February 8,  2016
Loss of Color in Glass Bulb
 
"When the bulb loses it's color, is that an impairment?"
 
We have reviewed NFPA 25, 2014 edition as the applicable standard.  Our 
informal interpretation is that the loss of color in the bulb does not affect 
the operation of the sprinkler and allows it to remain in service.
 
The requirement for inspecting sprinklers is Section 5.2.1.1 where sprinklers 
shall be inspected from the floor level annually.  The criteria for the 
inspection is Section 5.2.1.1.2 that identifies that any sprinkler that shows 
signs of leakage, corrosion, physical damage, loss of fluid in the glass bulb 
heat-responsive element, loading, painting unless painted by the sprinkler 
manufacturer, shall be replaced.
 
Since sprinklers are inspected from the floor, it may be difficult to see the 
bulb.  If there is no color noted, a closer inspection can be done to make sure 
there is liquid inside the bulb.  Rough handling of glass bulb sprinklers 
during shipment or installation can cause fractures in the bulb that allows the 
fluid to leak out.  This sprinkler will not operate unless the glass melts 
(2700 deg. F). 
 
The loss of bulb color will be addressed in the next edition (2017) of NFPA 25. 
 A public input as Second Revision No. 51 new text states, "Glass bulbs in 
sprinklers exposed to sunlight or installed in cold environments such as 
walk-in coolers and freezers might lose or change their temperature 
classification color due to the environment.  This loss of color should not be 
confused with loss of fluid in the glass bulb. Tests have shown that this loss 
or change of color in the bulb does not affect the operation or any other 
performance characteristics of the sprinkler, and these sprinklers can be 
allowed to remain in service.  The tests also showed that when sprinklers 
installed in cold environments were subjected to temperatures above 60°F 
(15.5°C), the fluid color returned."
 
 Click here for PDF Version 

Archives


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016  American Fire Sprinkler Association. All Rights Reserved


Quick Links

firesprinkler.org     Join AFSA     Scholarships

Safety Training     Technical Services

Informal Interpretation Request
 

   
Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15
May 16 - 27
July 18 - 29
Oct. 3 - 14
 
For more info, call: 
214-349-5965 ext. 132

 
        


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251


Reply via email to