Protection of CPVC Pipe from Punctures

"We installed 1-in. CPVC pipe in a wall from a lower floor to a sidewall 
sprinkler.
We have installed nail plates on the wood studs where the pipe passes through. 
The
wall is constructed with 3 5/8-in. studs where the outside edge of the pipe is 
close
to the edge of the 3/8 in. or large gypsum wallboard. The AHJ is citing Section 
6.7.2.5 for the protection of risers subject to mechanical damage to protect 
pipe
in between the studs. Does NFPA, IBC or IFC require any other protection for the
 CPVC pipe?"

We have reviewed NFPA 13R, 2013 edition as the applicable standard as well as 
the
2012 editions of the IFC, IBC, IRC, IPC, and the CPVC manufacturers installation
 instructions. Our informal interpretation is that there are no listings, 
standard
or code requirements to protect pipe in between the studs from a puncture 
hazard.

Nonmetallic pipe in walls do run the risk of being punctured by nails, screws, 
and
other similar objects. There is no code requirement with the exception of pipes 
passing through studs to protect the pipe. Section 6.7.2.5 states, "Sprinkler 
risers
subject to mechanical damage shall be protected by steel posts, concrete 
barriers,
or other approved means." This section does not apply to every pipe in the 
vertical
position that is located within a gypsum or plywood wall. This section is to 
provide
physical protection to the sprinkler riser since damage could impair the piping 
and components that provides water to the system. The wording does not apply to 
all vertical sprinkler pipes supplying a sprinkler in between two studs. The 
manufacturer
instructions, IBC, IFC and the NFPA standards are silent on the protection of 
piping
within walls faced or protected by gypsum or plywood. The only reference that 
could
be found is when plumbing pipe passing through studs within a wall in the 2012 
edition
of the International plumbing Code in Section 305.6 (305.8 in 2009 and 2006). 
This
indicates that in concealed locations where piping, other than cast-iron or 
galvanized
steel, is installed through holes or notches in studs, joists, rafters, or 
similar
members less than 1 1/2 in. from the nearest edge of the member, the pipe shall 
be protected by steel shield plates. Such shield plates shall have a thickness 
of
not less than 0.0575 in. (No. 16 gage). Such plates shall cover the area of the 
pipe where the member is notched or bored, and shall extend a minimum of 2 in. 
above
sole plates and below top plates. The 2012 edition of the International 
Residential
Code has the same wording in Section 2603.2.1 in 2012 edition. Several 
manufacturers
of CPVC piping have references to protecting the pipe when penetrating metal 
studs
so the studs don't scar or puncture thermoplastic pipe by using rubber or 
plastic
grommets such as those commonly used in the plumbing industry.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeJDo87pFQWA8=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eNKsHgdyHF6DwMn5h015kOh7dHPKXUMtywDMj0hzk9Urt5TCTK2Y-LEU5wlZYmHBt_ryqEnBQP2FUezulaU4-VL9r7GQxafk5PpKsy7Y1DBgThogHwnHjoxRNHKFGfSfwBqK3HLBoFmY=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
by

Josh Tihen

"Corrosion Inhibition of Dry and Preaction Fire Suppression Systems Using 
Nitrogen
Gas"

Wednesday

April 9, 2014

Free to AFSA members!

11:00 a.m. - 12:30 p.m. Central Time

1.5-hours
Register Button 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeycQWil74FYVgNOzMR8gaf-rUznrREirEikIroxclO7QFvFDMG42lsVHzf9jneRVO]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Sept. 8 - 19, 2014
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrqYZWWN7R4JNzAC_BOoH_bOknBpShPuU8O4nw-Sg-3MdQn86c2HSNhwrccJ6fG56ntQuKlJ0ymt6114eFb30Y2CB4ItXbjgPbr5FaF4FEYmDMAvmVrMIzdaM3T_6fNRWLQxNKQSxlfhhAP2u5V-T8MRro6tZyEEVjqatGCu-jYsvAEQTHFjMTQBy208uCdMV9wb8OT76ZbUjA==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mroZuuk43n6lZtSqmGmpBzfFbGZoxCTwE88G3FiBhNrWww==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeycQWil74FYX--qHikVCGWIydqhP6xzUiwzT2ba4FAH1_7Sz_c8AItCeb9kMwYeYP]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeycQWil74FYVqJH9kNEyVutIOsvgg9tppqfw8arTV9vVjd4EDDjfJ77BtK5Ahx6bG]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeJDo87pFQWA8=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrqYZWWN7R4JNzAC_BOoH_bOknBpShPuU8O4nw-Sg-3MdQn86c2HSNhwrccJ6fG56ntQuKlJ0ymt6114eFb30Y2CB4ItXbjgPbr5FaF4FEYmDMAvmVrMIzdaM3T_6fNRWLQxNKQSxlfhhAP2u5V-T8MRro6tZyEEVjqatGCu-jYsvAEQTHFjMTQBy208uCdMV9wb8OT76ZbUjA==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mropJa3inCf3ocPXhBVAVig9pU2CVSnbYKCWxPzvK2tZ69envp1CHBDiwwiJOe4VHtQA-9dU0269og==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrp27VDDOuYHoAxSZWXnS4PwIeKA7jP08LPewQl-KrWMBXBpCI1GyjPaiqxwIUrnQkWIEgk6_NDNaA==]
National  
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrpo95Qalt1Vx13HmeSgQSO4DbEwgXFAZI171girhzUHSg==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrpo95Qalt1Vx13HmeSgQSO4DbEwgXFAZI171girhzUHSg==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mroDPwIAs9qrr4WUKRIv8tdfmW6nL694yrA_O987Jxi3z3WOXEcd3-ImV6noqe77mCkzwlLPlO8tfA==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeycQWil74FYWfJs_KQLzdiL1nG1Pa85gF]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=0018OVWtDJqffjXZwpyLOM4xl_qZuivteQmB3sDZ6jJJYF7tCfbeSrNIEAXsHWUAH5eOrYSSiq7mrodlzgeWHgpp7bw1PLcKCTeycQWil74FYVUEOyP8bDr2NzlBZKQwnH5gDaSF2rP8w9HBW8iwRV8X2M8sTtaJ7l8]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116979101928&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001T-vvSkQsynwS1RbOPU79iw%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001T-vvSkQsynwS1RbOPU79iw%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to