June 13, 2016


Residential Sprinklers in a Compartment

 

“The AHJ is stating I cannot mix residential sprinklers with quick-response 
sprinklers in a hallway per 8.4.5.3. Is that correct?”

 

We have reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is that when residential sprinklers are installed within a 
compartment, all the sprinklers shall be of the residential type.

 

The text regarding this issue changed starting in the 2013 edition of NFPA 13.  
This states in 8.4.5.3, “Where residential sprinklers are installed in a 
compartment as defined in 3.3.6, all sprinklers within the compartment shall be 
residential sprinklers.” The new text referenced “shall be residential 
sprinklers” where the previous text removed was “shall be of the fast-response 
type that meets the criteria of 3.6.1(a)(1).” The issue wasn’t the thermal 
response element between the two types of sprinklers. The issue was the 
different design basis between quick-response sprinklers and residential 
sprinklers so they shouldn’t be mixed. What adds to this confusion is the 
Automatic Sprinkler Systems Handbook commentary addressing this issue did not 
change when the standard text changed in the 2013 edition. The commentary 
states, “When mixing sprinklers that are not of the same make, caution is 
needed to avoid the possibility of reverse operating order or spot operation of 
sprinklers. It is important that all residential sprinklers be of similar 
thermal sensitivity when they are installed in a compartment. The use of 
bulb-type and solder-type sprinklers or residential and other types of 
sprinklers is acceptable, as long as all of the sprinklers in the compartment 
are fast-response sprinklers as defined in 3.6.1(a)(1).” As such, the wording 
from the commentary is in error and conflicts with the text of the standard. 
Quick-response sprinklers and residential sprinklers cannot be mixed within the 
same compartment.

 

 

------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.