American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

May 7, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Detached Exterior Canopies

"The original building plans detailed lattice type canopies at nine different 
locations
which are separated from the building and are all sloped so there would be no 
location
for heat to collect if sprinklers were installed below.  The latest plan is to 
install
standing seam sheet metal on top of these lattice work canopies over the 
walkways
either at the exterior of the building or from building to building.  There are 
no storage plans and these are simply covered entrances at the exterior doorways
 and there is never any portion of the structure that touches or connects to the
 combustible assisted living home structures.  Most of the gaps from the 
occupied
building to lattice canopy is 1 ft 6 in. and greater.  Are sprinklers required 
for
the detached canopies?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that NFPA 13 may require protection for the combustible 
canopy.
The NFPA 13 standard does not specifically address freestanding canopies that 
are
separated from the main structure.  The IBC can provide some guidance on how to 
deal with this.  The IBC defines buildings as covered structure and although it 
is a separate building, there must be a minimum separation distance or rated 
construction
to treat it as independent.  Without one of the two, it is then considered as 
one
fire area.  The reference is Table 602 in the IBC.  An example is that the table
 shows for a distance less than 5 ft that 1-hour rated exterior walls are 
required
for a Group I occupancy.  If the exterior walls are not rated, the detached 
combustible
canopy would be part of the main building where Section 8.15.7 for exterior 
roofs
or canopies requires sprinkler protection for the combustible canopy.  Since a 
small
gap between the building and the canopy may not constitute a reason to omit 
sprinklers,
they can be omitted if the canopy or roof is of noncombustible or limited 
combustible
construction and there are no combustibles being stored or handled under the 
canopy.
 Also note that temporary parking of cars and the loading and unloading of cars 
under the canopy does not generate the requirement for sprinkler protection.  
Section
8.15.7 identifies other configurations for omitting sprinkler protection but it 
does not appear that this application meets those requirements unless the wood 
used
is fire-retardant-treated wood as defined in NFPA 703.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXf6fo9s2m_heI=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungv0c_tQjezMdKa8yY_1bpSKMAkVxOqRtS6EnFYif6gDyqvn2iGNYR9wI4355hdT9gsDyJ2z7sF9YoojEa5gfdUNDpFDeWm2EpM1wmW-YbnbTdqNZ0f9NaOR9YSwal_dTa9YqeuLsAq84=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Sept. 8 - 19, 2014
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLSREIhxmyUFFoweeX6pQfpPa9gRwi93_q3o3KoKPgDm28iqcN18jUee517nZXB4klriPtqiGlbfdjW2fB9VhC0PcuwZFj8xRFQqpoP_z44I1vKumtGy6IWBK1tbf5dNVhXpYUBwTEvNPoH6POfAxa-RdRvel-unCm1O9Qf6fpBEifeu2SfsypNoRfrZpHY_fLVMU41dTp4eiA==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLSSLPKwZgq_IHdvLikNt12NLOORo2Y997jYxWQg6h0f4Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXfhujlT9R8qjmrBKcGIzd5KETZo7l3S1gTiLnlJvXTI5_8-gDdO5X0TjvS5sCqY4_D]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXfhujlT9R8qjnn_gQqo5G5hYPP1aa648OQIBle22__gxj8-LNPdUyhVu2Uofj2hvT8]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXf6fo9s2m_heI=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLSREIhxmyUFFoweeX6pQfpPa9gRwi93_q3o3KoKPgDm28iqcN18jUee517nZXB4klriPtqiGlbfdjW2fB9VhC0PcuwZFj8xRFQqpoP_z44I1vKumtGy6IWBK1tbf5dNVhXpYUBwTEvNPoH6POfAxa-RdRvel-unCm1O9Qf6fpBEifeu2SfsypNoRfrZpHY_fLVMU41dTp4eiA==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLQBL6XlGPiOuca7Wek9uOlkk32q4eAqW-EZ7YWXd83o7sKawEo3L4xZ95Re4ve03Fjb0sIIFNjY-Q==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLTH6Vp2dZARo0OwmdCXNEaxNMWLc3K3kr9-9TmzGE5akTuYdK5LuO2DNnDR99ownd3pF-6yf4JBHw==]
National  
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLS55bl_T9XVwpl6b5zooJkA3-0XEUKNVspMobaPYM1KKw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLS55bl_T9XVwpl6b5zooJkA3-0XEUKNVspMobaPYM1KKw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLQ30rRb1UQoj0mgu10ys6ZyX_1ax8xjMw3rFox7XdxXd1yNkDFegxR6TpHNRGBbzjV82PrGIgz5Jg==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXfhujlT9R8qjmtHuGd0DeUJtbg2BjPvhED]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001Gnc4-Kv7T7hfnrWeSL12CYXxxozLI_5svDv7jy9impjmMQ0lLPARtQwq9O-piungh-q8r_yyBLRloX3QlBherBs824x-5pXfhujlT9R8qjkkKakZhw6eJ0yH1JoVFiQwRUbx_T3R1gb0M9KoqZWxXevfyB27Clpo]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117303672622&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001E5djMwqmUYq5m1aJbFNPsg%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001E5djMwqmUYq5m1aJbFNPsg%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to