American Fire Sprinkler Association [http://www.firesprinkler.org/] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ A newsletter dealing with codes and other technical issues May 30, 2013 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Recalled Sprinklers "Does NFPA 25 require recalled sprinklers to be replaced?" We have reviewed the 2008 and 2011 editions of NFPA 25. Our informal interpretation is that recalled sprinklers are expected to be replaced. The only guidance in NFPA 25 exists in the annex: A.4.1.4 Recalled products should be replaced or remedied. Remedies include entrance into a program for scheduled replacement. Although NFPA 25 2008 edition has a Section 5.2.1.1.6 regarding replacement of recalled sprinklers, that section was suppose to have been removed from the 2008 edition by an errata. This was submitted as proposal 25-62 and accepted but then rejected by comments 25-10 and 25-27. In other words, it was never part of the official 2008 edition. Although a simple issue (when viewed through the eyes all parties being interested in maintaining the reliability of the fire protection system), one must first recognize that NFPA 25 is written to the owner of the facility with the expectation that the owner will likely hire an inspection service provider (contractor) to perform most of the activities. The contractor is not capable or expected to perform all activities. Although typically skipped over, Chapter 4 is a critical section. As the title of section 4.1 Responsibility of the Property Owner or Designated Representative tells us, this section addresses what only the owner can do. Our guidance in the annex on recalled products is located in this section. Allow me to also say that designated representative is not the contractor but the occupant of the facility that has been given the authority to act overall in place of the owner. When a product is recalled, it is broadly published as required by the Consumer Product Safety Commission (CPSC). The owner's responsibility (as applicable to all other components within their building) is to address this issue when the recall takes place. It's also quite likely that the inspection service provider will inform their clients when recalls happen but it is not the responsibility of the contractor to find these products as part of an NFPA 25 inspection. The bottom line is that if the owner has little interest in maintaining their system, there is little that the contractor can do about it. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ NFPA 13 Public Inputs Due May 31st (This Friday) NFPA is soliciting input for the 2016 edition of the NFPA 13 standards. The proposals can be submitted using a Word document form or online. NFPA 13 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13] - Standard for the Installation of Sprinkler Systems NFPA 13D [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13D] - Standard for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes NFPA 13R [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13R] - Standard for the Installation of Sprinkler Systems in Low-Rise Residential Occupancies NFPA 24 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=24] - Standard for the Installation of Private Fire Service Mains Other standards accepting public inputs with later due dates: NFPA 14 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=14] - Standard for the Installation of Standpipe and Hose Systems NFPA 15 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=15] - Standard for Water Spray Fixed Systems for Fire Protection NFPA 20 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=20] - Standard for the Installation of Stationary Pumps for Fire Protection NFPA 291 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=291] Recommended Practice for Fire Flow Testing and Marking of Hydrants ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001K2GElqICn11c9MXgkBmSirHEo0Vkl9el-ESJqiJs2qxded_m4VHYPc-dSkJ5pmmEfDI6-L5SyOFA7a-AlYS2ES3enKcYHz4D6pk9c_baP7drEobVl4deC3NhTiZWzzPp] Hosted by the American Fire Sprinkler Association ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered in fire protection engineering. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright 2012, American Fire Sprinkler Association. All Rights Reserved ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ PDF Version PDF Link [http://r20.rs6.net/tn.jsp?e=001K2GElqICn11iJNIpaVS2QpKC9_Dsv1COI5w39RSRIUmSJgq28AwVCrxLbgSaoQFuMlSNhpTJdPwY-mSEB9gH0XW8DspScv9S3koqxDbFNmB7HSbzElButiZfBZgkHAo-JNitCY0eh-nlq67WGOPDbAtVpaCk1eEuIsZVgZjADgSeVgxRCttHmNL-ydi-v1qJnghh9NBf8cY=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Calendar AFSA Beginning Fire Sprinkler System Planning School July 29 - August 9, 2013 Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001K2GElqICn114dWOJ7n01tdPVN-ZnKz3SqYpxq8NmVfQ8L-HahOeOUnlNBTHTpmTeQ7qbwtCAK_HUuLvYZ8KkiOkgaQHeQxPZsI6RHmS9elsQvj4Vwg_9OLP6523ksYDWLlIDSeUwgBnaQp_D22PUY-cuXF1H-aSGot9I3TQ8cVtgTnJeLTHXQKOxJUsyrO8-9na4q5f_ARcdos1R9_EfI3fUEpapCLBLr--vEp3_7B_ObeVXgR6wydqMBo6LtnLICxicmq7aXmJCj3zkhz-bU6Mm2yRou8ed]. e-campus_logo [http://r20.rs6.net/tn.jsp?e=001K2GElqICn13oEn_CMWa_-OgR56LKLl4_ZgYi7ipANEu7pQAaVOh-3WP_cmSC-We8ZtpzMKAhojTZSn3Ue-znddJxDI7G8q5Nb3iDr48EnU7JLs6tfNx9fmTtsBK7PIUg] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Free Subscription to Sprinkler Age [http://r20.rs6.net/tn.jsp?e=001K2GElqICn11eaCm0ms3XCvGmqohAyvrkdC7MDGJ5TaTZkVbt98LAPx7w_D7WrogrtF6dQWZ_RKrITBnE2CQNpgfFtgOF7nQuVSnIpKPab6JKIVG-4Z3sK40FxOYH4XGXKPFhBXK6xHVnUXBMJlKcRp_pMKyrmZE_fav5MGHds2M=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quality Contractor [http://r20.rs6.net/tn.jsp?e=001K2GElqICn10gSdgd5mJDK2X5lZS8DDji5JsMqC2jdwcb_S_rDwouE9-saxARwjUXL_p7XLwlp5A2sei-7BJjxsoLw8InHfOm31_qEAQ8RcOQdru-ghpTF8pyGnojJ_HNzwPaFkB0Lzoyrwzqg54JkV5V4QZBFn7h_x2bCvGa7GY=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quick Links Firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001K2GElqICn11c9MXgkBmSirHEo0Vkl9el-ESJqiJs2qxded_m4VHYPc-dSkJ5pmmEfDI6-L5SyOFA7a-AlYS2ES3enKcYHz4D6pk9c_baP7drEobVl4deC3NhTiZWzzPp] AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001K2GElqICn114dWOJ7n01tdPVN-ZnKz3SqYpxq8NmVfQ8L-HahOeOUnlNBTHTpmTeQ7qbwtCAK_HUuLvYZ8KkiOkgaQHeQxPZsI6RHmS9elsQvj4Vwg_9OLP6523ksYDWLlIDSeUwgBnaQp_D22PUY-cuXF1H-aSGot9I3TQ8cVtgTnJeLTHXQKOxJUsyrO8-9na4q5f_ARcdos1R9_EfI3fUEpapCLBLr--vEp3_7B_ObeVXgR6wydqMBo6LtnLICxicmq7aXmJCj3zkhz-bU6Mm2yRou8ed] Buyer's Guide [http://r20.rs6.net/tn.jsp?e=001K2GElqICn13FZrZlRcnW1HaHQKk_w7o9yhuF1XhPaDrPMJ85L2d0EaXGmam6NXk9vz4CH77mKDZMjMcn68pOqLKm8v6lyVwX6aKEYYbOy89y01klgp6shj6zsvV7YoYsF0bLh0hWVcvJx6ddpaxfpMmeM9KI80MF] Join AFSA Video [http://r20.rs6.net/tn.jsp?e=001K2GElqICn10DfMqcKB-Z6ahq4xCORMu7ljn1kjnUTlLRyne__U2g6p5idcbB3lS8vK3hvb9tEZllwaG0io55ALiYR30_pycGO4uas06KF2NCKj_0qceFNeJg97P5sUvxt7NvSx5wrZtKVIhwyLbuHTEhUrEPDIcin5GXMUjhPnQ=] National [http://r20.rs6.net/tn.jsp?e=001K2GElqICn10smTiPHatTvEGb8u089ENWJSOPYntFF6eUJAxIcE0Y1rF4CvBlf97AnPRk1NYWRHCG53b3uGgtvw0dlVO5kjz4FHfGtThxOcAKbDHCM1iReGuVq52phrdH] Scholarship Contest [http://r20.rs6.net/tn.jsp?e=001K2GElqICn10smTiPHatTvEGb8u089ENWJSOPYntFF6eUJAxIcE0Y1rF4CvBlf97AnPRk1NYWRHCG53b3uGgtvw0dlVO5kjz4FHfGtThxOcAKbDHCM1iReGuVq52phrdH] OSHA Alliance [http://r20.rs6.net/tn.jsp?e=001K2GElqICn11_iMCAAkQM7tSI-S9gWXUENuT2xmpFLHfnE1tYZEnzo3-ieB_Ie8uzvKsST62GlU33skk8bLFJT_pbFovX9fnwm4kInp_7KnBCqZtwELNpyXj2WRUkGCPVak9Q5AkuedjVlFtSAgficQs9MUsOqwjh] Technical Services [http://r20.rs6.net/tn.jsp?e=001K2GElqICn13Yt8pr75h3B6QHc-ac5ZauGX9VfIMRISb_bqhwtjrgP9kHXNGPpHRFUduLoqFvL0SjvOUyG2P744zzrOCEQJOgW5LNTX-koqEMPh2NyNiLnW2GLLqxi5n8H0BFzXryt5iCTkUjPn7jkw==] Informal Interpretation Request Form [http://r20.rs6.net/tn.jsp?e=001K2GElqICn13rkK2H1c7D8TlD2fGvo0vrY2HGMBEditB7XydFjvKX6JyBTuia1eA09ijA4zxCOvrz7jPFym4Uu5OBIaEJGOnuIZgZoLAoLHdMH_5RJpWOcUEOQUzqHWBLMKn3gVDDi84QcjFHygtKGoiqIs8pOdE2tv6j8TyYA-3kQ5TFBXVRAw==] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Join Our Mailing List [http://visitor.constantcontact.com/email.jsp?m=1102312387686] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Forward email http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113617500031 This email was sent to [email protected] by [email protected]. Update Profile/Email Address http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001kuuO2qKf8-mKARbkc4-Mbw%3D%3D&llr=gdnaptcab Instant removal with SafeUnsubscribe(TM) http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001kuuO2qKf8-mKARbkc4-Mbw%3D%3D&llr=gdnaptcab Privacy Policy: http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp Online Marketing by Constant Contact(R) www.constantcontact.com American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | TX | 75251 _______________________________________________ Sprinklernotes mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org