August 15, 2016  

 

Mattress Storage - Solid Shelves

 

“We have mattresses stored on racks with open wire grated shelves.  The 
warehouse has ESFR K-17 sprinklers designed at 52 psi to a maximum 35-foot 
ceiling height, maximum 30-foot storage of Class I - IV commodities and Group A 
plastics.  The proposed racks for a new tenant are double-row with 72 in. wide 
shelves on each side separated by a 30 in. flue space between the racks.  When 
the racks are loaded with the mattresses, the mattresses will hang over the 
back of the racks so the flue space will actually be less than the 24 in. 
maximum flue space.  The mattresses will be stored both on their side and lying 
flat.  When the mattresses are stored on the shelves, the product will create a 
barrier on the shelves that is more than 20 sq. ft. that could be classified as 
solid shelving.  Are in-rack sprinklers required?” 

 

We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard.  Our informal interpretation is that in-rack sprinklers are required 
at every level.

 

The definitions indicate how to determine the size.  First, the rack shelf area 
is defined in 3.9.3.7.6 as the area of the horizontal surface of a shelf in a 
rack defined by perimeter aisle(s) or nominal 6 in. (152 mm) flue spaces on all 
four sides, or by the placement of loads that block openings that would 
otherwise serve as the required flue spaces.  The definition of solid shelving 
in 3.9.3.8 indicates that solid shelving is fixed in place, slatted, wire mesh 
or other type of shelves located within racks.  The area of a solid shelf is 
defined by the perimeter aisle or flue space on all four sides.  Solid shelves 
having an area equal to or less than 20 sq. ft. shall be defined as open racks. 
 Shelves of wire mesh, slates, or other materials more than 50 percent open and 
where the flue spaces are maintained shall be defined as open racks.  The 
definitions tell us that the area of the solid shelving is the perimeter aisle 
or flue space on all four sides.  If transverse or longitudinal spaces were not 
provided, the measurements would have to be taken to the perimeter aisle.  For 
example, if the longitudinal space were covered by mattresses and the 
transverse flue was left open at each rack upright, the measurement would be 
the front and back solid shelves plus the covered longitudinal space.  The 
definition of double-row racks in 3.9.3.7.1 has an aggregate depth up to 12 ft 
with an aisle width of at least 3.5 ft between loads on racks.  Multiple-row 
racks in 3.9.3.7.3 are greater than 12 ft in depth or single- or double-row 
racks separated by aisles less than 3.5 ft wide having an overall width greater 
than 12 ft.

 

The actual solid shelving size has to be determined for this application to see 
if 17.1.5.1 applies.  This section states, “Where solid shelving in  single-, 
double-, and multiple-row racks exceeds 20 sq. ft. but does not exceed 64 sq. 
ft. in area, sprinklers shall not be required below every shelf, but shall be 
installed at the ceiling and below shelves at intermediate levels not more than 
6 ft apart vertically.”  For standard spray sprinklers, this section allows 
in-rack sprinklers to be omitted from some levels if the in-rack sprinklers are 
spaced no more than 6 ft apart vertically.  This applies where solid shelving 
is located close together.  With ESFR sprinklers, this section may not apply 
(still needs to be clarified by the standard).  An example provided in the NFPA 
13 Handbook commentary indicates where solid shelving is provided 18 in. 
vertically between solid shelving that in-rack sprinklers located up to 6 ft 
vertically and not located at every tier can contain the fire size.  This could 
result in several levels of storage between levels of in-rack sprinklers. 
In-rack sprinklers provided at every other level would be located greater than 
6 ft apart vertically and would not meet Section 17.1.5.1.  Regardless of the 
ambiguity regarding ESFR systems, in-rack sprinklers are needed at each tier as 
indicated by Section 17.1.5.2. 

 

Previously, ESFR sprinklers could not be used when solid shelving existed.  
Starting with the 2013 edition, this changed though poorly presented within the 
standard.  The 2016 edition states: 17.1.5.5 Ceiling design criteria for CMDA, 
CMSA, and ESFR sprinklers shall be an applicable option for open racks combined 
with in-rack sprinklers installed in accordance with the criteria for solid 
shelving.

 

There are still some unanswered issues that you will need to resolve with the 
AHJ regarding the placement of the in-rack sprinklers.  The rack assembly could 
be called single-row racks with too narrow of an aisle (if the AHJ ignores the 
placement of the mattress when defining flue width in order to account for 
empty tiers of the rack) and it becomes a multiple-row rack.  If they accept 
the flue as 24 inches, you are still a multiple-row rack (due to overall width 
as discussed above) but you have a flue.  We are told to protect them as 
multiple-row racks as reminded in 17.1.2.3 Storage with aisles less than 3.5 ft 
(1.1 m) shall be protected as multiple-row rack storage.

 

The problem is that there is no valid guidance for in-rack sprinklers.  The 
guidance for a multiple-row rack is basically a maximum spacing along the 
transverse flue combined with a maximum area of coverage.  This does not 
translate to a hybrid multiple-row rack that now has defined openings that 
allow vertical growth of the fire.  Expect to provide an in-rack sprinkler 
within each individual 72 in. rack assembly and one in the flue.

 

------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20160815/f9d495d7/attachment.htm>

Reply via email to