September 12, 2016

  

IFC and Retrofitting Existing Standpipes

 

“The International Fire Code (IFC) states in section 1103.6 Standpipes: 
‘Existing structures shall be equipped with standpipes installed in accordance 
with Section 905 where required in sections 1103.6.1 and 1103.6.2.’  The fire 
code official is authorized to approve the installation of manual standpipe 
systems to achieve compliance with this section where the responding fire 
department is capable of providing the required hose flow at the highest 
standpipe outlet.  Does this mean that buildings with an existing standpipe 
system are required to be upgraded to meet current criteria (100 psi at the top 
most outlet)?” 

 

We have reviewed the 2012 edition of the IFC you indicated as the applicable 
code.  Our informal interpretation is it does not apply to existing standpipes.

 

The wording in section 1103.6, unfortunately, is very poor.  If you read just 
the first sentence, a literal interpretation implies existing systems must be 
upgraded.  If you include the second sentence, though, it is providing guidance 
on installing a new system (allowing a manual system even for a high rise in 
order to control costs).  A basic premise of the building codes is that 
facilities are not required to be upgraded when new editions come out.  In 
prior years, a standpipe was not required except for high-rise buildings 
(occupied floor greater than 75 ft).  Current codes now require standpipes 
starting at 30 ft.  As identified in section 1103.6.1, the IFC wants those 
buildings between 50 and 75 ft that don’t have a standpipe to retroactively 
install one.  This section used the same awkward phrase of “shall be equipped” 
as section 1103.6.  Everyone should agree that this is meant to trigger where 
new standpipes are to be installed. Looking at the entire section clearly shows 
us the intent is to address existing buildings that do not have an existing 
standpipe system. We discussed the issue with an ICC representative, who 
concurred that this interpretation is correct.

 

------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20160912/654e96bd/attachment.htm>

Reply via email to