April 4, 2016

Residential Sidewalls and Soffits
 
"Section 8.7.4.1.3.3 of NFPA 13, 2016 allows standard sidewall sprinklers to be 
installed under a soffit when both the minimum distance from the sprinkler 
deflector to the bottom of the soffit and maximum distance from the sprinkler 
deflector to the high ceiling is maintained.  There is no applicable section or 
provision in NFPA 13, 2016 for residential sidewall sprinklers.  Are 
residential sidewall sprinklers permitted to be installed under a soffit if 
both the minimum distance from the sprinkler deflector to the bottom of the 
soffit and maximum distance from the sprinkler deflector to the high ceiling is 
maintained?"
 
We have reviewed NFPA 13, 2016 edition that you indicated as the applicable 
standard.  Our informal interpretation is that the soffit requirement for 
sidewall spray sprinklers should also apply to residential sprinklers.
 
Although the allowance for a sidewall sprinkler to be installed beneath a 
soffit is identified only in section 8.7, this does not mean that the 
underlying reasons for its allowance applies only to spray sprinklers.  This 
just means that the public input was submitted on section 8.7 and the committee 
did not consider its broader application.  This is a common consequence of 
having to process such a large number of public inputs.  The basic evaluation 
for this issue as identified in 8.1.1(3) is whether there is satisfactory 
performance with respect to activation time and distribution.  Considering that 
the thermal link is the same for both sprinklers, the activation will 
effectively be the same.  The committee obviously considered the impact on 
activation time to be negligible.  Considering that the soffit is not in the 
path of the water discharge, the performance regarding discharge is unaffected. 
 As such, there is no logical reason not to extend the same criteria to 
residential sidewall sprinklers.  Since this is not explicitly identified in 
NFPA 13, concurrence by the AHJ is required.
  

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15, 2016
Only A Few Slots Left!

May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
 
For more info, call: 
214-349-5965 ext. 132

        
American Fire Sprinkler Association, 12750 Merit Drive, Suite 350, Dallas, TX 
75251

Reply via email to