American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

July 25, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Piers or Footings for Pipe Stands

"Is there any guidance as to the size (diameter) or construction of the concrete
 piers/footings for pipe stands other than depth below the frost line?"

We have reviewed NFPA 15, 2012 edition that you indicated as the applicable 
standard.
Our informal interpretation is that the only pier or footing details for pipe 
stands
are provided in the annex material.

The annex Figure A.6.3.2.2.4 shows the detail for the support leg footings for 
pipe
stands.  Several committee members were contacted regarding this figure.  The 
figure
was purposely inserted into the annex starting in the 2001 edition so there were
 no limiting factors.  The figure does not show any sizes or steel reinforcement
 within the concrete since it was not needed.  It's expected that concrete will 
be poured into a form or form tube with anchor j-bolts in place.  The diameter 
of
the footing or pier needs to be only slightly larger than the flange size.  For 
example, 4-inch vertical pipe may have a 9-inch flange.  The pier or footing 
would
need a diameter of at least 11-inches.  The depths are not shown because of soil
 variations.  The sprinkler contractor can subcontract this to the general 
contractor
or one of their subcontractors.  Since the loops are supported by several pipe 
stands,
the assembly should be quite rigid.  The other issue that will likely be 
discussed
in the next edition cycle is the use of the term footing.  The construction term
 pier may be a better option than footer or footing.  A pier is a column of 
masonry,
usually rectangular in horizontal cross section, used to support other 
structural
members.  A footer or footing is a continuous thick concrete pad installed 
before
and supports the foundation wall or monopost.  The bottom line is that no 
additional
measures are necessary beyond that shown in Figure A.6.3.2.2.4 for piers for 
footings
when supporting pipe stands for NFPA 15 systems.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqq9wfpNCPOppqRZ8Bwh1VOpOaHR-cdxTtA5IGwUaa0nUvsO4q17P01CjBdmFxSwn046AqovGiISq2NDbisIzo4HRNkJGXmdINQ4FiI8bUHeTcf4-C7SxB7r]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqooZi39lCgnRK5Skt_GgUO8GLTWVWsiFY2gBcRPwNN0YKuBCpRq00_2O4auOJXUx3gwbyNklp6LrCx38tNf743WobP7jOHVb69ph_Mq4xf9roxVtr3bliGaGn414ZRsLNBzOtu8N6GdlAwX6hUJOd7D2z31wMa8jR_wzSrdeGkpHdgwntW3XFpeYkk6i3zXROk=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Webinar
August 14
AFSA will present a
90-minute webinar
"NFPA 25, 2013 Edition Update,"
on August 14, 2013 at 11:00 am CDT.
This webinar is free to all AFSA members. More details, including registration 
information,
will be posted at firesprinkler.org soon.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqppXHGJSKTGAyE7BrjPrt1t_mH0Wp3sfLyLPL7HyXByWt9rsegmVz39gdl1JLvs9KR7i7_2_kam5c7Kr1Hi7H1PqtyDnxNi_ljKNqAK36X2fHmpKeRZxdjaFmMt1jqWY7EIEwb6PjPsI-Pm0dqeeFyoKNiAiMuGuVTGIQw64dnxtDyQFINXD3UVBdlwwk6pi-tjI_9wi0-gZMoEPD4iDK4na0FpfugHJieYp05AUGIOFH7heK2AdlgRW-CmgqUhEQ3ynFGI96vBhqNUmxU06mfi].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Oct. 28 - Nov. 8, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqppXHGJSKTGAyE7BrjPrt1t_mH0Wp3sfLyLPL7HyXByWt9rsegmVz39gdl1JLvs9KR7i7_2_kam5c7Kr1Hi7H1PqtyDnxNi_ljKNqAK36X2fHmpKeRZxdjaFmMt1jqWY7EIEwb6PjPsI-Pm0dqeeFyoKNiAiMuGuVTGIQw64dnxtDyQFINXD3UVBdlwwk6pi-tjI_9wi0-gZMoEPD4iDK4na0FpfugHJieYp05AUGIOFH7heK2AdlgRW-CmgqUhEQ3ynFGI96vBhqNUmxU06mfi].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqpzq3YpCjCRqq46_4pdXobb4Z7Sr8blvo5VG-jlwIvQy0i7GqLyF7I3MDSgT8dDLz_2DYrQoHz0jNflV5KZdIiMIkDAk8wPK6S1l4VTr68PhLUwEWiJeKpL]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqoMzG6qhbpwii12wUhqhZbF5Q4plxceaVO8YkyMouhUfK-rpXy40gbvYnyin-19JC9uPPr6Eka8cRe8Bk6qBiGZNkfThU9K242jzKPHC3OYI3wQE2fE2rgpcaKN_yeOyBrDRk8EffhnvSPIb3i57tBReUx9xc2w75Y=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqquBKoe3ZG0mmSsnBuKPb94xlhf68_y2PndsaEyusauueGXBx-zaFiDffBwciGnVvSuwshiUanoZKMZzI-d5P0-gXwZSG765M_enCLCZbTb47dUfQsqhpTbi1Tds3LxyyhqKBREN64PD5iMhbA3qYQUu42b8vq9gcg=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqq9wfpNCPOppqRZ8Bwh1VOpOaHR-cdxTtA5IGwUaa0nUvsO4q17P01CjBdmFxSwn046AqovGiISq2NDbisIzo4HRNkJGXmdINQ4FiI8bUHeTcf4-C7SxB7r]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqppXHGJSKTGAyE7BrjPrt1t_mH0Wp3sfLyLPL7HyXByWt9rsegmVz39gdl1JLvs9KR7i7_2_kam5c7Kr1Hi7H1PqtyDnxNi_ljKNqAK36X2fHmpKeRZxdjaFmMt1jqWY7EIEwb6PjPsI-Pm0dqeeFyoKNiAiMuGuVTGIQw64dnxtDyQFINXD3UVBdlwwk6pi-tjI_9wi0-gZMoEPD4iDK4na0FpfugHJieYp05AUGIOFH7heK2AdlgRW-CmgqUhEQ3ynFGI96vBhqNUmxU06mfi]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqrUgRKe4Qqc9VoebLNVSLEDn4HI9-fMebIqfcjIuJ3XMsPtVOBpAP1Qg-p53TQQBJg69S2NzrfxZOQ23zXVduBjdgbh6EXW4efXDK-1NzadkntcMb1-cwdWNo7VV5uIVLiwlk7evMSCqV7EK2X8mNxV]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqo0v5m4lUF3VWHbvFJ1Lp1BVlcpawlYcR6r_u-PRLUoL52JMOJQNQ_wXUA8IQKsVmyjhO7fgbxHM7FJ5ZuL7FbIhczSKe9AXvNTkFpts2wY0lpCl-HrRMbbLa5axsFJtnoRFwZRiktsFlcICz9PWvVLv_PANM4Zdfg=]
National  
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqpP1n8LsGkBpjXaRJcAmOAav78iw6AclXfgGtUq_h3Wl6sXOPU2XYhtVFJJ-_ddVK8sEGj9UKm-yx3Z6us3jULKwGEGyD0SWE8aR0Ln0qwb1N1lOJ0Rcamg]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqpP1n8LsGkBpjXaRJcAmOAav78iw6AclXfgGtUq_h3Wl6sXOPU2XYhtVFJJ-_ddVK8sEGj9UKm-yx3Z6us3jULKwGEGyD0SWE8aR0Ln0qwb1N1lOJ0Rcamg]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqq7T9vyziTyQXuLd0QI8RPKGCo_UlnmBww61Qlpk11YD5oS_Ks5MRhGJvX7Q_L4pJOkSRyDqCn1dX1G_I5H5GdlnzCJqMri-ftBpXC6_Uo_3QRoB1ixuibmHKM1BZ_YdkF-F2ov3wi5Z1xVul3Kq41X]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqrGOp4Uy6ZVgNn29yqNXKlnQwiEFttg-3KlFcdxnjETiwhmm3XD9GC4x6_LhqjAe34wlrC2Bnt2d0dDHz8yrXyM5JLjIHY6lyu2HC8NljBNtk5daf-JxNJX7svZl3_y50INcUXL6gl0IQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001ZbDpb1LWnqpfOlfu78SiOVI9FFKMzQjjCjJRiqGTbdCrBgj_UQghG-ekPXmCgqZFnOFzVmt80nlOM67L4-orSdNa9VNb6-Ydk7duv2SSLKZ77Vxsk4m2tgiG_RZy_zMc0-V4dyxo4r2Jy8gdwDuQ8Ckivw-5wv3W7awMJ-FyISdaaRGy9shtpg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1114290238562


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001KOeGAhHP9jGmSA1NNwlcrw%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001KOeGAhHP9jGmSA1NNwlcrw%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to