Solder-type Extra-High Temperature Sprinklers

"Paragraph 5.3.1.1.1.4 indicates that "solder-type" sprinklers with extra high 
temperature
classification be tested at 5-year intervals.  I assume that this also includes 
sprinklers with Quartzoid bulbs.  Is this the correct assumption?"

We have reviewed NFPA 25, 2014 edition that you indicated as the applicable 
standard.
Our informal interpretation is that 5-year testing requirement does not apply to
 glass bulb sprinklers.

The base requirement in 5.3.1.1.1.4 says that representative samples of 
solder-type
sprinklers with a temperature classification of extra high 325°F or greater that
 are exposed to semi- continuous to continuous maximum allowable ambient 
temperature
conditions shall be tested at 5-year intervals. The annex material clarifies in 
A.5.3.1.1.1.4 that due to solder migration caused by the high temperatures to 
which
these devices are exposed, it is important to test them every 5 years. Because 
of
this phenomenon, the operating temperature can vary over a wide range. This does
 not apply to glass bulb sprinklers. There is no exception for testing glass 
bulb-type
sprinklers at any other testing frequency.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHGF039pNS4Cw=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qSg3yKfCotFsJPHaReeay2uKS_y9Fg4TXj2o575JS3XIMKjCdqWDDAyy47azdNtpVvSaGBneKPfvxN3wXV0My8826f-10vcxXVxOKbA60jn5QaR1y5ohVJg2eswmPor8OQOEGsk56oio=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Sept. 8 - 19, 2014
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U60Z4TcVnkLw1f7iY1OxvpVjQ-nzroOl3mtYZAhHQXrC5FZ1da2Aqrejp0s6F0L1ENCwinLqSJfvzUqpM5jlJZtLVmv8kiAF-lZXFjrx8UYig6l9y0w1zBpRN-aTWxqSxrs5110wbbr832gdg0Zr6Eu9_Z7mPHgJK9KaJDRvwmY6Bv4HNR2nx7ugh0Xtrr3a1caQx5FvnKZklA==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U630a2tCTQu3U09vZpaSquXIaTSBwZWBKp1UtNu3LKW_QA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
NFPA 25, 2014 Edition
by
Russ Leavitt
June 19, 2014
This webinar examines not only the significant revisions that occurred and the 
reasoning
behind the changes, but also proposals that were rejected by the Technical 
Committee.
Cost is FREE for AFSA members.
Register Button 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHjdEWMxj0LMYpS9c1IDQFe75X83Zl_upQIRTq_6STuqzFl_OtE143WhrIXTsVVJ2r]
This seminar offers 1.5 CPD and 0.15 CEU.*
(*Note: There is a fee of $15 to acquire the CEU credits. The webinar/content is
 being given free, but the CEUs will have a fee.)
Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U60Z4TcVnkLw1f7iY1OxvpVjQ-nzroOl3mtYZAhHQXrC5FZ1da2Aqrejp0s6F0L1ENCwinLqSJfvzUqpM5jlJZtLVmv8kiAF-lZXFjrx8UYig6l9y0w1zBpRN-aTWxqSxrs5110wbbr832gdg0Zr6Eu9_Z7mPHgJK9KaJDRvwmY6Bv4HNR2nx7ugh0Xtrr3a1caQx5FvnKZklA==].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHjdEWMxj0LMZZvMeGwGCN_w8WpIGz6CvsI4mdwHwtG9CUqftFYPOm_Kl7WSO9HHyF]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHjdEWMxj0LMamfe5AmcYGj1f7kCbxnnvsz_9zboTtdwylaJZG120GnOS6zw4FbItK]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHGF039pNS4Cw=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U60Z4TcVnkLw1f7iY1OxvpVjQ-nzroOl3mtYZAhHQXrC5FZ1da2Aqrejp0s6F0L1ENCwinLqSJfvzUqpM5jlJZtLVmv8kiAF-lZXFjrx8UYig6l9y0w1zBpRN-aTWxqSxrs5110wbbr832gdg0Zr6Eu9_Z7mPHgJK9KaJDRvwmY6Bv4HNR2nx7ugh0Xtrr3a1caQx5FvnKZklA==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U61cmw9t4fS6Kjgo2bjyfwkj6SKdPkamf80TQRO1mqj2saCacx4bRr6I-oSmMiSxtx1Y1gCifU4jGg==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U60f3ntpNI0dfhws6kxxLXHFMjsyYhWoMqqQ0Vqfyc5oG06BrWQCUDNypEftEjKmah_uZn7jF7l2Lw==]
National  
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62yPvwmfHQdxGaV3ZKANJONtkDybhW90LmW2bHjWjhgxA==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62yPvwmfHQdxGaV3ZKANJONtkDybhW90LmW2bHjWjhgxA==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U63aJSnApLG0YBfLOFHXg9o8r3VyS-y5n9TzG9Qqn1cWf-tZ0kCTYCxXvNPeIldT7Wg60Hpk0xL1rw==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHjdEWMxj0LMYLjyOfbsDMWRcg-ioFBhXr]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001DrDN2Z5FqDsImcoyLDw-bpK_HWa77-c17ICBhCbiczvGtWGF5uwsJBNOF_jbyr_qq0-u0SL5U62V1-tIuvgXGgjyty9z43aHjdEWMxj0LMZv6v2HrTFmmSVCGjnvZ1j8xw2LLSe2TsnXjwQdqkJz5T1UuZRlmu5M]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117375091934&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001IF1QARHS1HPmvJqxI0zTkA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001IF1QARHS1HPmvJqxI0zTkA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to