April 11, 2016
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Sidewall Sprinklers on Opposing or Adjacent Walls

"There are two sidewall sprinklers in a single room on adjacent walls with a 6 
in.
deflector distance from the ceiling.  The distance between the two sprinklers is
 16 ft and the opposing wall is at 19 ft-4 1/2 in.  The specifications for the 
sprinkler
(in regards to maximum coverage area) range from 12 ft x 12 ft all the way up to
 16 ft x 20 ft.  The coverage area is 16 ft x 16 ft and the AHJ is saying that 
the
sprinklers will cold solder at 16 ft apart.  Do the sidewall sprinklers have to 
be spaced 20 ft apart because that is the maximum throw of the sprinkler at the 
highest psi per the data sheets?"

We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard.
 Our informal interpretation is that a sprinkler shouldn't be located within the
 maximum protection area of a sidewall sprinkler on the adjacent wall.

There hasn't been any testing regarding your application to determine sufficient
 distances when sprinklers are located on opposing or adjacent walls.  The 
minimum
spacing between sprinklers mounted on the same wall is 6 ft apart for standard 
spray
sidewall sprinklers and 8 ft apart for extended coverage and residential 
sidewall
sprinklers to prevent the wetting of the thermal element or cold soldering.  
Sidewall
sprinklers located on opposing walls and adjacent walls could be prone to cold 
soldering
so they have to be handled differently.  The conservative approach by the 
standard
is to locate these sprinklers outside the maximum protection area to avoid cold 
soldering another sprinkler.  This is addressed in Section 8.7.3.1.6 for 
standard
sidewalls, 8.9.3.4 for extended coverage sidewalls, and 8.10.3.4 for residential
 sidewall sprinklers.  Sidewall sprinklers should be located on the same wall 
for
future designs or located to prevent cold soldering.  An alternative since this 
is already installed is to apply the spray patterns from the sprinkler 
manufacturer
for the type and style of sprinkler if permitted by the AHJ.  Sidewall 
sprinklers
have an upward lift to them and then the water falls to a lower level from the 
ceiling.

 The spray patterns by the manufacturers for residential sprinklers show that 
the
wall wetting spray pattern is lower than 12 in. from the ceiling at the 16 ft 
distance.

 If the sidewall sprinkler is wetting the thermal element on the sprinkler on 
the
adjacent wall at 16 ft, then the sidewall sprinkler is likely providing 
protection
at the 20 ft spacing.

<a 
href="http://files.ctctcdn.com/66430f6a001/fada4328-b80d-4a55-aefa-bb4aecf8a865.pdf";
track="on" >Click here for PDF Version</a>
<a 
href="https://www.firesprinkler.org/technical-services/subscribe-technical-updates/";
track="off" >Archives</a>

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2016, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
<a href="https://www.firesprinkler.org"; track="on" >firesprinkler.org</a>   <a 
href="https://www.firesprinkler.org/membership/purchase-membership/";
track="on" >Join AFSA</a>   <a href="https://www.afsascholarship.org"; track="on"
 >Scholarships</a>
<a href="https://www.firesprinkler.org/education-center/safety-training/"; 
track="on"
>Safety Training</a>   <a 
>href="https://www.firesprinkler.org/technical-services/";
track="on" >Technical Services</a>
<a 
href="https://www.firesprinkler.org/technical-services/informal-interpretations/request-informal-interpretation/";
track="on" >Informal Interpretation Request</a>
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132

Reply via email to