August 10, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Limited Area System for NFPA 13D
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

"We were required to do complete drawings and hydraulic calculations on a single
 family residence new addition of 104 sq. ft.  We are only installing one 
sprinkler.
 The AHJ refers to limited area systems of the IFC that this is required.  Is 
this
correct?"

We have reviewed the 2013 editions of NFPA 13, NFPA 13D as the applicable 
standards
and the 2015 edition of the IFC as the applicable code.  Our informal 
interpretation
is that limited area systems can be applied on one- or two- family dwellings.

Section 903.3.8 for limited area sprinkler systems in the IFC indicates that the
 systems shall be in accordance with the standards listed in Section 903.3.1.  
NFPA
13D falls under this section in 903.3.1.3 and would be applicable for this 
application.
 Since this is a partial type of system, the code clarifies how to comply by 
applying
the applicable Sections 903.3.8.1 through 903.3.8.5.  Section 903.3.8.3 says 
that
where a limited area sprinkler system is installed in a building without an 
automatic
wet standpipe system, water shall be permitted to be supplied by the plumbing 
system
provided that the plumbing system is capable of simultaneously supplying 
domestic
and sprinkler demands.  Section 903.3.8.5 requires hydraulic calculations in 
accordance
with NFPA 13.  If a control valve is installed between the water supply and the 
sprinkler, it should be an approved indicating type that is supervised or 
secured
in the open position per Section 903.3.8.4.  When referring to the NFPA 13D 
standard,
there are no references to limited area or partial systems.  Historically, NFPA 
13D provided guidance for limited area dwelling systems, but it is no longer 
included
in the standard.  Thus one is forced to refer to limited area systems addressed 
in Section 4.2 of the NFPA 13 standard.  The commentary from the NFPA 13 
Handbook
indicates that certain codes or local ordinances might permit the installation 
of
a partial or limited area sprinkler system.  Section 4.2.1 indicates that when 
partial
sprinkler systems are installed, the requirements of this standard shall be used
 insofar as they are applicable.  Thus residential sprinklers can be applied and
 should meet Sections 8.4.5, 8.10, and the manufacturer's instructions.  As 
noted
in Section 4.2.2, the authority having jurisdiction shall be consulted in each 
case.
 Hydraulic calculations should also meet the applicable sections of Chapter 11. 
 Since the AHJ did not specify the protection criteria and NFPA 13D is the 
applicable
standard, using the criteria from Section 8.1 seems reasonable unless the AHJ 
specifies
otherwise.  Regarding the complete drawings, NFPA 13D does not require complete 
plans.  Section 4.5 indicates that documentation shall be available upon request
 to ensure adequate water supply, listed devices, and adequate sprinkler 
coverage
have been addressed.  As such, the requirement for a scaled drawing should be a 
written amendment.  These issues are worth discussingwith the AHJ prior to 
proceeding
since there is confusion on which standard is being applied.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UExOjMwUKO6RJ-MX5RFd0hYeK2mApU-YbscBcy6Hf9jzP116l-pkliEdP9hPQMk4K0xm9tRf4v0AgqqKuSb2H5MJ6kU8NNJooXd9AFDqHsdsB5jCFPOa25r-NlegZkCWa2A==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE4Itxwn_dgwa98l2I6XsSNJLR5RckbfbY_SivPTEgqFkIGbXPnEbsMI0emis8CdBc_2btXWqnLwY8y7N64AOFwDShenPRki7UNnL2UHiqR561CJ9B3hTynlC49R5T6wE9zeq-0rY5gKzRyyKh0YiugM8-sxRqBbKXDc0EQP7HL5J&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UExN4VF4Pwh_DUx1X-zhLnnFat9VPYl9mjz0C9KSQ02u0Sn-CoFURLTEAMfEjcOM6J2KpEJkyf4flxhfHkeKH4sQ2H7YckR8dK0Z841HKCRjX_SeBp8RD8UdQGfHekkpzNw==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE7nQDcq_Nt9I_mvAj3Cj9xkVDYtMup1Ef3xVtsQmDxfh9WKk0dri7hnrH7yqnMTYmeL0ZJpCiUd_pgHLISiWU13NxCU5IAR-glsCYycF6RKIni0ozmtkAl8ejsprI28IkN15VP8PT-wZRZ4KdovBtOAGg0141FNg_AjJY9OlxSi1Affwq7OOnBo=&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UEwwC42S6fjDy-sJj40yMujf5-e0-Mu6m1UxIFf51v0KiNn4hlsyo-F_zhXrCcHNhbywPWiSzj8k1R4PZ8das-rNppDzpwxKi4hvFTslaM_VAklSjEUvVpHBIORqq3O4r-Bt5tBOyCb8HLXOzILFwBuMIG4P-jC2l_w==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE_wYWa6RUtf1wCYCx0NOHZkqWhdF2hNpWJnCQ-lSzh6Tn-AHwj8tgbKuIMexVf1IELB5bqLIS0oNptKu9TGrTYtbRiS42sx648dB_unS1sd_428yzKam8J-80-pV_Y1OwScXBtgeKPtaC5fKVQrhhegmZNNjVqooRyZU175VPoBwlncZY2pis-sYGzt1IB_4DznqDOkgtqr4_65G82VNKBpYqdFAyaIeJJLMsLUMmyRv&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Liink 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE8FhgHeoafsymFr5vE7wQjxW9GnIuwI9aReDY-Oj1rVu0blBYUiK5vho4qPQwnhim0Uq2PgTPWV9riI8UgMsTg4uTqz_rLtMGO0RL7w9ZLijWTlhXFzdryS8HjwePcBtu7A0zA2i7BHvUQAulVFa44SK2QQmMb6wShZRNlqwU9VtyLBv7P7Cof4rWHuikGahtQ==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UExxLa9fRK5MwS_8TGcKrwI9Z50o6xlbe0RZxJfKp-GHk2GhxJTq7FaoH5m0K4NiG3HR-QxVw9br_4DTGPRQkzekaYgOvQ7AFGHmjf1R2S4v6RFCHMQeR4SGbrn5X-Y2VV0KQDLM60Ru4&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
September 14-25, 2015
Sold Out!
November 2-1, 2015
Sold Out!
For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE7nQDcq_Nt9IU_x4VM9C8JqhkvFp4WKT8nZVXRw8gfVVNaCfdkSfr4GYwp88JBKtOrNUl6aSa4DfdmOlCOucN63gL3OVYwTad9v5WFlRswwOSbWtD1pyWVVGGJxhxCJpk5c4YdrnAMJjAHzhMO_2v5lkuwtE6bu0QA==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE29yd0gHaS1DU-o0KeAkGyCNahR5_4zxUgZJAr0eueaUNQ045YZSepDrrHC-8Q4cxTJiLtFKh5a_HZgl3gT_BUYMG0dYC3jOjJx4ECs_ULBqUfUfaWZwlhjGQc3WyXcVyvpQZH69EZntyE3N1FyX6zU4hUMy1kp6eA==&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001LNP4DlKcLtIOHMCVYp6b3bFDYodCTrXqtTcb-D7dGE8K-7OQAq2UE1uUhY-Gf7Ibm5minSmOJEosW3T2-IduCMLkK-gA4nh4jLnmEI_oGCDRcE7RdlqiW8lG5KqUDESnJydhyiyYk_SDCoy4RF-89Zq5Dv3cc6jpsHuvcvlryxRy7VYgRNkCH9-jfxjODLF_88liq30UTuhvW7v5HE-cTwxw11xzc4TzamN-ZJj0QBuYrof7VHyIROYElJQkZhOL&c=B3acHbshmqtLacXgmJH-b6d9sFAXWQOcZom-XGxmQNmJibqrWPCwGA==&ch=0KcR8FbquUVuoxP__9-yTdxC9avWuZFB8PFTUaTTL50gZDp99R8ZnQ==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121831364006

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=8cb5a38c-a9d2-4aba-a431-2e80b997d0bb


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=8cb5a38c-a9d2-4aba-a431-2e80b997d0bb


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to