February 15, 2016

Discharge Criteria for Car Stacker
 
We have a parking garage that is approximately 15 ft high with a concrete deck 
and structural beams up to 24 in. depth forming bays of approximately 14 ft by 
10 ft. The parking a garage has a series of car hoists to allow for double 
occupancy of vehicles being stacked one over another. We are trying to position 
the sprinklers to avoid clearance issues. What is the occupancy classification 
for this application?"
 
We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard as well as the 2016 edition. Our informal interpretation is that the 
occupancy classification is Extra Hazard (Group 2).
 
This was specifically addressed in the 2016 edition of the NFPA 13 standard.  
The 2013 edition does not address car stackers. New annex A.5.4.2 for Extra 
Hazard (Group 2) occupancies includes a new item Number (9) - Car stackers and 
car lift systems with 2 cars stacked vertically.  Car stackers are becoming 
more common and were added to the newer standard. This makes sense since Extra 
Hazard (Group 2) addresses occupancies where shielding of combustibles is 
extensive.
 
Clearance issues for fire sprinklers can occur for garage parking. The base 
requirement is Section 8.6.6.1 that indicates that the clearance between the 
deflector and the top of the storage shall be 18 in. or greater. There are 
times where that is impractical where additional sprinklers have to be 
provided. This would require sprinklers to be placed on the four corners of the 
vehicle. Annex material A.8.5.6.1 addresses this clearance issue that states, 
"The 18 in. clearance does not apply to vehicles in concrete parking 
structures." Since that is located in Section 8.5 General, this applies to all 
sprinkler types. Parking garages with low height ceilings and piping runs with 
dry pipe systems create clearance issues for the sprinklers even without car 
stackers. This usually involves higher vehicles such as large SUVs and vans. 
Even if the vehicle locations are initially specified and sprinklers are placed 
accordingly, the striped parking locations can be moved at a later date and 
impacting the sprinkler clearances. This application has robust concrete 
construction and considered fire resistive. Thus, damage to the structure is 
not likely with sprinkler protection. The beams in this structure also create 
bays that will aid in activation of the sprinklers and contain the heat plume. 
The sprinkler system should be able to cool upper layer gas temperatures, 
prevent flashover, and control the fire. Sprinkler systems are designed to 
control the fire and allow time for the responding fire service to finish the 
job. Since stacked cars is not specifically addressed by the standard in 
effect, this is worth discussing with the AHJ. As indicated by Section 1.5 
Equivalency, alternative arrangements are acceptable provided that the level of 
safety is not reduced. There is no better source for supporting equivalency 
than a newer edition of the same installation standard.


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


   
Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
 
For more info, call: 
214-349-5965 ext. 132




American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251


Reply via email to