. This rule applies to the exterior or "open" spaces accessible only from the dwelling unit itself, and not a corridor or breezeway that is shared among multiple dwelling units. The previous sentence provides a key statement regarding your question. As such, sprinklers are not required in the corridor. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ NFPA 13 Public Inputs Due May 31st NFPA is soliciting input for the 2016 edition of the NFPA 13 standards. The proposals can be submitted using a Word document form or online. NFPA 13 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13] - Standard for the Installation of Sprinkler Systems NFPA 13D [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13D] - Standard for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes NFPA 13R [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13R] - Standard for the Installation of Sprinkler Systems in Low-Rise Residential Occupancies NFPA 24 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=24] - Standard for the Installation of Private Fire Service Mains Other standards accepting public inputs with later due dates: NFPA 14 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=14] - Standard for the Installation of Standpipe and Hose Systems NFPA 15 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=15] - Standard for Water Spray Fixed Systems for Fire Protection NFPA 20 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=20] - Standard for the Installation of Stationary Pumps for Fire Protection NFPA 291 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=291] Recommended Practice for Fire Flow Testing and Marking of Hydrants ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47wVnIpLDlynSo6OyoQhyCX9no63h4tg7adSidjornOsiv3t5D0DO6LRVUuoCMC16AQnj9JY9uC5DnqITftLtB5Y3qsTS8_o42IBEkxOWpGPRH8vnqaZmzpd] Hosted by the American Fire Sprinkler Association ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered in fire protection engineering. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright 2012, American Fire Sprinkler Association. All Rights Reserved ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ PDF Version PDF Link [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47xvHFfmtKphJehM-wmOGZSfHFanLlEByIr_2_l_5oZvX8xk6HFMxj8x3ftpei1Y5c81msTC45pnauFuyiXSrpXi_p7VFNCRQA8iG_mjLM2ZqF_rMdat9TxzFcCGYw5hGvrsrSQ9bZja1sYpUacmPMYW2FiiX0w1I8JwIPrw4U71TQxxmWZv4Nz-rzBxYUgXwGs=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Webinar Bob Caputo to Present an AFSA Webinar on "Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13 Part 3 - "Residential Sprinkler Requirements" Wed., May 29, 2013 Free to AFSA members! Register Button [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yaXO16p2Bh3Bd1CUIBvud7QI7uwso1B1KL3DgRe7sJkYwAr1fImJGwNJnsD1PAPiXwl_eWL1s31HJ_rygfaxtg4HDzAI_YcVvMiBq281A224wcgcpOxJUut5LWd2tQV9SPqOgVahA1V3UhLTMsp9bZ_-lC2SwfP4o=] For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yUugJ1KmBCf2cYFMtnUCwczfux4LPBGOhTETiER84c-EXSWIUCNJzn5TrjGwcFIMCRQnbgr2R7fejKhezZVY1yI0iz9ROm5f0Ubx81aqOOjbsqnzmcuGRAaDEybfg_j9Afh5Psc-fGUu4Naurf_S8wbog9_hTefNiMWu_p93XuUCV4UqQZa9ARDo2W-t_TivgB99e7agDR8S0V1zqo7GP6fWEr4gS6QtBaJr781gi6slzcgzs0eAE8mA37-1bn7Fhp6r3GDVG7Qc1w684E8etm]. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Calendar AFSA Beginning Fire Sprinkler System Planning School July 29 - August 9, 2013 Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yUugJ1KmBCf2cYFMtnUCwczfux4LPBGOhTETiER84c-EXSWIUCNJzn5TrjGwcFIMCRQnbgr2R7fejKhezZVY1yI0iz9ROm5f0Ubx81aqOOjbsqnzmcuGRAaDEybfg_j9Afh5Psc-fGUu4Naurf_S8wbog9_hTefNiMWu_p93XuUCV4UqQZa9ARDo2W-t_TivgB99e7agDR8S0V1zqo7GP6fWEr4gS6QtBaJr781gi6slzcgzs0eAE8mA37-1bn7Fhp6r3GDVG7Qc1w684E8etm]. e-campus_logo [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47zf3eNDqVgfAxfIV4M0_V5lLDqbOzIUiNrZwhrKGDvyPlIYNw00HCOihP3D6B_NvlUccD6sGD6Ca7TXtUXd2UlkrncfqzwbXwK756v5l8BeatA-1tzCiWCt] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Free Subscription to Sprinkler Age [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47z_SVwx6R9CSr2MROf6mI3U3trQ6NKhlBoL6110dpK1WWyVmbRUYNE8TjStVsxig0REib5iJVy-9o4wd8nCuyF-hBDy8s36xrdUWxqfXHGzoH0EiMAleozL1OLEojDBBT_wUaOdrOMEj0eKOdMb_2vWf-QdJ_Z5Wy8=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quality Contractor [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47x7hvDdgqhgJxKurXx5LAnE0UT7iQB0A89U5-KBnfWouLTfZ0zCQgDoaqIYdoTykY1Nj7aEdLhepOqVBcTr5M16OeviFug_bILxF1KyiUOK_L49g72A7wRNVGSWSAnshsGACDdOinEwAfEjc-_ybgyL94MFY4WdRhw=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quick Links Firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47wVnIpLDlynSo6OyoQhyCX9no63h4tg7adSidjornOsiv3t5D0DO6LRVUuoCMC16AQnj9JY9uC5DnqITftLtB5Y3qsTS8_o42IBEkxOWpGPRH8vnqaZmzpd] AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yUugJ1KmBCf2cYFMtnUCwczfux4LPBGOhTETiER84c-EXSWIUCNJzn5TrjGwcFIMCRQnbgr2R7fejKhezZVY1yI0iz9ROm5f0Ubx81aqOOjbsqnzmcuGRAaDEybfg_j9Afh5Psc-fGUu4Naurf_S8wbog9_hTefNiMWu_p93XuUCV4UqQZa9ARDo2W-t_TivgB99e7agDR8S0V1zqo7GP6fWEr4gS6QtBaJr781gi6slzcgzs0eAE8mA37-1bn7Fhp6r3GDVG7Qc1w684E8etm] Buyer's Guide [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47zbPylGX8yWXsr5m3HpC-jB40a-T2ZD5FxDcBXUQiAin80ZZZPzYkf5eoTFFz4taB2bpsSkvhWWA2NcT9MYB9eh-c7IGcU6zoFlQVn8BLqogPoadPNPfylAPG-AqmlGqwwROHm8ZFhKUUrXkIwXuL3-] Join AFSA Video [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yR8a852t4l8xjrWDZEAX1xsZJpHjH2E202aJYyjvR2-8rNL3bp9DSGg7UnJ6SWKwr1dZAtCuzb-eVxzHv3sV6QqUShxamNuR4FXD1myeAvjnm--06880hsL4V5e1StE67m1dTQdv4DnHBRQ3_Wh3MIX1aZwUGmqz8=] National [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47ySywUmbC9C1ukw2DdOXTNjPtJPlOzl8cTmr3Jh7Bp3V255yoAkskpci00Q_XqvHYHyxyLgr1ZRFio-CaXfVOJKT8NgThw1MlGv5m1rSbEg4ykd-eiaEGE4] Scholarship Contest [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47ySywUmbC9C1ukw2DdOXTNjPtJPlOzl8cTmr3Jh7Bp3V255yoAkskpci00Q_XqvHYHyxyLgr1ZRFio-CaXfVOJKT8NgThw1MlGv5m1rSbEg4ykd-eiaEGE4] OSHA Alliance [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47wt8_rXY9Lx65gnSaR1Aroo485KrDDSEeieuxKrjkRok35L8OxVpcSHvO0dOKtpmoCvRpLgSn8MjfV6ZNZqzErW_g_Atc6vrT_5fJeSSV-cFNuRtbZKVQZSnJusn0RvASlcNmcD131XQr5FAmI7chxi] Technical Services [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47yjk_IZLUvQSKTSIgWJMjvgzXlfXFWtZd4zObdSYJ-nXt9SdlgAf7OuQKBrZEPw5UsO5MDXEBMXc6ZD1S2sLNoj6TDNkX6BcmmWxFk1D8wZQboZAc0Go0ueSYgUnou2IBrRHizozcWB4g==] Informal Interpretation Request Form [http://r20.rs6.net/tn.jsp?e=001CqJNcvaX47zN5uP9TtAw8svY2s64PkI37JgHW8DzjTIaHT1G5TBvm87PPwlpudfYLYNMKXUZcEfUZIfTfeNQOnuZBzDdl5FNCThhYs6HhX_gP83VPmXvSL9Edoo2dtF1qn2DVgHFint_GRr7hu42aeW9ClRS_d97LMl5U_ekX1c1796xBu5r8g==] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Join Our Mailing List [http://visitor.constantcontact.com/email.jsp?m=1102312387686] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Forward email http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113558701926 This email was sent to [email protected] by [email protected]. Update Profile/Email Address http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001xX5XSa-g7ZEhF5_q0WSwUw%3D%3D&llr=gdnaptcab Instant removal with SafeUnsubscribe(TM) http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001xX5XSa-g7ZEhF5_q0WSwUw%3D%3D&llr=gdnaptcab Privacy Policy: http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp Online Marketing by Constant Contact(R) www.constantcontact.com American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | TX | 75251 _______________________________________________ Sprinklernotes mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org