American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

May 30, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Recalled Sprinklers

"Does NFPA 25 require recalled sprinklers to be replaced?"

We have reviewed the 2008 and 2011 editions of NFPA 25. Our informal 
interpretation
is that recalled sprinklers are expected to be replaced.

The only guidance in NFPA 25 exists in the annex: A.4.1.4 Recalled products 
should
be replaced or remedied. Remedies include entrance into a program for scheduled 
replacement. Although NFPA 25 2008 edition has a Section 5.2.1.1.6 regarding 
replacement
of recalled sprinklers, that section was suppose to have been removed from the 
2008
edition by an errata. This was submitted as proposal 25-62 and accepted but then
 rejected by comments 25-10 and 25-27. In other words, it was never part of the 
official 2008 edition. Although a simple issue (when viewed through the eyes all
 parties being interested in maintaining the reliability of the fire protection 
system), one must first recognize that NFPA 25 is written to the owner of the 
facility
with the expectation that the owner will likely hire an inspection service 
provider
(contractor) to perform most of the activities. The contractor is not capable or
 expected to perform all activities. Although typically skipped over, Chapter 4 
is a critical section.  As the title of section 4.1 Responsibility of the 
Property
Owner or Designated Representative tells us, this section addresses what only 
the
owner can do.  Our guidance in the annex on recalled products is located in this
 section. Allow me to also say that designated representative is not the 
contractor
but the occupant of the facility that has been given the authority to act 
overall
in place of the owner.  When a product is recalled, it is broadly published as 
required
by the Consumer Product Safety Commission (CPSC). The owner's responsibility (as
 applicable to all other components within their building) is to address this 
issue
when the recall takes place. It's also quite likely that the inspection service 
provider will inform their clients when recalls happen but it is not the 
responsibility
of the contractor to find these products as part of an NFPA 25 inspection.  The 
bottom line is that if the owner has little interest in maintaining their 
system,
there is little that the contractor can do about it.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 13 Public Inputs Due May 31st (This Friday)
NFPA is soliciting input for the 2016 edition of the NFPA 13 standards. The 
proposals
can be submitted using a Word document form or online.
NFPA 13 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13] - 
Standard
for the Installation of Sprinkler Systems
NFPA 13D [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13D] - 
Standard
for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and 
Manufactured
Homes
NFPA 13R [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13R] - 
Standard
for the Installation of Sprinkler Systems in Low-Rise Residential Occupancies
NFPA 24 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=24] - 
Standard
for the Installation of Private Fire Service Mains
Other standards accepting public inputs with later due dates:
NFPA 14 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=14] - 
Standard
for the Installation of Standpipe and Hose Systems
NFPA 15 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=15] - 
Standard
for Water Spray Fixed Systems for Fire Protection
NFPA 20 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=20] - 
Standard
for the Installation of Stationary Pumps for Fire Protection
NFPA 291 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=291]   
Recommended
Practice for Fire Flow Testing and Marking of Hydrants
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn11c9MXgkBmSirHEo0Vkl9el-ESJqiJs2qxded_m4VHYPc-dSkJ5pmmEfDI6-L5SyOFA7a-AlYS2ES3enKcYHz4D6pk9c_baP7drEobVl4deC3NhTiZWzzPp]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn11iJNIpaVS2QpKC9_Dsv1COI5w39RSRIUmSJgq28AwVCrxLbgSaoQFuMlSNhpTJdPwY-mSEB9gH0XW8DspScv9S3koqxDbFNmB7HSbzElButiZfBZgkHAo-JNitCY0eh-nlq67WGOPDbAtVpaCk1eEuIsZVgZjADgSeVgxRCttHmNL-ydi-v1qJnghh9NBf8cY=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
July 29 - August 9, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn114dWOJ7n01tdPVN-ZnKz3SqYpxq8NmVfQ8L-HahOeOUnlNBTHTpmTeQ7qbwtCAK_HUuLvYZ8KkiOkgaQHeQxPZsI6RHmS9elsQvj4Vwg_9OLP6523ksYDWLlIDSeUwgBnaQp_D22PUY-cuXF1H-aSGot9I3TQ8cVtgTnJeLTHXQKOxJUsyrO8-9na4q5f_ARcdos1R9_EfI3fUEpapCLBLr--vEp3_7B_ObeVXgR6wydqMBo6LtnLICxicmq7aXmJCj3zkhz-bU6Mm2yRou8ed].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn13oEn_CMWa_-OgR56LKLl4_ZgYi7ipANEu7pQAaVOh-3WP_cmSC-We8ZtpzMKAhojTZSn3Ue-znddJxDI7G8q5Nb3iDr48EnU7JLs6tfNx9fmTtsBK7PIUg]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn11eaCm0ms3XCvGmqohAyvrkdC7MDGJ5TaTZkVbt98LAPx7w_D7WrogrtF6dQWZ_RKrITBnE2CQNpgfFtgOF7nQuVSnIpKPab6JKIVG-4Z3sK40FxOYH4XGXKPFhBXK6xHVnUXBMJlKcRp_pMKyrmZE_fav5MGHds2M=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn10gSdgd5mJDK2X5lZS8DDji5JsMqC2jdwcb_S_rDwouE9-saxARwjUXL_p7XLwlp5A2sei-7BJjxsoLw8InHfOm31_qEAQ8RcOQdru-ghpTF8pyGnojJ_HNzwPaFkB0Lzoyrwzqg54JkV5V4QZBFn7h_x2bCvGa7GY=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn11c9MXgkBmSirHEo0Vkl9el-ESJqiJs2qxded_m4VHYPc-dSkJ5pmmEfDI6-L5SyOFA7a-AlYS2ES3enKcYHz4D6pk9c_baP7drEobVl4deC3NhTiZWzzPp]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn114dWOJ7n01tdPVN-ZnKz3SqYpxq8NmVfQ8L-HahOeOUnlNBTHTpmTeQ7qbwtCAK_HUuLvYZ8KkiOkgaQHeQxPZsI6RHmS9elsQvj4Vwg_9OLP6523ksYDWLlIDSeUwgBnaQp_D22PUY-cuXF1H-aSGot9I3TQ8cVtgTnJeLTHXQKOxJUsyrO8-9na4q5f_ARcdos1R9_EfI3fUEpapCLBLr--vEp3_7B_ObeVXgR6wydqMBo6LtnLICxicmq7aXmJCj3zkhz-bU6Mm2yRou8ed]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn13FZrZlRcnW1HaHQKk_w7o9yhuF1XhPaDrPMJ85L2d0EaXGmam6NXk9vz4CH77mKDZMjMcn68pOqLKm8v6lyVwX6aKEYYbOy89y01klgp6shj6zsvV7YoYsF0bLh0hWVcvJx6ddpaxfpMmeM9KI80MF]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn10DfMqcKB-Z6ahq4xCORMu7ljn1kjnUTlLRyne__U2g6p5idcbB3lS8vK3hvb9tEZllwaG0io55ALiYR30_pycGO4uas06KF2NCKj_0qceFNeJg97P5sUvxt7NvSx5wrZtKVIhwyLbuHTEhUrEPDIcin5GXMUjhPnQ=]
National  
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn10smTiPHatTvEGb8u089ENWJSOPYntFF6eUJAxIcE0Y1rF4CvBlf97AnPRk1NYWRHCG53b3uGgtvw0dlVO5kjz4FHfGtThxOcAKbDHCM1iReGuVq52phrdH]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn10smTiPHatTvEGb8u089ENWJSOPYntFF6eUJAxIcE0Y1rF4CvBlf97AnPRk1NYWRHCG53b3uGgtvw0dlVO5kjz4FHfGtThxOcAKbDHCM1iReGuVq52phrdH]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn11_iMCAAkQM7tSI-S9gWXUENuT2xmpFLHfnE1tYZEnzo3-ieB_Ie8uzvKsST62GlU33skk8bLFJT_pbFovX9fnwm4kInp_7KnBCqZtwELNpyXj2WRUkGCPVak9Q5AkuedjVlFtSAgficQs9MUsOqwjh]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn13Yt8pr75h3B6QHc-ac5ZauGX9VfIMRISb_bqhwtjrgP9kHXNGPpHRFUduLoqFvL0SjvOUyG2P744zzrOCEQJOgW5LNTX-koqEMPh2NyNiLnW2GLLqxi5n8H0BFzXryt5iCTkUjPn7jkw==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001K2GElqICn13rkK2H1c7D8TlD2fGvo0vrY2HGMBEditB7XydFjvKX6JyBTuia1eA09ijA4zxCOvrz7jPFym4Uu5OBIaEJGOnuIZgZoLAoLHdMH_5RJpWOcUEOQUzqHWBLMKn3gVDDi84QcjFHygtKGoiqIs8pOdE2tv6j8TyYA-3kQ5TFBXVRAw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113617500031


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001kuuO2qKf8-mKARbkc4-Mbw%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001kuuO2qKf8-mKARbkc4-Mbw%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to