Remote Area Reduction with Ceiling Pockets

 

“If in your remote area, you have a ceiling height of 21 ft 0 in. next to an 18 
ft 0 in. ceiling, can you utilize any area reduction if the 21 ft 0 in. is only 
a small portion of the area?”

 

We have reviewed NFPA 13, 2016 edition that you indicated as the applicable 
standards. Our informal interpretation is that the ceiling is too high for the 
quick response sprinkler reduction.

 

Section 11.2.3.2.3.1 in number (3) indicates a 20-ft maximum ceiling height, 
thus a reduction for quick response sprinklers cannot be applied. For protected 
ceiling pockets with ceiling heights less than 20 ft, then section 11.2.3.2.3.1 
can be applied. The percent reduction to the design area would be calculated 
from the highest ceiling elevation in the remote area. If the ceiling pocket 
falls outside the remote area, an additional calculation would be necessary for 
the area with the ceiling pocket to prove the sprinklers at the higher 
elevation. As such, the determining factor in applying a quick response 
reduction is the ceiling height and not the area of the protected ceiling 
pocket. Also, note that the quick response reduction cannot be used when there 
are unprotected ceiling pockets allowed by 8.6.7 and 8.8.7 that exceed 32 sq. 
ft. in area Section 11.2.3.2.3.1 in number (4).

 