American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

May 2, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Trapeze Ring Hangers

"We have installed a pipe trapeze to support a sprinkler pipe. We have attached 
a swivel ring hanger to the pipe trapeze.  Can a swivel ring hanger be used to 
support
the sprinkler pipe from a pipe trapeze member?"

We have reviewed NFPA 13, 2010 edition that you indicated as the applicable 
standard.
Our informal interpretation is that swivel ring hangers listed for trapeze 
applications
can be used to support pipe from a trapeze member.
There was a change in the use of rods and ring hangers for trapeze supports 
starting
with the 2007 edition.  The changes required swivel ring hangers attached to the
 trapeze member to be listed "trapeze" or "heavy duty" ring hangers that have 
heavier
metal.  Historically in the 2002 edition, Section 9.1.1.6.5 indicated that where
 a pipe is suspended from a pipe trapeze of a diameter less than the diameter of
 the pipe being supported; ring, strap, or clevis hangers of the size 
corresponding
to the suspended pipe shall be used on both ends.  It was permissible to have a 
larger size swivel ring attaching to a smaller size pipe (trapeze member).  The 
swivel ring was formed or bent to accommodate the smaller pipe to prevent the 
swivel
ring from elongating over time.  The 2007 edition of NFPA 13 included new 
changes
to trapeze assemblies.  Section 9.1.1.6.5 indicates that all components of each 
hanger assembly that attach to a trapeze member shall conform to 9.1.1.4 
(listing)
and be sized to support the suspended sprinkler pipe.  Section 9.1.1.6.6 also 
indicates
that the ring, strap, or clevis installed on a pipe trapeze shall be 
manufactured
to fit the pipe size of the trapeze member.  The committee wanted to address the
 issue of using a larger sized ring, strap, or clevis hanger for a smaller piece
 of trapeze pipe.  The committee felt that hangers are listed for the pipe sizes
 indicated.  For example, a 4-inch swivel ring should hold a 4-inch pipe.  The 
4-inch
swivel ring is capable of supporting a 2-inch pipe, but the listing is not 
obtained
in that manner.  The committee also wanted to remove the elongation issue.  The 
rod size was also in question.  A 3/8-inch rod on the trapeze assembly was 
allowed
to be used to support a 6-inch sprinkler pipe.  This change in wording would 
require
the rod sizes on the trapeze assembly to correspond with the rod size of the 
pipe
being supported.  Manufacturers have responded with trapeze or heavy-duty 
hangers
for trapeze applications with the adjustable threaded ring nut to accept 3/8-in.
 or 1/2-in. rods to support a larger sized sprinkler pipe up to 8-inches.  For 
example,
the sections will require 2-in. hangers for a 2-inch trapeze pipe.  When a 
6-inch
sprinkler pipe is supported, heavy-duty 2-in. trapeze swivel ring, strap, or 
clevis
hangers will be required on the trapeze pipe.  In addition, all rods in the 
assembly
will have to be a minimum of 1/2-inch.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_jeh9RTgA0aV78=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIikp9aW4VTJjY4gu1kaqZlR3sDUJF0xTNfLuHr2k2ylwvWFdKcGOEm2LeMltG8Btx6wFVDrBGNumOqmMuWGJvdRXOhQ_-ipksx4cIM_v5FZ9GYUlmap5ZRyV-OHHUOfWGtF-PSVfVjEQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Sept. 8 - 19, 2014
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56irc1cWR-cb2noz3ss51ZPzvRw1BJOpLQjO7woj3JY3l5dJTMQa5KjutBNyoFTTeCwW1nWTACY7Bz5CSGVSwuSy2tInuNCErscEyz3Y8Mmp5vUpfcr_ZIPp3hoJdIn-S_6bZCRT1YsdMZI2A3Dte2ZptwgjVhX9S6NOA_Il2BNV88m65CCNoS5F_yT_vFNnFxV64IR2oKmZKA==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56i5sYoIAU74At6LJNor3Sv42exPyrYLfEq2ZpR44L75LQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_je2g1UvSmz7xNOoKddVDtoZJ2MH3MMJmw7SedecB0iNKPNw2EcKN6Wz4BDihMI1eEu]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_je2g1UvSmz7xPp1UvAyyfrGOKaOaX2OEBU1X7D0iSSa7HHp-c0Nho1wMHS9PxUnFto]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_jeh9RTgA0aV78=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56irc1cWR-cb2noz3ss51ZPzvRw1BJOpLQjO7woj3JY3l5dJTMQa5KjutBNyoFTTeCwW1nWTACY7Bz5CSGVSwuSy2tInuNCErscEyz3Y8Mmp5vUpfcr_ZIPp3hoJdIn-S_6bZCRT1YsdMZI2A3Dte2ZptwgjVhX9S6NOA_Il2BNV88m65CCNoS5F_yT_vFNnFxV64IR2oKmZKA==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56jJ6umZbh_DjkFeuRom899O0CMbQKeUI4l3gZrNxYsleJK0emuMUGJCl27BCGDd24Jtz16PJu1e4w==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56glSBZIxmt7IWyxo2RbDXo6nBBPDJFufunhrJ9fWhYYex1L_5qbIneStS2fIp4aeEozDk691avjYQ==]
National  
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56h7NUoecikWopRtTfbZ6Xl9GOC4IH6qW6fEwRfiWuGQzQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56h7NUoecikWopRtTfbZ6Xl9GOC4IH6qW6fEwRfiWuGQzQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56g1Tjt-HxlXa6LtK5F34qwQ1dklbGf1tZodhWBvs5DV6kXbQgeb0EIuvU44P_8pPU387YLfxDDjdA==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_je2g1UvSmz7xOnxvTH904GF_pqM7Ux6JZc]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001gBtguv3Uugq2tHX59bdXy0b_1vWotrCQEo1bEgmibtqzyocVaTSEGSR9V9b9iRIIbFijMFTZ56iXKUyg4419Km5rLXirI_je2g1UvSmz7xO5Cvf0Gpkrr_95N77D1DpQAmz5oM1uV6SYxKngHkfptAYHfiNEgpPz]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117258578284&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=0019EuNHi-Rc2dFTA14mPTyZQ%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=0019EuNHi-Rc2dFTA14mPTyZQ%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to