Water Delivery Test for Preaction Systems

We have several double interlock preaction systems with very long pipe runs from
 the end of the last branch line to the exterior.  The additional pipe is adding
 additional time on the

60-second water delivery test required by NFPA 13.  Is this test intended to 
test
the duration for water to reach the building exterior or the last sprinkler in 
the
system?  If the latter is true, would using a sight glass to determine when the 
water arrives an acceptable approach?"

We have reviewed the 2013 edition of NFPA 13 as the applicable standard.  Our 
informal
interpretation is that water delivery to the last sprinkler is the point of 
interest.

The starting in the criteria is Section 8.17.4.4.3 that states that a test 
connection
consists of an assembly made up of at least 1in. piping, a shut-off valve with a
 plug, and terminating at an orifice that provides a flow equivalent to one 
sprinkler.
 Additionally, Section 8.17.4.4.4 identifies that the test connection is 
provided
at end of most remote sprinkler pipe (branch line as shown by Figure 
A.8.17.4.3).
 We typically use the discharge of water to stop the test because it is easily 
seen
but we are interested in the duration to reach the furthest sprinkler since that
 is what fights the fire.  This is indicated by the criteria saying when the 
water
gets TO the test connection (see Section 7.3.2.3.1.2).  Although not explicitly 
discussed in NFPA 13, the use of a sight glass will show when water reaches the 
test connection.  Such confirmation is no different than that used for wet pipe 
systems to confirm water flow as shown by Figure A.8.17.4.2(b) for a floor 
control
valve.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KnIebwlL45dUoQ82gxweRp-aDTPPmQ_43wW5dnoPsPyy3XlDa8o42tLeKLDRn_Lw1OtlbTYzy9VXy7DarM0o0K3ZyVz9bccxYCuw1HHvsoTStU07gpbVLWe]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KmDlkg-HvPu3gpvRCBjWzEAAtcJCQzvZE6SUFGo7fw0WjIQo1RdqjJDoAjgsX1czNS8D-KMaHuyXPJ_JcE0ib2tq_iestRIrRH19vgAgoiLZANn0ty_laNsLYVvkiXDFdDtK75m9aj3F18r3ZdRSed2Vo5d37ioRm6xRvEfH0GogELK2lmU8a30bfwQ_S3mCtk=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
July 29 - August 9, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkudwD9M9e-LJ_DiW_wZNp0IFZaEm1YlffkiX0U1ZzwmLEoyFBadyhbuc8ljiP9Q-YqaLItaBlCqFaqXoeVwvITTD1SUK-N5MzHCrlrh5FR47PXFKbY8LCGOKY0OJZDdS3yX1sqU7jdlRCEaK5muPM71Cz9sc6-cohq91lJRp4MVuz30727I2L9AM6sQKhwLVaG_v8YIgwgVln5GaEa6YgPq6rMJk9voSUYKQRCxQIT2YRXbyhJb448eX52AJJZCszKtySSff6L6jkzzqkOpscI].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KmimsVOB0D4ndQIwiyLjByOA1lMKu8CR0M1DjKIxcxb99uzkHkB_uWEHXlSiumdTzhYFtjYUDtjDi79BQxS3GYtVXFjJllr1U6Coav2N1kWRwVTT56y-lJx]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Webinar
August 14
AFSA will present a
90-minute webinar
"NFPA 25, 2013 Edition Update,"
on August 14, 2013 at 11:00 am CDT.
This webinar is free to all AFSA members. More details, including registration 
information,
will be posted at firesprinkler.org soon.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkudwD9M9e-LJ_DiW_wZNp0IFZaEm1YlffkiX0U1ZzwmLEoyFBadyhbuc8ljiP9Q-YqaLItaBlCqFaqXoeVwvITTD1SUK-N5MzHCrlrh5FR47PXFKbY8LCGOKY0OJZDdS3yX1sqU7jdlRCEaK5muPM71Cz9sc6-cohq91lJRp4MVuz30727I2L9AM6sQKhwLVaG_v8YIgwgVln5GaEa6YgPq6rMJk9voSUYKQRCxQIT2YRXbyhJb448eX52AJJZCszKtySSff6L6jkzzqkOpscI].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkOhqBAH7tptHwCwEwUxWfgTL9DBdwDJHSwYeybxJdYBnWZ0xXyscE1soDU3Ixt1qLsb2jGzF6T1IVr4isDAgBnqbqAsjWksuIEcl3vVY9DDOYUgDZufcxSO41u-b8q-MujY67KVu9B0DZB0ao-nYhbWtIwfA-R1YA=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkDJSzRfAnH6DJow-9G4TCPP_YsLomrxzo_ZL7WVKeylWQ-lPnr-QECHMEFOCjwxVfyrQxB2k4LavRocphSL7Q1dBRLehoUoXUxtF2wWebNWKPOPDt9O5LavAZdC7x4FVBRfyyOWWyBhSQwWN4bic0vCkRBY7XmPY8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KnIebwlL45dUoQ82gxweRp-aDTPPmQ_43wW5dnoPsPyy3XlDa8o42tLeKLDRn_Lw1OtlbTYzy9VXy7DarM0o0K3ZyVz9bccxYCuw1HHvsoTStU07gpbVLWe]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkudwD9M9e-LJ_DiW_wZNp0IFZaEm1YlffkiX0U1ZzwmLEoyFBadyhbuc8ljiP9Q-YqaLItaBlCqFaqXoeVwvITTD1SUK-N5MzHCrlrh5FR47PXFKbY8LCGOKY0OJZDdS3yX1sqU7jdlRCEaK5muPM71Cz9sc6-cohq91lJRp4MVuz30727I2L9AM6sQKhwLVaG_v8YIgwgVln5GaEa6YgPq6rMJk9voSUYKQRCxQIT2YRXbyhJb448eX52AJJZCszKtySSff6L6jkzzqkOpscI]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6Kk0kW6d7YkUrYekDK3Osa49IORZl703_rJFT7bd2hNAETfI6CIuYFzPCJuVWbt_uy0KxsyYu636hwMXys9aPMhunQJOt6OTfT3xtlZ351_oM1iemnhpk9B3-4k-PDKN6rR8rQdxceH0RRlh-S268NXH]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KnMY7TU75yfYq1qEKFiwA-vNli_wLh0m3qe4ueQBrsFTJ5QAkP3hIEzguezxDlQgjSXCnqhtYqsHCgqTddsPmcXtYnhG5x8j5aqYo67XP5UmAf8W1tsafm4JHQAm62dfCmFopn20zJ3pk6Q-vXGi4sFEflTeHkX3bc=]
National  
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6Kl8PcU538aq9qHpOshZdhcnBcYikVKMHbI9TEEBJrygI-orLCxTYswS9UvvmjixKx_8iTYaGjMLoGOEkAZWF8c8-tiC1Msh_YLovMROIiAtL8m6gwkViQP7]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6Kl8PcU538aq9qHpOshZdhcnBcYikVKMHbI9TEEBJrygI-orLCxTYswS9UvvmjixKx_8iTYaGjMLoGOEkAZWF8c8-tiC1Msh_YLovMROIiAtL8m6gwkViQP7]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KkVpPIDE1IBIEsRojNIyxG34ZzouwUwnKILlM8Ph88iBKzuhgfRsgcZUNDUFhmNy2PiPFli9SVRSJjhSWFzq0xkJjVSJDMRYdUnf9YZYNvS9ExrCM8VP661-u19UM-XyXn40l6il6tSiAhQGxUd9QD8]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KnQfUfzVe1K7gf1ecgs_k3PfBeDHeAFvmSa2aAo8705mbvuutJBaWSx1obSOgg0XQtHhKMiGMtX9powKERQAcn7zEvq-XUPuQxFQzL2GYxeCuU5U21EqWn8-NtDKQQPMgz-dZyC9uNKvg==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001GzQKU0I_6KknGTeOk5C8S2kBFVBAtuMcZG_yfFsmAL84wPVX3zUohwTabUn9W8UHQkywvq4McWgg94KjVNpylPzTq4NchYgHx6dsfDfuoTWyP_eYX2ieyw0KdhwlQ7_Yp5cm1vh7eo6wZQRckS1A1H_N1nKtkgNrokYhQRiINEygj9YzkYAkdg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1114181345089


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001EV68fWzb3KnGyhY87qNPXQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001EV68fWzb3KnGyhY87qNPXQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to