Annex Examples of Sprinkler Locations in Small Rooms

 

“Due to Figures A.8.6.3.2.4(b), (c) and (d), the AHJ is interpreting that in 
small rooms with multiple sprinklers, the room can't be more than 15 ft in the 
least dimension (per Figure (b)) or 30 ft in the long dimension (per Figures 
(c) and (d)). The AHJ thinks only small rooms with a single sprinkler can be up 
to 16 ft 6 in. wide in one direction (per Figure (a)). Can a small room be 16 
ft 6 in. wide with multiple sprinklers in a single row?”

 

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that the figures in the annex are only examples, but they do 
represent some maximum allowances.

 

The small room definition is basically the definition of a compartment with the 
limitation of light hazard occupancy and floor areas not exceeding 800 sq. ft. 
The small room application is not limited to offices. The small room can apply 
to any light hazard occupancy such as corridors, lobbies, bathrooms, conference 
rooms, etc. When calculating the area of coverage, you simply take the area of 
the room and divide it by the number of sprinklers. The S x L rules do not 
apply but the maximum area of coverage must still be applied. The examples in 
A.8.6.3.2.4 are providing four possible configurations attempting to show the 
limiting constraints of all criteria including the maximum area of coverage. 
Per your examples, a room has one row of three sprinklers. One of the 
sprinklers is located 7 ft 6 in. from the wall, you have another sprinkler 
located close to the middle of the room 15 ft from the first sprinkler and 10 
ft away from the third sprinkler, which is located 3 ft 10 in. off the wall at 
the far end of the room. Now the row of sprinklers is located 9 ft from one 
wall and 7 ft 6 in. to the other wall. This will give you a room size of 36 ft 
4 in. by 16 ft 6 in. for a total square footage of 599.49. This equals to 
199.83 sq. ft. area of coverage per sprinkler in that room. Example Figure 
A.8.6.3.2.4(a) may create some confusion because it is not a literal example 
since the A-B dimension shows a maximum of 7 ft 6 in. as does the B side, but 
the lower dimension reminds us that the total width is limited by the assigned 
area of coverage. Another limitation that should be noted is that the total 
room area cannot exceed 800 sq. ft. In closing, the referenced 16 ft 6 in. in 
one dimension for a room with a single sprinkler is an example of a maximum 
dimension. As stated in the standard, you can be 9 ft off a single wall leaving 
7 ft 6 in. to the other wall creating an overall maximum of 16 ft 6 in.

 

 

 

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; Tom Wellen, a PE registered in fire 
protection engineering; Jason Williams, CET, Manager of ITM Technical Training; 
and Tom Noble, E.T., Technical Programs Specialist. This is provided with the 
understanding that the AFSA assumes no liability for this opinion or actions 
taken on it and they are not to be considered the official position of the NFPA 
or its technical committees. 

 

Copyright 2017, American Fire Sprinkler Association. All Rights Reserved

 

 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20170626/62564ecb/attachment.htm>

Reply via email to