July 13, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Sprinkler Placement Under Obstructions

"When locating sprinklers under obstructions, Section 8.5.5.3 does not seem to 
be
very clear on the placement of the sprinklers.  Also, if the sprinkler is not 
located
under the obstruction, is there a concern of cold soldering from the ceiling 
sprinklers?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that the next edition of NFPA 13 will provide additional 
guidance.

The current criteria are Section 8.5.5.3.1 that indicates sprinklers shall be 
installed
under fixed obstructions over 4 ft wide.  This indicates that the sprinkler 
should
be located directly under the obstruction.  There are some applications where 
this
is impractical.  We know that the heat plume will spill out the sides of the 
obstruction.
 The next edition will address this issue with new text as Section 8.5.5.3.1.1 
that
will state, "Sprinklers shall be located below the obstruction and not more than
 3 in. from the outside edge of the obstruction." It would have been cleaner if 
the text said no more than 3 inches beyond the outside edge since an extreme 
interpretation
could be the placement is still be under the obstruction but no more than 3 
inches
from the edge.  This aspect is clarified by additional text concerning cold 
soldering.
 When sprinklers are located beyond the outside edge of the obstruction, that 
sprinkler
will be subjected to water spray from sprinklers above and can create a cold 
soldering
condition. One could rightly argue that it doesn't matter since the hydraulic 
procedure
only requires one of the two sprinklers to be included in the calculation on the
 premise that only one of them will activate.  As it turns out, though, this 
would
be incorrect.  Just like section 8.5.5.3.3 of the 2013 edition requiring 
intermediate
level / rack storage type sprinklers under open gratings, a new section 
8.5.5.3.1.2
with require the same type when a sprinkler is located adjacent to the 
obstruction.

Regarding the deflector distance below the obstruction, this would depend upon 
the
construction type assigned to the bottom of the obstruction.  Most obstructions 
seem to look like unobstructed construction.  The next edition will have new 
text
as Section 8.5.5.3.1.3 that will state, "The deflector of automatic sprinklers 
installed
under fixed obstructions shall be positioned no more than 12 in. below the 
bottom
of the obstruction."
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ35GNxNsLrp3RkCaQHP59_1YO5JHdYG_rRMuz0-tpOXqatHfq1TLgVXjHPvY8C160sBd9LGSKLYbMrQu528nSbvCIJmpMtsKz8tfAMONxp96nlp1eVPvC9MFsKxGTA_Smw==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ3_A70EfWtT7HtMzliEDsY5C-fcbLJcLJC2-gKZSa_AJKLM4uUvC7eIs_y-MD5ijkxXSkdtz8L0YMztj4bAPRu7HHaRmqcPOE1JUR32hpXKUmSW0H0EWVSgcgl-rGAbicjJQeGNLSN_s1v3BzY9GOtm1iPq3nYhLE7QuKkUaLAvS&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ0l4vffm-7f5zBB7WdPGgIlpolwnserwIGgXzgS9zVy-f_sUvIYY8suLqoqLleiSSwXHJRu9mguZNMp96KvCUrr4yqidB7nQZJQ065XcDQsZYjUynL69w7WOvxUdi9D8uQ==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ5agyR4_96_na0Urimf88TQCMWCAvaaPAqfaCU7AGZTNTmOLBLpeR6FHn3A3Ae-_p-CMWsR-Gnlz4gnbxJ9DZ5sNwx23uuUc65_5q0OchwnIiD2QZWPIiPVcPn2QZfzDk8CybJhXSzl6Uh6oY2ab83xWA-RaMEOGtjNaDBKfbtRMnNMjQztiznI=&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ7YYsycxXw5LBI6fIazkGF2Z5Md_zlSDijGSAtC_KxrhacT23WYjNOKbGJ0M7w5tCMZWZ4wdJ5paZk2fvEuc7bHhL6liG-qq_4ntPmQ7GudmtKblr1V3kSwJUUkIC-tDlVUH_zb6mn1zYHoycvdIs8pf-d5ezODqsQ==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ-n3xlIhbSOEe7sG3PJ6NbOQMAtspUEV6l-RhH4Gebzbj4S9zoqAJpe1sHOp1Wkt9FwoxWGyo3lJ3O_CZqm3-Co6O3o5PY3M_HfYzr2CG28qslOlmQAx_sKEcpvTgq9lHWkrYW9Khuk7TR3ybMe6uUyCrYLF1OCM4wFRBUh5sAP3ohN8SP8QFPx_x4STl5RJUgBIZfYPXoLW_Sf671GDOvC93VqbOk5JRXZjRseP0o62&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ85HXBjyvmBd54kVmRqlvc-l6-Zqa8RgZgFD9tmiEFlLtLIkPb-mtFUdOC7_YVvMnZjAI4a8mCfHkOx6kLGYSLxnhZGm-eIF4CLlJXgkhaoDC6Jq2bcaA0Gz5xc_r16EtEZEQkUY8Lwqoh9FLIzP9-dpt_sjOTu4fa2TTQNinldmfdK3UcLkCN24Jtvk2UK0VQ==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ9GQQ3QFDF2sd87ly2jDesn1mnC8o5ie8tkYcABK_O5ReZ5YHyVkakcCs8wNTdfdt8hzkYFGcKTJUlRlnvRsBsZR3bNtDYdaKXEMpkx330moH2qJEYaq5xIzs3PWLFUekVMEalRY-EU7dWpvgM-JgxWIKrD3waA8Ouy5_L_SRNpYvCO6hX35qNAiVSYwIBYCyg==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ9GQQ3QFDF2s1N5WYx9m0QAUxf9GuR9knXeJFz7Jv8HUHM-cPTgJN-pTKi8eozguj6qecfCQJ8iZh_U1f2sHdv4o2b7MXuTaFzjD6NZiTmwxvkyHh7Poj0cNEvUuXIFuGe2fPlgujs3s&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
Sold Out!
November 2-13, 2015

For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ5agyR4_96_nUDTDToA_3d0HGxJ93-DtXz_km-IE2RV8cLvhPNpBYH5sqtYC3RVkCUx79i7f0TrwbXfibQ-DpYBhi1VymKZ5jUfakMMODW6XUKVpaUbp9s9ZAryhAcckHN2JG6tXcTkFwRNdraJeWipJ6YZLemznIA==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZwM4-lFc6ga0H-spoAFHHV_kkl8rGXpL1yrZWY1l983ff5RxXsrZRIWMOovp7QSXCGq_HkToOGEQ2M3BNrQt7ayTqG4gDIil8WN10Mguen98C6NP9Gr4Bm23GbgTmfjYMSIMb2c-X2AIDJEx6qaYxazFj9ihQfDx2g==&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001Nt0KWuUcKTBL0VzhVIb9uk7FiXhypX5N5KP0a2IJzt_09iVpibdfZ1uXq6YjWEFe2xEqDD6cbLu5Y8Q23pNPdYpSM2a_LKsDpLBFIjOKiaJwU57__wwnrQrWhyvE5OpXJEV1OPmPxA49dmJiavO35hDZ-RyQt9GBsGmaenpbgg2NDMTeFx9HtIZXlgPMq6caB0pQYL1xWfq-AawdOVzlZT0DrJa2y3bNZKtS6QG72WXyt-Wc8T0NUuDLfdw_V2EA&c=f4MQ7qS9I5h4L0rXfE0F-9LaXAO-18nQnFPalwIkWmP9pCYCQC4Mow==&ch=h64VOV1xuWPj0jXrcC65cBpEEDzJplob1U_dgVsfgtT29ayZ5UeEzQ==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121574430036

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=26210297-5d12-4936-a242-62741977f200


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=26210297-5d12-4936-a242-62741977f200


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to