July 20, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Cold Soldering Movable Partition
"Two sprinklers are installed on opposite sides of a folding partition. When
the
partition is open, the sprinklers are less than 6 ft apart. Is this
acceptable?"
We have reviewed NFPA 13, 2010 and 2013 editions that you indicated as the
applicable
standards. Our informal interpretation is that although baffles are required by
the standard, it may not be necessary for this situation.
The movable walls or partitions are common applications in buildings to separate
a room into smaller rooms. This requires sprinklers to be placed for proper
coverage
when the movable wall or partition in both the open and closed positions. When
the wall is open, the sprinklers are spaced closer than 6 ft where a baffle is
required
by Section 8.6.3.4.2. The intent of the baffle is to prevent water spray from
reaching
the adjacent sprinkler. This is to ensure proper coverage by the sprinklers.
This
is different for your situation. The sprinklers are spaced where sprinkler
coverage
is still provided even if a cold soldering event occurred when the wall is open.
The baffle is not critical for this application. Thus, the system would still
operate as designed without the baffles. The cold soldering may affect the
area
of coverage of the sprinklers. Evaluate how much area of coverage may be
increased
from the cold soldering. A sprinkler may cold solder but the operating
sprinkler
will also prevent the condition of flashover inside the space. Since this
situation
is not specifically addressed by the standard, discuss this with the AHJ.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOCbjacqAotcJfoplYvLp_g0QlxMLFIENIf3_polkTuLiUMCzyFfErll6fCfzreIrMgiJo8UxH6gaF0oM3Il5M7N7yHLUFX-ybE0qkNYqAO5nvKuxfX6GmvkAD03H4Izjmw==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Join AFSA
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOPG_DkgI0c5zzVQJtNjpNoWM6QrszsIv3Fj0C4Ai86vuYfxfhAIGyCycnZJ-7F3Qz2srjbYV5R1LEK3tBW_0tU3O7XQrO-yfSRMjF4p8WB_xVBMRwrPOpkXmsFt7wL_qn1BC8n0VcKx1lVsx2h5LbVe7Xey8vdagCqwUusE3-KSa&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Scholarships
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOPHMzIIcI2uVOHdBdmmaeisJG9TnZWDdWQUXrtP-VmMiay-q6nd3Cq80dQ4YT7wqsbRx9kOTNmyXe5SGCF3rNLgqnivzuVoM-mpuLoCPsBx8Ilx2nX4Bh-TNggktKOwBVg==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxON6WPWlT-Tx7rMRy4w_7wLsnvQGdChkT7wq-Tm1-1eTC-0eEZkZX-zCOc3_gYlD9k1z4jR992olYE_lpexu2VqXmvedoAj_nMgqCGVmPyH-1BREyi2sNacIqSBMolxpaA2Eyui1bm7Iy_NlLT8YKtVWQothWkJEh5JltYDcPaDJUe7K05yVC4NE=&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOCPKmg8vOEF-3jzgks7smEZWXomb65ThjsW5GYituIGps9wnmIcrbUo9XHiI5eXChysbsZj5eJwgDb2aN2C-lox3EAKGf2-rm_t1QHLEPg_akgWjxk9nTz7c7MkHbus_xygVFgjRPWcZs2FVvNpmpAJt2UTkd8zT9A==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Informal Interpretation Request
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOCn88FPRaYCytTomICJBcqneqjKt8zPklEHbxULv4uE43JGBa7rYnsS2YC1dsz0OTZLaNG52Iqf3DMW9n_1S9MIX7j8c7nEufPIZck6vMSVo3lOLDtEKS-rPmUiK_F1nnd4hek8GE5GnedGsAQkYuWEl1kufzAkc4Tkczs7zOm6h8Ro_u8a3SJH52hhOeCMHsIGRpYNYikhVWBZYGrtZa6HH7YGCI_xt2EpM8H5b9muA&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOF4MYNAKVVW5-BDAe0SObv6q0-xWdH96bddmSdEqLXLAnG5-4VtopyIQ8Al9uCIwlD0GbaMYTwVK6Sl4HArnkbF0iAsNBD5ElLhSI4haG4HbhWefXgsLBF0gGd6-H9ZCy7MNStD6O3zJucBwSKo3Mqo3-NuRcntHiSzxCaAl5ZX9nUPl9TsZjsNCOXOAXOnmJw==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Archives
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOMSJFQ8KrMODAPq6DSW8e1OA1pSe6zOH6K7GiTx_4FYLnaqkDQeAecNtykxk9PIPG6Waiwy_IcpqTPCSwJIhlk02yJ5IGNKEUF44QRsxg4d7557kL7VgqGjSZ-7MW8X0Z4d4aHLtIZWe6iSQzS8aNS0eK9LX6RWc9AlKlZs3LoqKjHqnNzQdI2HKsvHIc2ScDw==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOMSJFQ8KrMODS0ZK3FoWOHRGzOGMhhXp594PCVTuXS-x--jdZz3_oHBtfuCTkZvcclXxhU2k2sN91ZocbvJumVh8pxm8qYjjh2brWRW-Kp0dBN2Gj3XNQ3mUK03HCIfh6Q8VXZiwVEQh&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
Sold Out!
November 2-13, 2015
For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
SA Cover for TU
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxON6WPWlT-Tx7Aj7navZSb_KR_-zRNh1Kqy2vM1wkIQ1etS-rxVXiSlT3g09HoBdPK2hw-HFtKqQINX83POxEOvn-Tlgl5v6lPFfjgLvIxMOmZvBZWtn92h7DI-nCvkMPd-mxHH1OROPb4-ASQWUI-dldBUlLikgTmw==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
Free Subscription
to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOExdW75Qje0XOa5GW_RV5nvXsLxo7D_6VfUdbQcUYsOj44XavG0WmpKvot8IsYwTIZy7Dmsi8uaDi3UPaDIclT49AiJsYPG5qyr03zezxtbjf9KlSI5PupXVJG_Tcp3JhGmQYzvBeDjXLyG_0LSlex7idh3sd7wV1w==&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition
[http://r20.rs6.net/tn.jsp?f=001yOrq9XYY-gB6QjEaO9ZbGmUzUBeSG2obK_E0pNsIbp_UpIkOI5LxOO2jI6CAQYbC-QHG6icHt6_i8vzPwj3a_qa6v6uwHvDUNNcqsqapBno366cC2cUZDcPewm4eLOtZn7t-2fzopcW4U7ohCEtXtnzHI639R2QGxTcbPx1oHP2n_FRz1zIpWlTWQn4IeaAsmSRJ-FCBkaIyhrzQhZdUGgC5Lrik24RczO8YvdsqAIqg3NvdLeGguEtucPy2fNmJ&c=G1m5RISCiarOFoNGlDDFv9AAqBrO__sHqc6ZywTB3_D8CKr2DRn9lQ==&ch=cYiw9bncLhEEcDxtn3YsJ-WfjhzUB11mOQqOyhHm5crHD1dWhAJFxA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121642633432
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=71b819c2-91aa-4345-88ad-b55c2c234baf
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=71b819c2-91aa-4345-88ad-b55c2c234baf
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org