December 21, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Roof Outlet Piping Arrangement
"In Figure A.7.3.2(5), a non-rising stem gate valve is depicted.  Is the 
depicted
control valve required in areas not subject to freezing conditions?  Where are 
the
requirements for this control valve being installed in this standard?"
We have reviewed NFPA 14, 2013 edition which you indicated as the applicable 
standard.
 Our informal interpretation is that the control valve is not needed if the 
application
is not subject to freezing conditions.
Figure A.7.3.2(5) is an example of an arrangement for piping a hose outlet to 
the
roof.  This is not intended to require this exact piping arrangement for every 
hose
outlet located on a roof.  For example, some buildings have stair access to the 
roof.  The outlet(s) is located either within the stair tower or on the exterior
 wall of the stairwell.  A control valve is added so the piping exposed to 
freezing
conditions can be isolated and remain dry.  If needed, a ball drip is added to 
remove
any residual water from the piping.  The control valve is not desired in areas 
not
subject to freezing.  An arrangement without a control valve would actually 
expedite
firefighting operations since the hose valve would be charged with water.  
Regarding
the control valve for the roof outlet, the references in Section 6.3.2 and 6.3.3
 do not specifically address the control valve for the roof hose outlet.  
Section
6.3.2 states, "Valves shall be provided on all standpipes, including manual-dry 
standpipes, to allow isolation of a standpipe without interrupting the supply to
 other standpipes from the same source of supply."  This is for a valve 
typically
at the bottom of the standpipe as it relates to the supply main.  Section 6.3.3 
states, "Listed indicating-type valves shall be provided at the standpipe for 
controlling
branch lines for remote hose stations."  The roof hose valve is not typically 
considered
a branch line since the piping extends vertically through the roof where Section
 6.3.3 would not be applicable.  On a side note, a proposed change is added for 
branch lines in Public Comment No. 5 that states, "Listed indicating-type valves
 shall be provided at the standpipe for controlling branch lines where the 
distance
to the remote hose station exceeds 40 ft measured along the pipe."
<a 
href="http://files.ctctcdn.com/66430f6a001/e85666b8-049d-4c68-9346-de1f7488669d.pdf";
track="on" >Click here for PDF Version</a>
<a 
href="https://www.firesprinkler.org/technical-services/subscribe-technical-updates/";
track="off" >Archives</a>
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA WEBINAR PROPOSALS
Do you have an idea for a training presentation benefitting AFSA members?  
Submit
your training proposal for consideration as an AFSA webinar.  AFSA webinars are 
usually 90 mins in length and are educational in nature (as opposed to product 
or
service endorsements).  If you would like to share your knowledge and expertise 
that would benefit fire sprinkler contractors nationwide, please submit your 
idea
for consideration.
C<a href="https://www.firesprinkler.org/trainers"; track="on" >lick here</a> for 
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
<a href="https://www.firesprinkler.org"; track="on" >firesprinkler.org</a>   <a 
href="https://www.firesprinkler.org/membership/purchase-membership/";
track="on" >Join AFSA</a>   <a href="https://www.afsascholarship.org"; track="on"
 >Scholarships</a>
<a href="https://www.firesprinkler.org/education-center/safety-training/"; 
track="on"
>Safety Training</a>   <a 
>href="https://www.firesprinkler.org/technical-services/";
track="on" >Technical Services</a>
<a 
href="https://www.firesprinkler.org/technical-services/informal-interpretations/request-informal-interpretation/";
track="on" >Informal Interpretation Request</a>
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
Jan. 11 - 22, 2016
Sold Out
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Reply via email to