August 8, 2016   

 

Ceiling Pocket Volumes

  

“NFPA 13D limits the total volume of all unprotected ceiling pockets in a 
compartment to no more than 100 ft3 whereas NFPA 13 is limited to 1,000 sq.ft.  
Typically, NFPA 13 is more stringent. Please confirm the above references are 
accurate and, if so, please explain the intent of the wide variation between 
the volumes.”

 

We have reviewed NFPA 13, 2013 edition and NFPA 13D, 2013 edition as the 
applicable standards. Our informal interpretation is that these volumes are as 
intended.



You’re right that NFPA 13 is a more stringent document but that primarily means 
that it provides a longer lasting, more robust system along with extent of 
protected areas so as to provide life safety and property protection.  It 
doesn’t mean that all aspects are more stringent. Ceiling pockets is a good 
example. The allowance for ceiling pockets was first added to NFPA 13 back in 
the 2002 edition based on fire modeling performed by AFSA. It was shown that 
large ceiling pockets (bigger than 1,000 sq. ft. and much deeper than 3 ft) 
could be unprotected and the adjacent quick response sprinklers in the lower 
ceiling would activate at least as fast as a standard response sprinkler in a 
flat ceiling. The requirement for QR sprinklers in a light hazard occupancy was 
only added in the 1996 edition so the acceptance of a standard response 
activation time was not an issue (keeping in mind that the reduction of the 
remote area for using QR sprinklers is not allowed). On the other hand, NFPA 
13D?s use of residential sprinklers (as well of NFPA 13 section 8.10) has 
always been based on a fast response element. As such, they can’t tolerate a 
significant delay in activation times. Considering that ceiling pockets have 
become a prevalent feature, it’s desirable that it’s addressed by the 
standards.  The technical committee accepted a proposal allowing 100 sq. ft. as 
a small enough volume so as to have minimal impact on the activation time. 
Don’t forget that an indentation of no more than 12 inches is not considered a 
ceiling pocket. NFPA 13 remains a more stringent standard even with larger 
ceiling pockets.



------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20160808/3219103e/attachment.htm>

Reply via email to