sprinklernotes
Mixing Sprinklers with Different Temperatures and Operating Elements



You have asked the following question: “Can you have a 165-degree fusible link 
sprinkler and a 155-degree glass bulb sprinkler in the same compartment?” In 
response to your question, we have reviewed NFPA 13, 2016 edition as the 
applicable standard. Our informal interpretation is a 165-degree sprinkler can 
be installed in the same compartment as a 155-degree sprinkler.

165-degree sprinklers and 155-degree sprinklers are both rated as 
ordinary-temperature per Table 6.2.5.1. Section 8.3.2.1 states: 
“ordinary-temperature and intermediate-temperature sprinklers shall be used 
throughout buildings.” The same temperature rated sprinklers are required in 
the same compartment to reduce sprinkler skipping. Sprinkler skipping is when a 
sprinkler that is not in the immediate vicinity of the fire activates. This 
will decrease the flow and pressure of the sprinklers closer to the fire 
causing those sprinklers to be less effective. 165-degree sprinklers and 
155-degree sprinklers (and even larger differences such as a 135 and 165) will 
have an insignificant difference in activation times. The bottom line is that 
both are ordinary-temperature sprinklers thus allowing them to be installed in 
the same compartment.

An interesting unasked question is can you combine both ordinary- and 
intermediate temperature ratings. A literal application of the text implies you 
can since it says “and” in Section 8.3.2.1. Not long ago we had to use only 
ordinary-temperature sprinklers unless there was a localized higher temperature 
risk. The committee finally realized that mixing in intermediate sprinklers for 
localized temperature exposures made a lot less sense than allowing 
intermediate-temperature sprinklers to be used throughout. As stated in the 
Sprinkler Handbook, “the response time of quick response intermediate 
sprinklers is not that different from standard response ordinary sprinklers.” 
This should be read that you can use one or the other (when not addressing 
localized exposures). Although there is no significant difference in activation 
of a 165-degree (ordinary-temperature) sprinkler and a 175-degree 
(intermediate-temperature) sprinkler, there is a line in the sand needed to 
avoid mixing 135-degree and 225-degree sprinklers.