August 3, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Hangers for Insulated Pipe
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

May insulated fire sprinkler piping being installed inside of a PVC pipe be hung
 from the outside of the PVC instead of the hanger being attached directly to 
the
fire sprinkler piping on an under floor fire feed main installation?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that the NFPA 13 standard does not specifically address this 
application.

Section 8.16.4.1.3 does allow for pipes to be protected from freezing using 
insulating
coverings, frostproof casings, or other means of maintaining a minimum 
temperature
between 40 Deg. F and 120 Deg. F.  Chapter 9 does not address the piping support
 for arrangement in your question.  The space between the inside of the PVC pipe
 and the fire main will be filled with foam insulation.  It seems reasonable to 
apply the hanger on the outside of the PVC provided it will maintain its ability
 to support the pipe and the weight of the water filled fire main.  There are 
several
issues that this unusual piping installation raises.  Chapter 25 requires a 
visual
inspection of the pipe during the hydrostatic system acceptance test.  The PVC 
pipe
and foam insulation would prevent this from taking place.  Another issue is that
 the fire mains would not be in compliance with Section 6.3.7.10 for pipe and 
tube
identification.  It requires that all fire sprinkler pipe over 2 feet in length 
be visually marked with the manufacturers information.  Since this situation is 
not specifically addressed by the standard, discuss approval by the AHJ is 
required.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUfI3w6JNci5D4MxwoSHQkrdCqGyXpnWucSIYqN2LvBBvBBgsPrazUQxCI-6KGp626McBVLNLDxuwLXF6V5FskuPecQTjEDyzaB0EgKpF2sd0CmCWa5hKhRwJpkiYrBYbiA==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUffNCcrazT54l35uO4szIKHD1_G7mRmnftKcD7Fvw6okATiFV69Rz62Oms_80cKWo2MNxiFSMWgm3vT1ioQ3Kq7qcxb0GR_JblBU2NOD_RV6QW_oI5kLGJCIlDNetU6JFrS_GebrsES9URgxwi-irPJWA6ghxFLUIPXC-7q3RLaz&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUXHJuPBZORU-j5nEr3bO7i2q5isNFIvYACRHztu97MfRaHJNX-28wAJ2HyGTgklDpdJPa242KsF9I6qduUgxCTvUWGtCjOLoadX8YVlDNk5hJ_I1CzTFYylnYufEo_7cNg==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUUiKcKn6O468qvs4LcRXao_lwUJb5uiZ2PTbYkDtXNUgiL05j493sLPrHqRw-HL7_4kwy4foxcRmUjYAuYatlzTYWfNwlwhF-ZCBnSUGpjQ1iy2qEx_POI9hkBu-MKDU_jGsLjHtMQ8ayUWkQTPTCgcy7vODvv7PFo8kf6DM_GaLOP1MFM0YD1A=&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUcGb3eqYXFVO1zQXY2rO4Grjwo3m6h5Tdl13gmdJqz__LI8GLWjYrf9YcAcSqTmXK19gX4HIfdn4v2MyAvSrSFhXAzU_G714u9wb1c97_hHDS2aZya0mDHmSiUSFyKXND484HaxiKO60f6YBVJx4xYRBZU7nedrZlg==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUQI00H9kp21ohDVIBEYsg7P4ovVItSPqn9a7l44NRvK3n7kRMbRqSr2iwZf7KUD5FL7eujooe7m_J9sMyGCShhWtcy01GebKEwHaY8aAREkuGL0SWdOp1xprzXbVHOccYilpoMEUO9QFmMH6zr8sQQ23D1MGr0PUcwLkY7EZo14YLmwADFvJFdLhNUITcMzQdNy6A4GpkWzqg6D_-pcqJjogIoF4hb7o-XqAGtXy19Mt&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Liink 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUcrcj8nAt1nIHbkfV94P4BTOb8dVo4TitAjruD2gSIDin9YlS64oe1zjbrYBgKaf9f-aFpbqeHRVavDZPaErBI6t2UaWu5To81OpyxBrLij0Cu7IweGRiN8_YOFSiTXJ2Z-wRlq8Iw8Cwz47IztIUFPvXqQ7qwVkB2fSYjTobPHIaMbrOyYvqNRkydUdjdtexw==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUfcQhfrgBHMoFyU5iBw-qJFSjed5K7VlozOe1vWKtjzbCcNe7JLMFzXA-no5TDGTJSvY5K5nbGfsg8gzhpnzCefEf3Hq0OSnt4oSvSHBZZpXpyVn6N1aQKPZ8qYp3jZBK3O87zqCg6b2&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
November 2-13, 2015
Sold Out!
September 14-25, 2015
Sold Out!
For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUUiKcKn6O4688PQWDdhBFoCc9Sh9ipGEZlJkIZ3D6AYcL6ekIKqNID7VpaqWWZxo-z5_WYJsWouMLDgnT4UcAZpDN3MnlrXnRVzQNCUjg58M0CVUubkkYgkDvpkyHRIZKYpmAdKmy_rppdEtS4l9WeBywHS1RQKrbQ==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUYrEHzf25_u3-048L_dR2i7ooe2-Rfb62gGmNgXugjuYbhwSPQC31Bn5nufbw9Z6ZNzgS0UAxDt8wJHs-ahcbuVBFStmeBiUzYRP0ZfXCDtiioAwJGHLS445tqdae3DBxf1vLocr7qWGlY6KGSLcTU55FGG7WsmsLQ==&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001dmlZBQW46TXTBoCfMvIe7hz-43sHQUM4o7NIGLLBPLfNQouvtsLkUeXvENcwn8NOAU5kTgOq-0AwEmiZTydnq65dnbIrT9qnn-zSgd75TGckTyWMHy4cZrhMiQFX9Ldlwzsm3ikrd875IomllZLuKWwC0z5Iqp6cSXW9cfdU5g6nQfsEInXHcS3D5WZl_c6tcaxJnKOTWV_bD33Lc4oJldduOoocxXRaI_jOru6FNK4p4toQqDPUsPAP9Y_S1LzB&c=z9ZuaF3AWefboq7DAi1tQOw9xX4VajqSQaacUjPYt4Al5lamOSqv_Q==&ch=U4hO-eU7HMXbL26nxDHF76hvxthtuHt62qEVmXyykyb8vHyXHWBYUw==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121765419555

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=2dc6100d-e0b1-4e63-81ca-83b758b39d8f


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=2dc6100d-e0b1-4e63-81ca-83b758b39d8f


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to