February 1, 2016

Corroded Sprinklers
 
"We have been using a testing laboratory for testing ESFR sprinklers that are 
20 years old. The response time results are reported as "Normal" or "Failed". 
The problem is that they also comment on the condition of the sprinkler and use 
a term to describe most sprinklers as "Lightly Corroded or Loaded". This term 
is used when there is no visible sign of decay, but the sprinkler is 
discolored. Once they label a sprinkler "Corroded" we are compelled to replace 
the sprinklers, even though we would not consider a mildly tarnished sprinkler 
to require replacement provided all sprinklers in the sampling otherwise tested 
normal. Does the laboratory observation require the sprinklers be changed if 
they are tested "Normal" and the "corrosion" appears to be simply uniform 
discoloration or tarnishing?" 
 
We have reviewed NFPA 25, 2014 edition as the applicable standard. Our informal 
interpretation is that discoloration or tarnishing of brass should not be cause 
for replacement.
 
There is no definition in NFPA 25 for corrosion. The dictionary should be 
referenced when NFPA does not define a term.  The online version of Webster's 
Dictionary indicates that corrode is to eat away by degrees as if by gnawing; 
to wear away gradually usually by chemical reaction; to weaken or destroy 
gradually. Section 5.2.1.1.1 indicates that sprinklers shall be free of 
corrosion and Section 5.2.1.1.2 indicates that any sprinkler that shows signs 
of any corrosion shall be replaced. This taken literally indicates that 
sprinklers will require replacement. With that said, Annex A.5.2.1.1.2(2) does 
address the question. This states, "Corrosion found on the seat, or built up on 
the deflector that could affect the spray pattern, or a buildup on the 
operating elements that could affect the operation can have a detrimental 
effect on the performance of the sprinkler". Light surface corrosion on the 
boss, frame arms, and/or the deflector, or surface discoloration, not impacting 
the operation of the sprinkler should not warrant replacement. A degree of 
judgment should be exercised in the determination of the extent, location, and 
character of corrosion that would necessitate replacement." Thus if a sprinkler 
turns green, it is likely a form of corrosion and should be replaced. The 
commentary in the Water-Based Fire Protection Systems Handbook under Section 
5.2.1.1 says that when there is a concern over whether sprinklers will perform 
as intended due to loading or corrosion, representative samples can be tested 
following the requirements of 5.3.1 to determine if replacement is warranted. 
It should also be noted that brass and bronze will discolor over time and such 
discoloration is not usually considered corrosion or loading. Although the 
testing laboratory may label the sprinkler as corroded, past verbal comments 
expressed by representatives of testing laboratories indicate that they may not 
test the sprinkler if it has corrosion to the point of needing replacement. The 
use of the terms "Lightly Corroded or Loaded" used by a laboratory could be 
used to address any issues regarding future litigation. Thus, this leaves one 
to use a degree of judgment regarding discoloration or tarnishing when 
addressing the replacement of sprinklers.


Click here for PDF Version

Archives


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016  American Fire Sprinkler Association. All Rights Reserved


Quick Links

firesprinkler.org     Join AFSA     Scholarships

Safety Training     Technical Services

Informal Interpretation Request
 

   