Horizontal Combustible Concealed Space

 

“The concealed space sprinklers per 8.15.1.6 indicates that concealed spaces 
less than 3 ft shall be protected using listed sprinklers. We have an open wood 
truss construction that is tapered with the above portion being 5 ft and the 
lower being 2 ft.  Concealed space sprinklers have specific requirements one of 
which is they are not listed in spaces greater than 3 ft. Q1) Should truss 
spaces be protected by standard spray sprinklers throughout? Q2) Should the 
space be protected by concealed space sprinklers throughout? Q3) Should the 
space be protected by a combination of standard spray and concealed space 
sprinklers? If so, which design strategy is applied (area/density or concealed 
space strategy?”

 

We have reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is that there are several approaches that can be used for this 
application.

 

The wording in the standard may not be the best, but this section is requiring 
the use of sprinklers listed for applications for horizontal combustible 
concealed spaces less than 36 in. deep. As noted in the Handbook commentary, 
listed standard spray sprinklers were ineffective for fire control since the 
shallow space inhibits the discharge pattern development. When the space is 
greater than 36 in., standard spray sprinklers can be used. The sprinklers 
listed for horizontal combustible concealed spaces have better fire control 
since they provide a flatter pattern of spray. Additionally, the space must be 
horizontal (slope no greater than 2 in 12), the upper deck must be combustible, 
and there must be structural members that channel the heat (even as small as 
top chords on joists). A concealed space that does not contain all these 
conditions in NFPA 13 does not require the specifically listed sprinklers and 
as such, standard spray sprinklers can be used when steel pipe is used. There 
are listing requirements for CPVC piping located in protected horizontal 
concealed combustible spaces. The manufacturer of the plastic piping has 
additional requirements to follow. The manufacturer’s data sheet may indicate a 
minimum depth of 12 in. is needed in the concealed space to apply the specially 
listed sprinkler. Section 8.15.1.6.1 does allow the specially listed sprinklers 
to be used where the space is less than 12 in. from deck to deck in accordance 
with Section 8.3.1.2. The requirements of listings in Section 8.3.1.1 shall not 
apply where construction features or other special situations require unusual 
water distribution, and listed sprinklers shall be permitted to be installed in 
positions other than anticipated by their listing to achieve specific results. 
It is worth noting that 8.15.1.6 (and the sprinkler cut sheet) indicate these 
sprinklers shall only be used in spaces less than 36 in. The question does come 
up as what to do when the 2 in 12 slope with a long run creates a portion of 
the concealed space that is greater than 36 in. Section 8.15.1.6.2 indicates 
that sprinklers specifically listed to provide protection of combustible 
concealed spaces described in 8.15.1.6 shall be permitted to be used in 
accordance with 8.3.1.2 throughout the area when a portion of the area exceeds 
a depth of 36 in. As such, you have a choice to continue the concealed space 
sprinklers into spaces exceeding 36 in. On that note, Tyco has a CC3 sprinkler 
listed for horizontal concealed spaces up to 60 in. The other option is to 
transition to standard spray quick-response sprinklers when the space is 
greater than 36 in.

 

Regarding the remote areas, there will be at least two different remote areas 
required. The minimum size of the remote area for standard spray sprinklers in 
this space would be 900 sq. ft. If there is insufficient area, the smaller 
actual size of the remote area can be applied, but additional water flow may 
have to be added as dictated by 23.4.4.2.4. Note there is an example on how 
this is applied in the annex. The other calculation would be the concealed 
space sprinklers having a minimum remote area size of 1,000 sq. ft. There is no 
guidance on how to address smaller remote areas that aren’t the entire 
compartment since the prior criteria apply only to the density/area method. 
There is no requirement to separate the two types of sprinklers. The exception 
is the draft curtains required by the manufacturer’s data sheets for the listed 
concealed space sprinklers. Refer to the sprinkler’s data sheets for the 
specifics on the draft curtains. It’s much cleaner if you simply use the listed 
sprinklers throughout the space.

 

 