March 28, 2016

Overflow Pipe Size for Underground Installations 
 
"There is a question about the overflow pipe size and discharge location. In 
this case, a tank room or water vault is being built inside a high-rise 
building located five stories underground. The waterlines coming into the tank 
are two 8 in. automatic fill pipes and one 8 in. manual fill pipe. What 
calculation would be performed to determine if an 8 in. versus a 10 in. pipe 
could be used for the overflow? If an 8 in. pipe supplies the tank, why would 
an 8 in. overflow not be sufficient? With the tank and pump room being located 
so far below grade level, there is no good way to discharge the water of the 
overflow pipe in the scenario above to a drain. Is it implied that the overflow 
pipe should be routed through the building and up to grade level to discharge 
the water?"  
 
We have reviewed NFPA 22, 2008 edition that you indicated as the applicable 
standard. Our informal interpretation is that overflow design should be 
coordinated with other trades such as plumbing.
 
NFPA 22 does not provide guidance on calculating the size of the overflow pipe. 
Section 14.5.2.3 indicates that unless the maximum fill capacity is known and 
the overflow capacity is calculated to be at least equal to the fill capacity, 
the overflow pipe shall be at least one pipe size larger than the fill line and 
shall be equipped with an inlet such as a concentric reducer, or equivalent, 
that is at least 2 in. larger in diameter. Theoretically, the same size pipe 
should be sufficient. However, a search of studies on the Internet showed that 
the configuration of the overflow pipe in the vertical orientation addressed 
the incoming flow whereas the horizontal orientation with elbows did not 
perform as well.  A Weir box or funnel for the overflow pipe also assisted with 
the drainage. The overflow pipe has to contain a screen to prevent animals from 
entering the tank where that will reduce the surface area of the pipe thus 
affecting the flow.  NFPA 22 appears to compensate for that by upsizing the 
overflow pipe. The pipe should discharge to atmosphere or air break with a 
drain. An overflow that is piped five stories above the level of the tank would 
pressurize the tank and its components during overflow.  As such, the plumbing 
engineer should size a drain to accommodate in case of tank overflow. This is 
also beneficial from a risk management perspective if there is a breach of 
supply piping into the underground structure. The drain should be sized to 
prevent flooding of the structure at the lower levels. The maximum fill 
capacity should be determined and communicated to the engineer of record. They 
should apply the applicable building or plumbing code to dispose of the 
overflow water at the tank location.
  


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


   
Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15, 2016
Only A Few Slots Left!

May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
 
For more info, call: 
214-349-5965 ext. 132

        
American Fire Sprinkler Association, 12750 Merit Drive, Suite 350, Dallas, TX 
75251

Reply via email to