March 14, 2016

ESFR in Concealed Spaces
 
"Can ESFR sprinklers rated at 200 deg. F be used as attic or concealed space 
applications?"  
 
We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard as well as the 2016 edition.  Our informal interpretation is that ESFR 
sprinklers might be allowed under certain circumstances.
 
ESFR sprinklers would not be appropriate for these spaces for a new design.  A 
concealed space created with existing ESFR sprinklers from building 
modifications is plausible.  The 2016 edition of NFPA 13 added new text in 
Section 8.3.3.1 that sprinklers in light hazard occupancies can be an ESFR 
sprinkler.  Section 8.15.1.3 specifies that concealed spaces are light hazard.  
Thus, ESFR sprinklers can remain in place.  However, if the concealed space 
meets Section 8.15.1.6 for horizontal concealed combustible spaces, then the 
sprinkler protection should be listed for use in horizontal combustible 
concealed spaces (with a slope not exceeding 2 in 12).  As such, this would not 
allow ESFR sprinklers to remain in place.

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


   