March 7, 2016

Insulation on Combustible Upper Surfaces
 
"We have a horizontal concealed space above the ceiling with a wood upper 
surface and 2x6 in. wood joists.  The joists are filled with noncombustible 
insulation.  It is less than 36 inches between the deck and the ceiling.  The 
materials below the joists are limited-combustible or noncombustible.  The 
local AHJ is requiring sprinklers in this space.  Am I required to use 
sprinklers listed for horizontal concealed spaces?"  
 
We have reviewed the 2013 edition of NFPA 13 you indicated as the applicable 
standard.  Our informal interpretation is that standard spray sprinklers can be 
used.
 
Technically, this space does not required protection per Section 8.15.1.2.17.  
The insulation is an acceptable covering for the wood material negating it 
being classified as "exposed" combustible construction.  In other words, the 
insulation is considered the outer boundary of the assembly.  The local 
jurisdiction is requiring this space to be protected.  This leaves the question 
as to whether sprinklers should be listed for horizontal spaces per Section 
8.15.1.6.  This section requires a special listing when three conditions exist. 
 These are:
(1)  A shallow concealed space less than 36 inches in depth,
(2)  The space is horizontal (slope not exceeding 2 in 12), and
(3)  A combustible upper surface.

All three conditions have to be present (just like the attic requirements in 
Section 8.6.4.1.4).  Although the upper deck is wood construction, it is not 
the upper surface.  That would be the insulation.  Although it is a different 
allowance, Section 8.15.1.2.17 explicitly defines insulation as an acceptable 
covering removing the wood from the evaluation.  Since all three conditions do 
not exist, the requirement to use sprinklers listed for shallow combustible 
concealed spaces not apply.  As such, standard spray sprinklers can be used to 
protect this shallow concealed space.
 

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


   
Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
 
For more info, call: 
214-349-5965 ext. 132

Reply via email to